Low Fault Level Effect on LRA and FLA

04/23/2019 7:31 AM

Hi There,

What effect will a low fault level at source (1kA) have on starting large 450kW DOL motors. and why?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Low Fault level effect on LRA & FLA

04/23/2019 7:35 AM

If the fault is large enough, (a) circuit protective device(s) will disconnect it, and the <...motors...> will not start.

<...FLA... LRA...> are characteristic design features of the <...motors...> at various voltages, and are unrelated to a <...1kA...fault...> in the supply cables.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #1
#2

Re: Low Fault level effect on LRA & FLA

04/23/2019 7:55 AM
Register to Reply
Participant

Join Date: Apr 2019
Posts: 4
#3
In reply to #2

Re: Low Fault level effect on LRA & FLA

04/23/2019 8:08 AM

RLA = Rotor Locked amps

FLA = Full load Amps

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Low Fault level effect on LRA & FLA

04/23/2019 8:33 AM

Quite.

It remains impossible to relate these features to fault currents.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Low Fault Level Effect on LRA & FLA

04/23/2019 6:29 PM

Actually, available fault current level can have an effect on starting. If the source is too soft, the LRA can cause a significant voltage drop and that in turn may affect the acceleration time, up to and including a stall condition.

No mention of voltage levels but by virtue of using the term DOL and kW for motor size, let's assume 400V nominal. So LRA on a 450kW 400V motor can be over 5x the stated 1kA available fault current, meaning it most assuredly will cause so much voltage drop that I doubt the motor can start DOL at all. FLA therefore will have nothing to do with it because if the motor is tripped off-line, FLA is irrelevant.

It will have no effect on the value of LRA or FLA of the motor, which is how this was entitled, but the question asked is different.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#6

Re: Low Fault Level Effect on LRA & FLA

04/23/2019 11:11 PM

Assuming an induction 3 phase motor, with normal starting current...

It is likely that an extremely low available fault current such as 1kA symmetrical (assumed) is due to very small generator system or to extremely high impedance between generation and consumer.

In the case of a small generator, i.e. 450kW to 900kW, the generator voltage regulator may not have the range to develop the voltage (motor accel torque), usually a field forcing circuit and voltage restrained overcurrent protection on the stator leads is required to supply the current to bring to motor up to speed from a stop.

In the case of a very weak supply system, the system impedance between the source generators and starting motor is very high. The voltage at the motor terminals could be so low at start the the motor would not be able to accelerate the load in the time required to avoid extreme rotor and stator heating and/or motor current protection activation.

The fault current is listed in amperes, and there is no voltage reference. Assuming a 600hp ~ 600kVA motor, and assuming the fault current is 1000A at 415V basis, it amounts to 718kVA fault source, less than twice the motor rating, so normally not enough to get the motor started.

Reduced starting methods would generally not work, unless the rotor was wound and had stepped resistors, or was specially designed to safely take the heat generated during an extended start. The actual driven load speed characteristic is needed to analyze the starting capability.

A variable frequency drive for the motor (i.e PWM inverter) will work in this case, providing the motor driven load breakaway torque is low. You do not have much of a margin available, limited by your source and the hardware current rating of the inverter, often a limit you encounter when driving constant torque loads

Register to Reply
Participant

Join Date: Apr 2019
Posts: 4
#7
In reply to #6

Re: Low Fault Level Effect on LRA & FLA

04/24/2019 2:19 AM

Hi All,

Not the ideal power supply.

Just bit more info the utility supply is 22kV 15km from source sharing power with 14 other customers we transform the 1600kVA TX 4% Z to 11kV to 400metres to a underground coal mine transform again 800kVA 4% Z down to 1000V. The machine is a standard design continuous miner DOL.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#8
In reply to #7

Re: Low Fault Level Effect on LRA & FLA

04/24/2019 12:33 PM

You used your utility fault contribution to calculate the 1000 ampere 3 phase bolted fault contribution?

i would think you would get closer to 10,000 amperes symmetrical, even with the 800 kVA transformer.

i would assume given this configuration (not knowing the 1000 sc avail) you would have no trouble starting your motor if unloaded. Your locked rotor available torque is maybe slightly less than you might get with a larger transformer, but assuming the transformer is a unit transformer, no other large rotating machinery, it is a generous rating for a unit transformer, applications quite common in industry. They (unit transformer) perform quite well as a replacement for a reduced voltage starter, often a cost effective option when considering various options to reduce flicker on the upstream power system.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Low Fault Level Effect on LRA and FLA

04/24/2019 4:48 PM

One wonders what all those <...1kA...> are heating? That's one hell of an arc!

Thank goodness someone else is paying the electricity bill...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10

Re: Low Fault Level Effect on LRA and FLA

04/25/2019 8:21 AM

In my opinion, the short-circuit current at 800 kVA 11/1 kV transformer terminal could be 10 kA.

The rated current of 450 kW/1000V induction motor it is about 320 A and at 3 times starting current [developing 25% of rated starting torque]it produces 15% voltage drop.

By reducing the load [including inertia of the motor and of the load] to a less than 25% one start could be done.

__________________
Julius
Register to Reply
Participant

Join Date: Apr 2019
Posts: 4
#11
In reply to #10

Re: Low Fault Level Effect on LRA and FLA

04/25/2019 9:14 AM

Hi All,

I have done a spreadsheet which I need to attach ( how does one do it on this site) to show that fault level at source plays a major part in starting large (450kW) motors on DOL. The kA rating at the motor supply transformer (10kA) will not help when the Intake supply is on 1.4kA it pulls the voltage down.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#12
In reply to #11

Re: Low Fault Level Effect on LRA and FLA

04/25/2019 12:58 PM

The only part missing is the short circuit available at the utility connection to make the calculation. You have provided all the other details, we assume your mining machine is a constant torque load with somewhat normal 150% or less breakaway torque and negligible inertia reflected back through the gearbox to the motor.

It would be helpful to know if this is a problem with new equipment, and whether you have similar installations that work ok under similar conditions. Or if this is a suspected cause of otherwise unexplained incidents.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #10

Re: Low Fault Level Effect on LRA and FLA

04/26/2019 6:36 AM

It needs to be noted that <...reducing the load [including inertia of the motor and of the load]...> has no effect on the <...LRA...> or the <...FLA...> as these remain features of the particular motor employed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#15
In reply to #14

Re: Low Fault Level Effect on LRA and FLA

04/26/2019 12:55 PM

Just the time spent at those current levels...

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#13

Re: Low Fault Level Effect on LRA and FLA

04/25/2019 1:51 PM

Sorry! I forgot to divide by √3 [1000/√3].So the short-circuit current it is only 6500 A. However, if the motor start current will be 6*Irated =1890 A then Zstartmotor=0.3 ohm and at start [s=1] the current will be 1460 A that means the torque could be 60% of the start rated torque. The voltage drop at the motor terminals it could be 226 V[=22.6 %].

__________________
Julius
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#16
In reply to #13

Re: Low Fault Level Effect on LRA and FLA

04/26/2019 1:01 PM

The OP states that the SC current is 1000A but gives no voltage reference or location? It is implied to be at the motor, which is possible, but appears to be improbable...

Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

7anoter4 (2); Anonymous Poster (1); JRaef (1); Padlock01 (3); PWSlack (4); rwilliams (5)

Previous in Forum: Parallel Connection   Next in Forum: Technical

Advertisement