We have 2*38.5 MW coal based steam turbines, both always runs at 25 MW individually, Auxiliary consumption 5 MW and inter connection cement plant 9 MW and export to GRID is 36 MW
Whenever grid disturbance occurred the grid circuit breaker opening and plant came to home load at TG-1: 3.5 MW and TG-2: 5.8 MW
after that points are noted as bellow
1. TG-1 load rapidly dropped to 0 MW and Generator tripping on reverse power protection.( if we are in alert position TG-1 breaker manually opens while load dropping condition and saves from Turbine trip)
2. Whenever TG-1 load dropping, TG-2 load raising rapidly.
3. TG-2 withstanding home load at 9.5 MW ( 5 MW power plant auxiliary and 6.5 MW Cement Plant auxiliary )
4. after getting clearance from GRID, going synchronised
5. Before Close the Breaker we observed following parameters
TG-2 active power : 9.5 MW
Reactive power : 2.1 MW
Power factor :0.987 Lag
Voltage : 11.25 KV ( matched with Grid voltage)
Frequency : 49.99 to 49.98 ( matched with Grid Frequency)
after getting Synch permit we are closing breaker then immediately Load was hunting from 13.5 MW to 1 MW
here we are observed turbine actuator Hunting rapidly.
and unable observed frequency of the Generator and Speed of Turbine
let me know any suggestion why TG hunting started after synchronization