REF

04/04/2019 7:41 AM

Dear all

in our plant installed new transformer 400/18 KV , the restricted earth fault

protection operated when any fault happened with over head line ,we check all

current transformer polarity its ok,please can any one help to know the reasons for

Restricted earth fault operated.

thanks for all

Register to Reply
Pathfinder Tags: REF
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: REF

04/04/2019 8:08 AM

Start here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#2
In reply to #1

Re: REF

04/05/2019 12:22 AM

It seems that it is working properly, since it is a very sensitive ground fault detector, and most overhead line faults tend to be ground faults. Maybe it is misapplied?

My guess, if you are sure it is not working properly (from my very first observation today of this method of ground protection system since I started in power system engineering in 1975 in the US), your line current transformers are saturating before your neutral current transformer.

Perhaps the drawback of this theoretically very sensitive method of detecting a ground fault is that the current transformers need such a high ratio that your realized sensitivity is much worse than the theoretical 15% over winding rated current.

In the US, if we can protect the transformer windings for ground faults down to 10% of the winding voltage rating, we're doing good. For the delta side, on a solidly grounded system, in practice, a ground fault relay in the residual connection (51N) will not actuate reliably for fault current below the Current Transformer primary rating, i.e. a ground relay in the neutral of 1500/5 ampere current transformers will not trip even on the 0.5 ampere setting unless you have a good 5 amperes of secondary current.

Relay schemes that need to be restrained for magnetizing current seem complex. A transformer of the size to warrant that sort of protection should be protected with differential protection, mature and common enough designs to include easy set up for different current transformer ratios and saturation characteristics. Then the layer of protection for your transmission lines can be separate, and tailored to the needs of that system.

The actual power system grounding and application of your restricted earth fault relay is important for diagnosis, solid wye ground, zig-zag grounding transformer, multiple grounds on the system, delta or wye supply to your distribution line, available fault current, these details will be helpful to further diagnose your problem. Maybe the relays are set to the wrong current threshold setting, for instance.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: REF

04/05/2019 8:42 AM

"any fault happened with over head line" - Do you mean 400kV OHL. If true, it is clearly a matter of stability of REF protection, considering that you already confirmed the CT secondary wiring to relay including polarity of phase and neutral CTs.

The way forward is to get the stabilising resistor calculation verified.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Oct 2013
Posts: 72
#4
In reply to #3

Re: REF

04/05/2019 11:37 AM

Thank you all for their answers

yes I mean 400KV OHL

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#5
In reply to #4

Re: REF

04/05/2019 5:41 PM

So the line is feeding into a delta winding, and your power system ground is remote?

Your lighting arresters (with a ground path) might be inside of your protection, unless your relays are fed from bushing current transformers...

Register to Reply
Commentator

Join Date: Oct 2013
Posts: 72
#7
In reply to #5

Re: REF

04/06/2019 3:42 PM

dear

thanks for your response

yes our protection feed from bushing current transformer

thanks

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#6
In reply to #4

Re: REF

04/06/2019 5:21 AM

Asser, Once you find out the real problem, do post the details.

I am supposing the transformer is YNd connected and is acting like zero sequence current source for earth faults in 400kV lines feeding the faults (though there is no source on secondary side of transformer).

Common problems I have come across with HiZ REF protection schemes:

1) The neutral CT is left shorted near (or on top of) the transformer.

2) The polarity of neutral CT is not verified during stability check and is incorrect.

__________________
Raghunath
Register to Reply
Commentator

Join Date: Oct 2013
Posts: 72
#8
In reply to #6

Re: REF

04/06/2019 3:58 PM

thank you for your interest

We check the neutral bushing CT it is connected to the relay and the polarity it is ok,since when

transformer in service the Bais HV REF>>>Diff HV REF ,but when the fault happen in the line

the Bais HV REF become less than Diff HV REF

thanks

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#9
In reply to #8

Re: REF

04/06/2019 8:31 PM

Just curious, are you using the High Voltage bushing current transformers for the line current signals? It certainly seems that the polarity is reversed, assuming the protection is designed to detect ground fault current within the transformer case.

I suppose it might not be the first time someone was not paying attention to the primary polarity marks when they assembled the current transformers to the bushings. Certainly difficult to verify visually at this point...

The secondary winding for your transformer is connected in Delta?

Do you have generation sources on both sides of your transformer?

Do you have transformer differential protection installed?

Register to Reply
Commentator

Join Date: Oct 2013
Posts: 72
#10
In reply to #8

Re: REF

04/07/2019 8:37 PM

Dear sir

the transformer have three winding (LV,TV) 18KV Delat connected and HV 400KnutV

Star connected. All CT (one in neutral side and three on phases) bushing type

the same CT uses in differential protectiont and restricted earth fault protection

Each delta side connected to generator and star side connected to the 400kv grid

thanks

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#11
In reply to #10

Re: REF

04/07/2019 9:10 PM

So it seems unlikely that the bushing current transformers for the differential protection would have been installed correctly and the phase CTs incorrectly, so the polarity is likely OK, as you have verified.

if you do have a ground fault on your lines, your generator needs to disconnect at some point before you melt or seriously damage one of your transmission phase conductors. If the faults are on the main line, then opening up your high side or low side circuit breakers is the correct response. If the faults are beyond other transmission circuit breakers, then your primary REF protection should have some time delay to allow the downstream or remote circuit breakers to open, selective tripping or coordination. Other options include distance relays, where the transmission conductors are modeled and the relay is set to respond for a fault fed by your generator(s), through your transformer, for some line distance from your transformer, uses predicted X/R fault currents, without overlapping zones of protection beyond distant protection zones.

Your current REF protection is supposed to be quite sensitive, but I suspect that it gives you no more sensitive protection in practice than your transformer differential protective relay, due to current transformer saturation, as I explained earlier for residual (CT neutral) connections. As a backup for your differentials, adding some time delay up to the damage curve of your line conductors would seem worthy of consideration. A chat with your system protection designer MIT be helpful.

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ASSER (4); PWSlack (1); raghun (2); rwilliams (4)

Previous in Forum: Voltage Drop Calculation for Star Delta Starter Motor   Next in Forum: Rotor Winding IR Test

Advertisement