How to set HF Transformer NWL

08/15/2019 3:52 AM

Does someone has experience in setting the parameters of an HF Transformer of the make NWL USA (Nothelfer Winding Laboratories)installed on an electrostatic precipitator for a boiler coal/bagasse?
We have just installed one. It is not working well on bagasse as there is lot of smoke coming out of the stack.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: How to set HF Transformer NWL

08/15/2019 5:21 AM

The chances of someone from <...Nothelfer Winding Laboratories...> responding to the original post are remote-to-negligible!

The <...We...> needs to telephone <...Nothelfer Winding Laboratories...> directly and obtain advice "straight from the horse's mouth", and not wait around on CR4 on the off-chance that someone, somewhere, might be tempted enough to respond.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Participant

Join Date: Oct 2018
Posts: 4
#2
In reply to #1

Re: How to set HF Transformer NWL

08/15/2019 7:19 AM

I have already contacted them & got some help. We had some improvements. We still have smokes coming out of our stack on bagasse. The NWL guy works in an office & usually does not have field experience. Other persons working in a power plant who have encountered similar problems with HF transformer on bagasse may help.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: How to set HF Transformer NWL

08/15/2019 7:25 AM

So is that the end of the matter (rhetorical question - NNTR)?

Get back onto the supplier and seek further help until the issue is rectified. Become their pest! If necessary, obtain a site visit from someone there that can help!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: How to set HF Transformer NWL

08/15/2019 11:59 AM

You are only chipping at the smallest piece of the iceberg...

https://www.thermalenergysystems.com/issct10.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#5

Re: How to set HF Transformer NWL

08/16/2019 7:40 AM

Check the condition of the bags.Check the differential pressure across the bags.They may be clogged by fine particulates.Perform a thorough examination of the bag material.Holes in the fabric can allow unfiltered gas to escape.This would normally show up as a decrease in differential pressure,but if the bag media is clogged,the differential in pressure may not be noticeable.Check the condition/adjustment of the forced draft and induced draft fans and check the chemical composition of the stack gases.You may be running with insufficient air.

The excessive smoke is not caused by the NWL,it may simply be overloaded.A well designed,properly sized and installed static precipitator can replace bag house filters and require less maintenance and cost.A bag house requires about six times the energy to pull the gases through the filter media.

Some applications and areas do not allow only Electrostatic participators,so check with the local authorities.

When you call Nothelfer Winding Laboratories again, be a "squeaky wheel",pester them,nag them until you finally get results.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Participant

Join Date: Oct 2018
Posts: 4
#6
In reply to #5

Re: How to set HF Transformer NWL

08/16/2019 8:22 AM

Our ESP is not a bag filter. It consists of metal electrodes. It has 3 fields which are energised by transformers. Operating voltage is around 50 kV 500 mA. We have 2 sets of turbo-alternators, boilers & ESPs. ESP 1 is working quite well on both coal & bagasse. ESP 2 is working well on coal but there is lot of smoke on bagasse.

In June we did our annual maintenance. We repaired some holes in the ESP casing, replace the roof, repare holes in the economizer hopper just before the ESP. We replaced the transformer on field 1 with an HF Transformer NWL. This has a higher kVA and is the latest technology and is supposed to collect more ash.

The problem is that the company who did maintenance on our ESP, installed the HF transformer. They purchased it from another company not directly from NWL. We managed to get a contact from NWL on the website who helped us. We got some improvement. But still we have smoke from our stake. So NWL has not obligation towards us.

We have fine tuned the rapping times of the collecting & discharge plates. May be there is still some improvement to do here.

I will like to know if I can increase my kV & mA on the HF transformer on manual mode. Now on bagasse, it is 48 kV and 676 mA .

When there is collecting plate rapping on field 1, there is a peak in opacity. I need to solve this issue.

The rapping times are as follows:

Field 1Field 2Field 3
OnOffOnOffOnOff
Emissif/ DE2hr30s2hr30s2hr30s
Collectrice/CE15s2m22s7m12s20m
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #6

Re: How to set HF Transformer NWL

08/16/2019 11:11 AM

It would seem that the airflow must be adjusted between coal and bagasse, either increased or decreased...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#8
In reply to #6

Re: How to set HF Transformer NWL

08/18/2019 10:03 PM

Your flue gas velocity may be too high to charge the particulate in time, which is likely much finer and perhaps more conductive than the original design. Your burner settings and design could be different enough between the 2 boilers to require a different design, or burner operation is not as it was before, secondary air mixing, combustion zone temperatures. The intensity of rapping may be dislodging the particulate rather than allowing it to slip down, especially if lighter and/or finer.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

HiTekRedNek (1); PWSlack (2); Randhir1 (2); rwilliams (1); SolarEagle (2)