Generator and Capacitor Questions: Parallel Connections

10/14/2007 10:02 PM

Friends,

Can we connect capacitor parallel to generator output?

Why generator manufacturing on pf 0.8?

__________________
KAKASAHEB TAMBE
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: GENERATOR -CAPACITOR

10/15/2007 5:07 AM
Register to Reply
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#2

Re: GENERATOR -CAPACITOR

10/15/2007 7:49 AM

If your generator has automatic voltage regulation then the power factor correction capacitor may interfere with the correct operation of this unit.

__________________
A day without a smile is a day lost
Register to Reply
Participant

Join Date: Oct 2007
Location: INDIA -MAHARASHTRA-PUNE
Posts: 2
#3
In reply to #2

Re: GENERATOR -CAPACITOR

10/15/2007 10:35 PM

DEAR

AUTOMATIC VLTG REGULATION IS AVAILABLE ON DG

THAT MEANS WE CAN INSTALL CAPACITOR

__________________
KAKASAHEB TAMBE
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#4
In reply to #3

Re: GENERATOR -CAPACITOR

10/16/2007 2:51 AM

If I understood the other poster correctly (Peterd), you should first check with the manufacturer of the regulator before using the cap.....it may interfere with the regulator's functioning in some way.......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Commentator

Join Date: Feb 2007
Posts: 60
#5

Re: Generator and Capacitor Questions: Parallel Connections

10/16/2007 6:52 AM

A direct connection of a capacitor on the generator output terminals will lead the later to self excitation, and thus over voltage.

For this reasons, it is always necessary to

a)intall at generator terminals a lightning arrester and a capacitor for the atenuation of overexcitation effects

b)provide the system with an overtvoltage protection. It will actuate if the voltage exceeds a certain value. It is important that further to open the breaker terminals it als actuates in the excitatin, not only disconnecting it, but also providing its de excitation

Regards

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#6

Re: Generator and Capacitor Questions: Parallel Connections

10/17/2007 5:44 PM

There is no good reason to connect a capacitor across the generator output, and plenty of reasons not to do so. Power Factor correction capacitors should be connected as near to the load as possible, to minimize the reactive current flowing through the power cables.

The pf rating of 0.8 on the generator does not mean that the generator always operates at that power factor, just as a generator rated at 500 KW does not always produce that much power. Since the manufacturer has no way of knowing what load the end user will connect to the generator, he designs the unit to a standard value. The power output, and the power factor, are determined by the connected load. The pf rating of 0.8 is the lowest power factor which the generator can supply and still produce rated KW.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Commentator

Join Date: Feb 2007
Posts: 60
#10
In reply to #6

Re: Generator and Capacitor Questions: Parallel Connections

10/18/2007 1:39 PM

You are almost right.

But in order to avoid voltage surges in large generators, it is used to apply a combination of a capacitor and a lightning arrester.

This is useful for surges of the switching nature.

Regards

Register to Reply
Power-User

Join Date: Aug 2006
Location: Central Florida in the good old US of A
Posts: 332
Good Answers: 2
#7

Re: Generator and Capacitor Questions: Parallel Connections

10/18/2007 8:03 AM

I was under the impression, that power factor correcting capacitors were to be installed near the inductive load, not at the power generating source.

__________________
Eschew obfuscation.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #7

Re: Generator and Capacitor Questions: Parallel Connections

10/18/2007 9:50 AM

That is the same as Post #6 said and I agree with you both!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Aug 2006
Location: Central Florida in the good old US of A
Posts: 332
Good Answers: 2
#9
In reply to #8

Re: Generator and Capacitor Questions: Parallel Connections

10/18/2007 12:48 PM

It's a terrible thing to get old!

__________________
Eschew obfuscation.
Register to Reply
Anonymous Poster
#11

Re: Generator and Capacitor Questions: Parallel Connections

02/15/2011 2:47 AM

Mr. Tambe,

As you know that the requirement of power is in terms of Active and reactive power both due to magnatization of transformers, few inductive part of transmission line and most of the inductive load, it is necessory to make generators on pf 0.8

Prof. P. M. Sonwane

CR4 Admin - email address removed

From the Site FAQ: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses. You can share this information via the CR4 internal messaging system.

Register to Reply