330525 GAP VOLTAGE SETTING

10/14/2007 6:42 PM

Can anyone tell me what the gap voltage should be set to for Bently Nevada 330525 Velomitor XA probes ( used for vibration monitoriong of a pump ) going through a P&F barrier into a Bently Nevada 3500 system ?. I am at present working on a project in Russia and with the 10 hour time difference between here and the UK I am finding it difficult to speak to anyone in English regarding this. I have also tried to look for this info on the net to no avail all other aspects are covered apart from the gap voltage setting. WE HAVE A SUPPLY VOLTAGE OF -24vdc. Can I assume that the gap should be -12vdc which is the mid point of the supply voltage?.

__________________
BOUNTY HUNTERS ARE DANCING ALL AROUND ME.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Feb 2007
Location: AYRSHIRE SCOTLAND
Posts: 10
#1

Re: 330525 GAP VOLTAGE SETTING

10/14/2007 11:00 PM

OR DOES THIS MODEL OF VIBRATION SENSOR HAVE A GAP VOLTAGE AT ALL?

__________________
BOUNTY HUNTERS ARE DANCING ALL AROUND ME.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#2

Re: 330525 GAP VOLTAGE SETTING

10/15/2007 11:32 PM

Gap voltage is usually set at 9V with a plus or minus of 0.1. It doesn't have to be prefect as the vibrations give your change in indication.

Register to Reply
Anonymous Poster
#3

Re: 330525 GAP VOLTAGE SETTING

10/16/2007 12:19 AM

usually -10V for bently naveda 3500system. it may not be correct to take mid point because of linearity and mystem requiremnt. The -10V is arrived by leaving -2V both side.

Register to Reply
Anonymous Poster
#4

Re: 330525 GAP VOLTAGE SETTING

10/16/2007 9:47 AM

Hi Joseph

I am not sure what you mean by "Going through a P&F barrier?

But, the gap voltage is preferably -10VDC and the reason for this is as per below

1. The supply voltage is -24VDC and the usable linear voltage is between -2 and -18VDC

2. The above is based on the fact that the sensor output linear response is between -2 and -18. As you may be aware, the sensitivity of your sensor is 8mV/micronM.

3. The above mean that the gap voltage change of 1/1000mm or 1micron will give you 8mV DC gap.

4. Therefore, looking at our linear response of between -2 and -18V, one would like set ones neutral/zero position of the probe midway either side (sensor far or nearer to the shaft).

This point is - 10VDC.

Regards

Ephraim Tekete

Ass. Div. Engineer Condition Monitoring

Sappi Saiccor (Pty) Ltd (Reg.no.1989/001135/07)

Phone: +27 39 973 8199

Fax: +27 39 973 8805

Mobile: +27 83 236 1081

Mail: Ephraim.Tekete@sappi.com

Register to Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#5

Re: 330525 GAP VOLTAGE SETTING

10/17/2007 2:48 AM

Hi Joseph

For bently nevada 3500 system set the gap voltage at -7.5 to -10 vdc. but if you go towards -10 then you are at the end of the linear area and near the knee, as you go out the linearity drops rapidly. ideal is -7.5 where you are at around 35 mils and its the best spot to be on. You get pretty accurate values here.

regards

Naveen

Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#6
In reply to #5

Re: 330525 GAP VOLTAGE SETTING

10/28/2007 9:04 PM

Naveen,

I am not sure what model of probe you are using, but for most Bently probes, and for the 3300, systems -10VDC is the center of the range, and the linear range is typically from about -2.5 VDC to about -20 VDC.

A gap set for -9 to -10 VDC is fine for a radial probe. For a thrust probe you need to be careful how you set things up. Depending on how much float you have in the machine, a standard probe may not have enough range. We often zero on the active thrust shoe to accomodate range issues.

Register to Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#7
In reply to #6

Re: 330525 GAP VOLTAGE SETTING

10/29/2007 3:29 AM

Hello Steve..

Iam using 3300 NSv system. for centrifugal compressors and also for turbines.I also use other systems . I find good results at the gap volt of -7.5VDc to say -10Vdc, and with my observations i feel that -10.5 is the max you should go up and that you are on the knee.

regards

Naveen

Register to Reply
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#8
In reply to #7

Re: 330525 GAP VOLTAGE SETTING

10/29/2007 7:54 AM

I am sorry, I am still not sure what 'knee' you are talking about.

If you look at the bottom graph you can see that the prox output is linear from about -2 V to about -16V, if you graphed it out further you would find it is still linear to about -19 and then the curve starts to roll off.

Prox probes are designed to operate anywhere in this linear range. We typically try to gap in the middle of the range, about 45 to 50 mil and -9 to -10 VDC only so if there is a big vibration (on the order of 70 mil pp) that the output remains linear.

If you knew that you would never see a vibration over a couple mils pp, you could gap at say -3 VDC and see very little error. In fact the need for the linear range is not for radial probes, it is so radial and axial probes can be interchangable. Axial probes may well need every bit of eighty mils linear range.

Register to Reply
Anonymous Poster
#9

Re: 330525 GAP VOLTAGE SETTING

11/04/2009 5:52 AM

It should be installed such that gap voltage shows -10V DC while shaft is at rest.

Register to Reply
Anonymous Poster
#10

Re: 330525 GAP VOLTAGE SETTING

12/09/2010 11:37 PM

Is there any significance for the eddi current in the gap voltage setting?