We recently trying to start 425KW, 415V, 3Ph motor, we found tripping by ELR relay in the feeder of the motor. we test IR with 1000V for motor and cable and found values are good. Cable laid from feeder to motor is 3 run 3core cable. Changed the Earth leakage relay and CBCT also of the feeder. And checked the relay setting too which perfectly matches with the existing ELR setting of 425KW motor other feeders. Earth cable has been laid from feeders and terminated in a good way and also local field earthing found to be good. Please help us to diagnose the trip which is happening.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Mr

04/17/2019 4:47 AM

Having replaced the ELR [assumption: "earth leakage relay"] and CBCT [undefined] it is now possible to determine whether the fault lay in the ELR /CBCT, the motor feeder cable or the equipment downstream of it:

  • If the fault persists, then the latter is the case, so then it is a case of isolating the motor from the cable and trying again, and then reconnecting the motor and trying again.
  • If the above is inconclusive then carry out a "Megger" test on the above to yield more information.
  • If the fault has gone away, then it was in the displaced ELR/CBCT, which now needs to be presented for recycling under the pan-European WEEE Directive before the Brexit Date of 31st October 2019.

If in doubt, consult a qualified local Electrician.

Simples. ζ

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
2
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#2

Re: Mr

04/17/2019 6:20 AM

Get a local electrician involved. Sounds like the protection devices are working properly and there is a real (but simple) fault.

Could be as simple as one of the 3 run conductors has been switched to another phase or phase rotation incorrect.

Another help for that electrician would be background information like was the motor previously running and has been moved to another location? Does the motor turn "free" manually (with power isolated!)? Does the ELR trip with the cables disconnected (and isolated) at the motor end? (This will assist in determination of the fault being in cabling or motor fit-up.

Big energy BE SAFE!!

__________________
Just an Engineer from the land down under.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: Mr

04/17/2019 10:08 AM

CBCT installation is a challenge when you have three nos 3-core cables to pass through its window. Assuming that the cable armour is not passed through the CBCT window, I guess the problem is with the centering of these cables in the CBCT window.

It is recommended to select a CBCT that has window as large as twice the dia of all the three nos three core cables put together.

The ELR maloperates during start as that is the time the error current out of the CBCT is highest due to residual flux in the CBCT window.

You may have to either re-engineer the CBCT/ELR scheme or resort to bypassing/disabling the protection for the time the motor takes to come to full speed.

Increasing the ELR pickup setting can be considered, but I doubt it will help.

ELRs are made to comply with IEC 60947 and can have non-operate threshold as low as 50% of the pickup setting.

Increasing time delay is counter-productive as it will allow motor to burn when there happens to be a real fault.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 809
Good Answers: 65
#4

Re: Mr

04/18/2019 5:47 AM

Check to ensure that the motor cables are passing through the ELR CT are in the order RST RST RST not with all the R phases together, all the S phases together and all the T phases together. by not keeping the cables in trefoil will produce a magnetic imbalance in the CT.

It can also be a motor winding fault causing an unbalanced motor current at start leading to the ELR CT saturating and giving a false trip. Check the winding resistance with a low ohms bridge tester.

__________________
Hare today, goon tomorrow!
Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Just an Engineer (1); PWSlack (1); raghun (1); Stef (1)

Previous in Forum: Minimum Distance From Tray Ladder 33 kV   Next in Forum: Any Idea About Constant Current Source for 5,000V Power Supply?

Advertisement