Technical Assistance and Advice to Save Energy Required

04/10/2019 8:05 AM

We would like to have your kind assistance regarding our technical query. We are using Slipring type Electric Motors (1250 HP) 1000 kW, 950 RPM 400VAC 50Hz. in our 15 re-rolling mills. We want to reduce our energy losses for these motors and wish to use Frequency Drive for these mills. Can you please assist us with your technical advice if we can save 15% to 20% energy with using VFDs? We also have same mills with electric motors 1000 kW in 6600V 50Hz. Please advice if you can suggest High Voltage VFDs for these motors and we can save the same 15% to 20% ? You are requested to kindly assist us with your technical expertise and please quote for both VFDs in low and high voltage drives for 1000 kW motors. We look forward to hearing from you soon. Best regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#1

Re: Technical Assistance and Advice to Save Energy Required

04/10/2019 11:08 AM

No, not likely to save 15% to 20% energy.

But, by all means, contact several vendors of VFD's. They will be happy to tell you how they can help you.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2
In reply to #1

Re: Technical Assistance and Advice to Save Energy Required

04/10/2019 12:22 PM

...particularly on <...please quote for both VFDs ...>, as CR4 doesn't do that.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: Technical Assistance and Advice to Save Energy Required

04/10/2019 12:43 PM

One Billion Dollars....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Technical Assistance and Advice to Save Energy Required

04/10/2019 1:30 PM

Go to this web site:

We just discuss stuff. We don't sell anything on this forum.

Register to Reply
6
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Technical Assistance and Advice to Save Energy Required

04/10/2019 2:56 PM

You can only save energy when you reduce losses. Changing to a VFD on a rolling mil will present no significant change in the throughput efficiency. If someone is telling you that it will, they are attempting to steal your money.

VFDs only offer significant energy savings when applied to centrifugal (quadratic) loads such as pumps and fans where they REPLACE less efficient means of flow control by taking advantage of the affinity laws of fluid dynamics because as flow is reduced, less torque is required. You have no such opportunity with a rolling mill, it requires a constant amount of torque regardless of speed and that means energy required from the motor remains the same regardless of how you change the motor speed. You have losses in the wound rotor motors, but you will have those same losses using a VFD, plus you will add the 3-4% losses of the VFD!

Since you already have slip ring wound rotor motors, one thing you could look into is a slip recovery system that would connect to the wound rotors and convert some of the rotor losses into regenerated electrical energy back to your grid.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 6)
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#9
In reply to #5

Re: Technical Assistance and Advice to Save Energy Required

04/11/2019 5:49 PM

VFD's can be used on constant torque loads, if selected and set-up for this type of load. If you are running the slip ring (wound rotor) motors at a reduced speed then you have the losses of energy in the secondary circuit going through the slip rings from the motors. You will have to work closely with the manufacturers and be ready with a lot of data about the typical speeds the motors are running. A qualified engineer is a must for your application, so choose the person carefully with a good look at the references and completed projects done by this person. Call the customers that have been named to verify the adequacy of services.

--JMM

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #9

Re: Technical Assistance and Advice to Save Energy Required

04/11/2019 8:46 PM

I wasn't implying that VFDs don't work for constant torque loads, they absolutely do. But they don't save ENERGY on constant torque loads, unless maybe you are using them to replace a mechanical speed changing system like a vari-drive that has more losses. The OP was implying they wanted to save a lot of energy vs the slip ring control method, and that is not going to be the case if he leaves the old motors in place.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#11
In reply to #10

Re: Technical Assistance and Advice to Save Energy Required

04/11/2019 9:02 PM

If I remember correctly, a slip-ring (wound rotor) motor can provide nearly full torque over a substantial speed range. If his application is running the motor at a reduced speed because of some form of resistance being used on the secondary conductors, then a VFD can be used, and will give a reduced speed with the losses being drive losses instead of resistor heat losses (with potential energy savings here). He would have to short the three slip rings together and remove the secondary resistor assembly along with the brushes that had been riding on the slip rings. I am sure you know all this.

Some posts have suggested an alternative method whereby the energy loss currently in the secondary resistor circuit is redirected into power being regenerated onto the incoming line. I have never done this nor have I heard of it before, but it certainly sounds reasonable.

If, however, the heat loss in the motor's secondary resistor circuit is being used somewhere else for process heat, then the savings will probably be small.

Hopefully the Original Poster (OP) can log back in and give us some more information.

Register to Reply
Participant

Join Date: Apr 2019
Posts: 2
#12
In reply to #11

Re: Technical Assistance and Advice to Save Energy Required

04/11/2019 9:37 PM

Thank you Meuller for your kind response and helpful information.

I will update if we go to do anything and whatever response we get from it.

Thanks & regards,

Salman

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6

Re: Technical Assistance and Advice to Save Energy Required

04/10/2019 3:19 PM

Skip to 3:00

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#7

Re: Technical Assistance and Advice to Save Energy Required

04/10/2019 3:25 PM

Here is a link that will explain slip recovery methods and the considerations you should study before you purchase and upgrades. In the proper applications,much energy can be saved,but only you or your team can decide the best direction. This link is provided for guidance only: https://www.tmeic.com/sites/default/files/assets/files/library/TMEIC_SEPT_ICR_low_1260284113.pdf

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#8

Re: Technical Assistance and Advice to Save Energy Required

04/11/2019 12:57 PM

Namaska, Aap kaisi hai. Seimens, ABB, Schnieder. Now showing in a local phone book near you.

Happy to quote you, please forward the contact person details, along with none refundable deposit and PO.

Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: