Rotor Winding IR Test

04/05/2019 5:51 AM

Good day,

I have a question about the resistance reading between the rotor winding of a 1000KVA Leroy Somer LSA 50.1 alternator, and earth.

As far as I know, when performing an IR (insulation resistance) test between the disconnected rotor winding leads and the alternator main shaft (earth) the resistance should be very high (K/Ohm or M/Ohm) or even infinity (if brand new)

In my case, when using a high quality Megger meter, the test voltage that increases from 0V to 1000V over the 60 second test period should go up to at least 800+ Volts AND indicate a high resistance at the end of the 60 second test, if the rotor winding was good.

However, during my actual test the voltage barely rises to 11V before the megger start sounding alarms and resistance does not even register on the display.

I am second guessing myself and just want another expert opinion.

In my view the alternator is bad and must be rewound/replaced.

Any views on this?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Rotor Winding IR Test

04/05/2019 7:14 AM

<...the alternator is bad and must be rewound/replaced....Any views on this?...>

Yes.

  1. The <...Megger...> has fried some insulation somewhere inside the <...alternator...>.
  2. Get on the phone to <...Leroy Somer...> and discuss it with them before doing anything further.
  3. Time is money. Spend it on getting to the end of this matter rather with them rather than waiting and hoping someone on CR4 will provide a valuable answer to the problem. "A watched pot never boils" - Anonymous Poster #0
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Mar 2016
Posts: 26
#2
In reply to #1

Re: Rotor Winding IR Test

04/05/2019 8:37 AM

Hi there,

To quote you "The <...Megger...> has fried some insulation somewhere inside the <...alternator...>"

The megger cannot fry anything in the alternator. During an IR test is the megger's job to introduce rising voltage (from 0 to 1000VAC) to the winding in question to test for breakdown to earth. It cannot fry anything, least of all a massive winding such as the rotor winding.

I guess my question was misleading. What I should have asked is for confirmation as to whether my test showed that the rotor is down to earth.

My megger indicates that there is breakdown to earth already occurring at 11VAC, just after the test is started, test voltage is introcuced at 0 VAC and starting to rise, and upon conclusion of the test after 60 seconds the IR resistance does not even register on the MegOhm scale on the meter.

Operational voltage to the rotor winding is between 0VDC and 100VDC after passing from the exciter and diodes to the rotor. IR test voltage is 1000VAC.

Actually I'm answering my own question here. I just wanted confirmation from someone in the know.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #2

Re: Rotor Winding IR Test

04/07/2019 1:47 PM

Well, if it wasn’t the <...Megger...> then it was something else that fried the insulation. So what? The solutions are the same.

It’s time to get on the phone.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Rotor Winding IR Test

04/05/2019 9:03 AM

The winding probably just needs to be re-coated with epoxy...

https://www.lasertechnologiesinc.com/lamination-refurbishing-core-plate-coating

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Associate

Join Date: Mar 2016
Posts: 26
#4
In reply to #3

Re: Rotor Winding IR Test

04/05/2019 9:18 AM

Hi,

Thanks. Yes, we will strip the 1000KVA Leroy Somer alternator and send it away for refurbishment and/or replacement. I am on a major Chevron production site in Nigeria and way out in the swamp, so these jobs aren't easy.

I still want someone with knowledge about this to varify my initial question about my IR test.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #4

Re: Rotor Winding IR Test

04/05/2019 11:29 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#10
In reply to #4

Re: Rotor Winding IR Test

04/06/2019 8:48 AM

Yes, it will require surgery, unless the brush rigging/ slip ring insulation has failed in a non-spectacular manner.

Unless it was subjected to a violent overspeed, it sounds like a warranty failure if it turns out the winding went to ground. If it was wet, you should get more than 11 volts.

Did you try reversing the Megger polarity? How about a regular Fluke on ohms?

Register to Reply
Power-User

Join Date: Jul 2014
Posts: 113
Good Answers: 4
#6

Re: Rotor Winding IR Test

04/05/2019 10:43 PM

What is wrong with the item, in the first place?

Register to Reply
Associate

Join Date: Mar 2016
Posts: 26
#7
In reply to #6

Re: Rotor Winding IR Test

04/06/2019 4:40 AM

I explained it in the first post

Register to Reply
Associate

Join Date: Mar 2016
Posts: 26
#8

Re: Rotor Winding IR Test

04/06/2019 4:44 AM

Thanks all!

Conclusion: after using 3 separate Meggers to prove the same fault we now have conclusive evidence that the insulation resistance of the rotor breaks down to earth when load is introduced.

The alternator will be removed and replaced.

Register to Reply
Power-User

Join Date: Jul 2014
Posts: 113
Good Answers: 4
#9

Re: Rotor Winding IR Test

04/06/2019 5:06 AM

No you didn't. I expected you to say the alternator has no output, or it is getting very hot or the chassis is live.
If you get an ordinary multimeter, what is the resistance?
Get 6 x 9v batteries and 4k7 resistor and a LED and see if it illuminates.

And the next thing you do is get a 40 watt globe, preferably on a 100 watt isolating transformer and connect it to the transformer and then cut one lead and with the two probes, touch the two points you say have a low resistance and see if the globe illuminates.
The first law of electrical wiring is: NEVER TEST A FAULTY CIRCUIT WITH A MEGGER. It gives you a false reading. No circuit breaks down at 11v.

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers: