Minimum Height Required for 36 kV XLPE Cable Termination

04/08/2019 2:34 AM

What is the minimum required space - from the gland plate to the terminals - inside a switchgear cable chamber, for a 36kV XLPE Cable?

Is there a Standard for the same?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Minimum Height required - from gland plate to the terminals - for cable termination for 36kV XLPE Cable

04/08/2019 3:59 AM

The minimum space is that needed to bend and terminate the cables without kinking the insulation or other mechanical damage to the cable. It is a function of cable conductor and insulation size and stiffness.

Minimum recommended bending radii can be had from the cable manufacturer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#7
In reply to #1

Re: Minimum Height required - from gland plate to the terminals - for cable termination for 36kV XLPE Cable

04/10/2019 7:20 AM

As a rule, 20 times the diameter of the cable gives the minimum bending radius. Once installed this can be reduced to 15 times the cable OD. Nowadays, to save on trenching and squeezing bends underneath switchgear they now allow 10 times the cable OD. This I find disagreable and absurd as anyone who can bend a 1200mm2 single core to that radius, or a 630mm2, 3 core, SWA to that bend needs his head read or has great medical cover.

Quickest method to check a bend, measure the diameter of the core of the cable drum and that is the minimum bend allowed for that cable.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Minimum Height Required for 36kV XLPE Cable Termination

04/08/2019 7:24 AM

Are you using heat shrink with terminal boots or using gel fill?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #2

Re: Minimum Height Required for 36kV XLPE Cable Termination

04/09/2019 1:34 AM

Heat Shrink

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Minimum Height Required for 36 kV XLPE Cable Termination

04/08/2019 12:08 PM

No there is not a standard because not all cables are made the same. Utilize the data from the cable manufacturer.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#5

Re: Minimum Height Required for 36 kV XLPE Cable Termination

04/09/2019 10:18 AM

Yes, there actually is a standard that most countries use. There is also an NRS standard for terminations inside switchgear and if you are using a heatshrink termination, you should know the measurements shown on the instruction sheet is minimum dimension allowable.

33kV(36kV), single core or 3 core is 960mm from lug hole to gland plate minimum distance required. No, you will not get that from gear manufacturers. If this was screened PILC, you can go to 690mm. That is what gear manufactured will give you. If you stipulate the gear is for XLPE cable they will charge higher for the gear due to more metal being used.

But as for standards and NRS's they exist.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#6
In reply to #5

Re: Minimum Height Required for 36 kV XLPE Cable Termination

04/09/2019 12:12 PM

I should have added, install a gland plate extension if the space is short. See Raychem (TYCO, {taking your company over}) for gland extenders.

http://www.cableservices.co.uk/cable-terminations/Tyco-Box-Glands-Insulators.pdf

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Minimum Height Required for 36 kV XLPE Cable Termination

04/10/2019 12:24 PM

Once can always use non-flat gland plates, of course.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); IQ (3); PWSlack (2); redfred (1); TonyS (1)

Previous in Forum: Rotor Winding IR Test   Next in Forum: Technical Assistance and Advice to Save Energy Required

Advertisement