Reverse Power Protection

07/01/2019 8:49 PM

We have a 11KV to 415v utility power transformer and also 320kva genset and also we are making arrangements to connect the 20kw solar power system ( PV SOLAR HAS NO BATTERY). Now we providing LARSON AND TUBRO MAKE MRP11 reverse power relay at the transformer 415 v side, and the maximum load feeder one only lighting 7kw and feeder 2 vrv ac system 80 kw. My doubt is, is it rquired DG side REVERS power ptotection

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Reverse Power Protection

07/01/2019 10:35 PM

You must determine if in any situation that the current can reverse flow and overload a circuit...

..."In simplified terms a relay that operates with current flowing only in one direction and not the other. Ie, current flowing forward above the trip threshold will cause a trip, current flowing in the reverse direction above the tripping threshold will do nothing."..

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#2
In reply to #1

Re: Reverse Power Protection

07/02/2019 9:39 AM

Yeah, but I cringe when the video guy talks about current flowing the wrong direction instead of power.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: Reverse Power Protection

07/02/2019 12:43 PM

I know this falls short and is perhaps confusing as well, but it's the best one I came across...If you see something better feel free to post, or if you get particularly motivated you could make an informative video on this and/or related subjects...?...but no pressure...haha, I know you're so busy...like me....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#4
In reply to #3

Re: Reverse Power Protection

07/02/2019 2:47 PM

Hey, except for the Current/Power "nit", I thought it was very well explained, better than I could have done.

I especially liked the description of the workings of the Reverse Power relay, basically, a multiphase AC motor that turns backward and closes contacts if the current/voltage phase relationship indicates reverse power.

Register to Reply
Participant

Join Date: Feb 2010
Location: Manitoba, Canada
Posts: 1
#5
In reply to #2

Re: Reverse Power Protection

07/03/2019 8:45 AM

I'm going to show my ignorance here, but can you expand on that Rixter?

__________________
Ant Circles
Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#6
In reply to #5

Re: Reverse Power Protection

07/03/2019 2:17 PM

AC ... Alternating Current.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#7
In reply to #5

Re: Reverse Power Protection

07/03/2019 7:11 PM

In AC systems, current flows back and forth and voltage swings positive and negative. Power equals voltage times current. So power flows in the same direction that the current is flowing when the voltage is positive and opposite the current direction when the voltage is negative.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8

Re: Reverse Power Protection

07/08/2019 8:23 AM

You expect us to guess a lot.....

Transformer rating ??

Generation :- 320KVA Diesel Generator (DG) + 20 kW solar = 340 kVA

Loads : 7 kW lighting + 80 kW [vrv ac system ??]

Reverse Power Relay: switches or trips what?? or is it for DG?

Must suppose transfo is > 340 kVA rating exporting all generation.

Grid Operators usually have detailed requirements about protection to be met before generation connection is permitted.

Reverse power [Grid to DG direction] with DG shutdown & disconnect time delay of seconds would be usual, also disconnect & shutdown at loss of synchronism/Grid. Motoring a diesel engine is not a good idea - mechanically it will not do it harm short term but what if there is no power because all the fuel is pouring onto the floor?

Particularly, they do not want your gen keeping their line live if it disconnects at their end - it makes trouble for them to reconnect and danger for their workers and public e.g. line wire on ground.

According to usual standards, 20 kW Solar PV controllers must have auto shutdown if Grid is lost.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9

Re: Reverse Power Protection

07/08/2019 8:50 AM

To the Grid, your 87 kW load looks like "reverse" power - if generation [export] is normal.

DG may only take 40 kW when "motoring" [reverse power], so whole 415V monitoring cannot tell if DG is motoring or it is just normal loads.

I think the reverse power relay must trip off 415V breaker connecting DG to distribution board or transfo. Obviously, you want your load to be fed when DG is being maintained.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10

Re: Reverse Power Protection

07/08/2019 11:02 AM

This is local code ENA_EREC_G99 for connecting generators of <1 MW to mains (DNO = Distribution Network Operator). It is >300 pages, not all applies to particular type/size generator..

http://www.dcode.org.uk/assets/files/Qualifying%20Standards/ENA_EREC_G99_Issue%201_Amendment_4_(2019).pdf

Section 10 is protection, particularly.....

<<10.3.1 Suitable protection arrangements and settings will depend upon the particular Generator installation and the requirements of the DNO’s Distribution Network. These individual requirements shall be ascertained in discussions with the DNO. To achieve the objectives above, the protection shall include the detection of:  UnderVoltage (1 stage);  OverVoltage (2 stage);  UnderFrequency (2 stage);  OverFrequency (1 stage);  Loss of Mains (LoM).>>

Considering your circumstances, I do not think power direction relay is reliable way of detecting loss of mains LoM, but is advisable [monitoring generator current & voltage for power flow] to protect genset.

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (3); Adark (1); Rixter (3); SolarEagle (2); truth is not a compromise (1)