Enquiry About Distribution Transformer

08/03/2019 11:56 PM

Our 2.6MVA rated to 22000/400V s currently set to tap 4 (i.e output voltage of 410V).

When we measure the voltage at the secondary side, the voltage is fluctuating between 405V -417V.

Any reason for having a fluctuating output votlage ?

Also, what happens if our off load tap changer is not tighten properly or the tap changer for each phase is not at the same tap ?

__________________
There is no limit towards how much one can learn.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Enquiry About Distribution Transformer

08/04/2019 2:54 PM

The incoming voltage could be fluctuating for any number of reasons causing the secondary to mimic, also you could have a loose tap or wiring connection...You do not state if this under load, what type of load, or no load...

Taps can be adjusted to match more closely the voltage desired if the output of transformer does not match the voltage present...

https://electrical-engineering-portal.com/using-tap-changers-to-match-the-system-voltage

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#2

Re: Enquiry About Distribution Transformer

08/04/2019 2:55 PM

What is the frequency of these fluctuations?

Is the load connected when you see these fluctuations?

Is field wire connected?Have you measured load current during these fluctuations?

Have you HI-Pot tested the transformer primary and secondary,as well as all connected wiring and loads?

Loose connections will obviously result in a spurious output,and not having the taps in the proper places will usually result in a different output voltage than desired or an overload situation.

Insulation breakdown can cause voltage fluctuations,but at these voltage levels,it is usually very evident;Follow the flash and smoke.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: Enquiry About Distribution Transformer

08/04/2019 10:28 PM

Check whether fluctuation in some other tap, if it is there, check incoming voltage, if not check tap changer contacts and it’s wiring for any loose connection

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 809
Good Answers: 65
#4

Re: Enquiry About Distribution Transformer

08/04/2019 11:17 PM

Are you measuring the output voltage with a true RMS meter or a moving iron meter?

A digital meter can be subject to external influences like RF etc so an old style moving iron meter is less subject to HF influences. Fluke sell an excellent snubber to connect between the meter terminals and to the device under test which supplies a load to deaden fluctuations.

As for the tap changer not having all phases connected to the same tap then you will have circulating currents in the windings heating the coils and likely failure will happen sooner. The only way a tap changer can get out of sync is if the shaft between the switches is broken and then you have BIG problems.

If the tap switch is not making then you will have arcing and the production of gas from the breakdown of oil but if you listen on the tank then you will certainly hear it burbling. The arcing will also generate RF.

I used to repair and test transformers for nearly 20 years back in the dark ages.

__________________
Hare today, goon tomorrow!
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#5

Re: Enquiry About Distribution Transformer

08/06/2019 3:12 PM

Distribution transformers are designed for a maximum load current, about 3700 amperes per phase [3 phases, 400V side] in your case.

The transformer is designed so voltage falls typically 4% between zero current and maximum current with uniform loading. The voltage at the high-voltage input of the transformer is closely regulated by the supply company.

Most load equipment can operate with +/- 10% voltage fluctuation without harm - fluctuations in light from lamps is most noticeable effect.

The users on your transformer turn their loads on-off when required - so the load is always fluctuating.

417volts/405 volts = 1.030 , say 3% variation.

Possibly the load is never zero or maximum within time-span of your measurement.

The fluctuation you see is what would be expected due to load variation.

Since you gave no indication of the interval between your readings or the load current or if they were one phase alone or maximum- minimum of three phases; no further comment is worthwhile.

Off-load tap changer will put all phases on same tap - since it is not operated on-load, it cannot cause variations.

A faulty mechanical linkage is unlikely - do you have reason to think taps have been changed since installation??

Loose electrical connections would cause overheating and operation of a gas warning relay on an oil-filled transfo of this size. You have not written if transfo is "dry" or oil-filled.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6

Re: Enquiry About Distribution Transformer

08/07/2019 1:17 AM

I agree with 67model.

This is possible since the voltage drop from no-load to full load will be 14.6 V

According to IEC 60076-5 Table 1 – Recognized minimum values of short-circuit impedance for transformers with two separate windings-for 2 501 to 6 300 kVA the minimum short-circuit impedance is 6%.

The rated current [low voltage] In=2600/0.4/sqrt(3)=3753 A

The voltage drop at rated current and 0.85 power factor will be:

DV=sqrt(3)*In*(R*cosfi+X*sinfi)

[usual X/R for this transformer is 10].

The transformer impedance Z=0.4^2/2.6*6/100=0.00369 ohm

X=0.003674 and R=0.000367 ohm.

DV=sqrt(3)*3753*(0.000367*0.85+0.003674*0.527)=14.6 V.

So, in order to produce 400 V [at tap 3] the no-load voltage has to be 414.6 V

On tap 4 it has to be 2.5% more: 400*(1+2.5/100)=410 V at full load and 424.6 at no load.

All this in case the high voltage will be 22 kV.

If the tap no. is now 4 -instead of 3 where it has to be 22/400 V- that means the high voltage was less.

Let's say at full load you have 405 V instead of 410 V and instead of 22 kV you have 405/410*22=21.73 kV

At no load the low voltage terminal voltage will be 405+14.6=419.6 V.

__________________
Julius
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Enquiry About Distribution Transformer

08/07/2019 6:22 AM

<...voltage is fluctuating between 405V -417V...>

Actually, it <...is fluctuating...> from -417V to +417V.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8
In reply to #7

Re: Enquiry About Distribution Transformer

08/07/2019 10:13 AM

Of course, you're right. It happens 50 times in a second.

__________________
Julius
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Enquiry About Distribution Transformer

08/07/2019 10:51 AM

A <...fluctuating output voltage...> is to be expected, as this indicates the changes in load elsewhere on the distribution system as users switch onto and switch off it.

If <...the tap changer for each phase is not at the same tap...> then one might expect different voltages between phase and neutral on each phase. One might expect this with a range of single phase users on the distribution system anyway.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!