HT Motor Trips After Stop Command

07/01/2019 10:44 AM

We have single MV breaker with 10 kv motor, 560 kw FLA 41 AMPS (2 nos) for roller press application. Before stopping motor, the loads of motor is 17 amps each , it trips after giving stop command.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: HT Motor Trips After Stop Command

07/01/2019 11:14 AM

On what measurement does <...it trip...>, though?

What are the consequences of the <...trip...>?

These snippets, which have been withheld from the forum, are fundamental to the search for the solution(s)!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3
In reply to #1

Re: HT Motor Trips After Stop Command

07/01/2019 1:36 PM

It trips on the rug.

What? Did you really expect something useful from nothing presented?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #3

Re: HT Motor Trips After Stop Command

07/02/2019 7:54 AM

It's the best that can be done with only two sentences. Not much of a story, is it (rhetorical question - NNTR)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: HT Motor Trips After Stop Command

07/01/2019 11:18 AM

Sounds like a short in the switch....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4
In reply to #2

Re: HT Motor Trips After Stop Command

07/01/2019 1:55 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Associate

Join Date: Jun 2019
Posts: 50
Good Answers: 1
#13
In reply to #2

Re: HT Motor Trips After Stop Command

07/09/2019 8:37 AM
Register to Reply
Associate

Join Date: Jun 2019
Posts: 50
Good Answers: 1
#14
In reply to #2

Re: HT Motor Trips After Stop Command

07/09/2019 8:40 AM

CR4 Admin: removed link to virus-infected site

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#15
In reply to #14

Re: HT Motor Trips After Stop Command

07/11/2019 2:59 PM

WARNING!!!

LINKS IN THE ABOVE POSTS GO TO A VIRUS INFECTED SITE.

DO NOT CLICK ON THEM!

REPORTED TO ADMINS.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 806
Good Answers: 65
#5

Re: HT Motor Trips After Stop Command

07/02/2019 3:36 AM

It could be that one phase is opening before the others or two phases are hanging up and causing the motor to be single phased thus causing the trip.

Check your contactor.

__________________
Hare today, goon tomorrow!
Register to Reply
Member
India - Member - New Member

Join Date: Jun 2008
Posts: 7
#8
In reply to #5

Re: HT Motor Trips After Stop Command

07/02/2019 11:45 AM

Hi

Thanks for ur reply.

It is a ABB vd4 11kv breaker, its not contactor

Thanks

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #8

Re: HT Motor Trips After Stop Command

07/02/2019 1:02 PM

The smallest trip current I can find for this breaker is 630A. I would be nervous using a circuit protection breaker an order of magnitude greater than the anticipated full load. You are not presenting us with a full picture of your situation. Is this breaker that trips also providing power for other loads?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7

Re: HT Motor Trips After Stop Command

07/02/2019 11:38 AM

Hope Stop command is not wired in Trip relay circuit!!

__________________
Raghunath
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#10

Re: HT Motor Trips After Stop Command

07/03/2019 9:31 AM

Are the rollers nipped when the stop command is issued?

Is there a variable frequency drive between the breaker and the motor?

The motor protective relay that trips the breaker should give you an indication of the type of fault, some code will show up on the display

Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#11

Re: HT Motor Trips After Stop Command

07/05/2019 2:36 PM

Your motor circuit must have exceeded the safe parameters of your MV breaker.

Check your motor starting method used as well as the rated amperage of your MV breaker if it is well rated for the job and adjust your parameters where necessary.

You can use a suitable rated "soft starter" to start and stop the motor with a proper stop ramp time setting to achieve a "soft stopping" of the motor and your MV breaker will not trip if well rated. The stop ramp is the time from full voltage until stop voltage (initial voltage) is reached. If you set your stop ramp time to zero, the stop will be like a direct stop, and you will experience the same tripping of the MV breaker.

The thyristors in the soft starter implements the soft start and soft stop of the motor by gradually increasing and reducing the motor voltage according to a set ramp time for the soft starting and soft stopping of the motor.

__________________
Patrick Whowha
Register to Reply Score 1 for Off Topic
Associate

Join Date: Jun 2019
Posts: 50
Good Answers: 1
#12
In reply to #11

Re: HT Motor Trips After Stop Command

07/09/2019 8:35 AM

The stopping method can be changed from "coast to stop" to ramp down stop. The deceleration time must be set properly to avoid the regeneration. The coast to stop or faster deceleration of the motor may cause motor to work as a generator. The motor starts feeding its kinetic energy, converting into electrical, in the capacitor bank of the converter of the VFD. The voltage across the capacitor may reach above the over voltage limit and the drive may trip with over voltage fault.

Read More:https://sdvelectrical.blogspot.com/2018/11/dynamic-braking-of-motor.html