What is the minimum required space - from the gland plate to the terminals - inside a switchgear cable chamber, for a 36kV XLPE Cable?
Is there a Standard for the same?
Re: Minimum Height required - from gland plate to the terminals - for cable termination for 36kV XLPE Cable
04/08/2019 3:59 AM
The minimum space is that needed to bend and terminate the cables without kinking the insulation or other mechanical damage to the cable. It is a function of cable conductor and insulation size and stiffness.
Minimum recommended bending radii can be had from the cable manufacturer.
04/10/2019 7:20 AM
As a rule, 20 times the diameter of the cable gives the minimum bending radius. Once installed this can be reduced to 15 times the cable OD. Nowadays, to save on trenching and squeezing bends underneath switchgear they now allow 10 times the cable OD. This I find disagreable and absurd as anyone who can bend a 1200mm2 single core to that radius, or a 630mm2, 3 core, SWA to that bend needs his head read or has great medical cover.
Quickest method to check a bend, measure the diameter of the core of the cable drum and that is the minimum bend allowed for that cable.
Good Answers: 181
Re: Minimum Height Required for 36kV XLPE Cable Termination
04/08/2019 7:24 AM
Are you using heat shrink with terminal boots or using gel fill?
Good Answers: 170
04/09/2019 1:34 AM
Heat Shrink
Re: Minimum Height Required for 36 kV XLPE Cable Termination
04/08/2019 12:08 PM
No there is not a standard because not all cables are made the same. Utilize the data from the cable manufacturer.
04/09/2019 10:18 AM
Yes, there actually is a standard that most countries use. There is also an NRS standard for terminations inside switchgear and if you are using a heatshrink termination, you should know the measurements shown on the instruction sheet is minimum dimension allowable.
33kV(36kV), single core or 3 core is 960mm from lug hole to gland plate minimum distance required. No, you will not get that from gear manufacturers. If this was screened PILC, you can go to 690mm. That is what gear manufactured will give you. If you stipulate the gear is for XLPE cable they will charge higher for the gear due to more metal being used.
But as for standards and NRS's they exist.
04/09/2019 12:12 PM
I should have added, install a gland plate extension if the space is short. See Raychem (TYCO, {taking your company over}) for gland extenders.
http://www.cableservices.co.uk/cable-terminations/Tyco-Box-Glands-Insulators.pdf
04/10/2019 12:24 PM
Once can always use non-flat gland plates, of course.