Generator Synchronization Problem

08/15/2019 6:31 AM

Hi everyone..

We have 3 generators in the plant.

During our operation when we start Genset 1 it will run in normal operation. Then when we start Genset 2, the two genset will synchronized and operate in normally. The problem is, when we start genset 3 and synchronize to the 2 genset, Genset 1 will trip by Loss Of Field. The same problem when we start first Genset 2 and Genset 3, in will synchronize normally but if we start Genset 1 and trying to synchronize with Genset 2 and Genset 3. it will trip and the tripping is the same Loss of Field.

What is possible problem and solution for this scenerio.

Thank you.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#1

Re: Generator Synchronization Problem

08/15/2019 7:46 AM

Not my field, but what happens when you start #1 and then try to start and synch #3?

Both fault scenarios that you describe involve trying to sync #1 and #3. There may be a cable fault or similar in that set of connections.

As I said earlier, not my field, just a guess!

__________________
Just an Engineer from the land down under.
Reply
Participant

Join Date: Aug 2019
Posts: 2
#2
In reply to #1

Re: Generator Synchronization Problem

08/15/2019 8:11 AM

When we synch #1 & #2, no problem but if synch #3, #1 will trip loss of field relay,

If synch only #1 & #2, #2 & #3 or #1 & #3, no problem in synch. The problem is when synch the 3 generator #1 will trip because of Loss of Field, every time we synch the 3 generator

Reply
4
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#5
In reply to #2

Re: Generator Synchronization Problem

08/15/2019 3:46 PM

Did generator trip instantly on breaker close, or after a delay?

Posts suggesting you might have generator switched [or set] to minimum voltage droop are valid.

The important points are that to raise voltage, excitation must increase; to reduce voltage, excitation must be reduced.

If the voltage regulator thinks the line voltage is high relative to its own setting it will reduce excitation. If the volts do not drop enough, it can reduce field current below the value which gives open-circuit voltage equal to line and absorb current from the other machines to drop volts, even go to low excitation current which is seen as a trip event by a monitor, usually with a delay.

Unless trip occurs instantly, it should be noticeable that the problem gen has leading power factor or Vars of opposite sign to other machines, while others show a normal lagging load current. From here we cannot see what instruments you have.

The capability of a gen in leading power factor is about 1/3 of lagging capacity [at zero excitation current]- it might be enough to force volts down when load requires just two machines, but not when load needs 3 machines.

It appears it is always No.1 which trips.

  1. The voltage setting of No.1 could be low relative to other units - the simplest technique, when breaker connects to line, is to set all generators to same unloaded voltage and for all to have same droop to share load.
  2. There could be a fault in the switching or measuring circuitry which puts the gen into droop & raises its volt setting when its breaker closes causing insufficient droop. The measurement usually comes from a current transformer, which could even have been shorted-out during maintenance, but not restored after. There are other techniques than droop to keep electrical load shared.
  3. Some sharing system other than droop could have a problem at the No.1 point, even that an "on-line" contact at this point is faulty.

67model

Reply Good Answer (Score 4)
Guru

Join Date: Jul 2012
Location: Madison, WI.
Posts: 2074
Good Answers: 77
#10
In reply to #5

Re: Generator Synchronization Problem

08/16/2019 10:03 AM

Sounds like you may want to check your switch gear for ground faults.

__________________
Knowing is the end result of learning, not believing.
Reply
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9912
Good Answers: 1141
#3

Re: Generator Synchronization Problem

08/15/2019 8:53 AM

This is just a wild guess...

The governors of the machines can be either set to isochronous or droop. Isochronous maintains a constant frequency whereas droop allows the generator to slow down under load. The same situation goes for voltage regulators. Droop allows the generator to share the reactive current.

Governor in non-droop mode:

Governor in droop mode:

Voltage regulator in non-droop mode:

Voltage regulator in droop mode:

When you parallel generators, one and only one should be in isochronous or non-droop mode, the master which controls voltage and frequency. If both #1 and #3 are set in isochronous or non-droop mode, you might well see what you are experiencing.

https://www.svri.nl/en/isochronous-vs-droop-control-for-generators/

Reply Good Answer (Score 2)
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#4

Re: Generator Synchronization Problem

08/15/2019 2:16 PM

https://cr4.globalspec.com/thread/69707/Droop-of-a-Generator

Vinu_Answers has a good response in the above thread.

Reply Score 1 for Good Answer
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#6

Re: Generator Synchronization Problem

08/15/2019 10:53 PM

Suggestion only: Google reactive load of transmission lines.

Reply Score 1 for Off Topic
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#7

Re: Generator Synchronization Problem

08/16/2019 3:57 AM

Are the generators the same size? Does 'size' matter?

Is the 3rd generator brought in because he first 2 are on full load? , or are all three brought online before the load is applied?

__________________
When arguing, remember mud-slinging = lost ground.
Reply
Participant

Join Date: Aug 2019
Posts: 2
#8

Re: Generator Synchronization Problem

08/16/2019 5:56 AM

They are the same capacity 6MW, they operate only during power interruption of the Utility. The question is, why Genset 1 will trip after it is synchronize to other 2 generator, it only operates normally if we use only 2 generator. For example, if we synchronize Genset #1 and Genset #2 or Genset #1 and Genset #3 it operates normally, problem occurs when we synchronize the 3 generator, Generator #1 will trip after we synchronized with 2 others with some delay not instantly. The cause of tripping is "Loss Of Field". Why it is only Genset #1 having problem. The two others operate normally.

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9
In reply to #8

Re: Generator Synchronization Problem

08/16/2019 9:58 AM

I take it you have read posts #3, #4, #5??

It seems you agree that the problem is with Genset #1.

You have answered the post that asked if generators were all same size.

It is most possible the voltage regulator on Genset #1 has a fault, but it could be that it has a "wrong" selection from the plant control, even a "breaker closed" contact not working. It might be that Genset #1 "Loss of Field" protection is set wrong or has a fault.

Since #1 is able to synchronise and connect it is unlikely that "Loss of Field" protection which checks actual field current is faulty - it could be saying FAULT but its contact is disconnected from trip relay until Genset #1 is on-line. A look at the circuit diagram for "Trips" might find an "arming" contact [e.g. Generator to Line breaker auxiliary contact or "Breaker Closed" relay contact] in series with "Loss of Field".

However, Genset #1 would operate normally (same as other units when they start & load) before trip.

Normally, a generator will take some current & MW as soon as it connects - synchronisers do not have to be perfect. Power factor could be lead or lag and MW positive or negative. The governor will be given a raise demand at connection & MW will ramp up.

If the generator field current stayed constant, the power factor meter would indicate a falling leading power factor as MW increased until the generator loses synchronism with parallel gensets at much less than full MW.

In a historic system, the operator would increase the field current as MW increased, field current at full MW would be several times that to synchronise.

When 3 phase & Automatic Voltage Regulator [AVR] became common, it was realised that a current transformer could be made to put a voltage in series with voltage sensed by AVR, so that a leading power factor current reduced voltage to AVR proportionally, making it increase field current. If the volts setting was not altered, full MW would be got at high leading power factor.

With that in mind, some questions.....

  1. What are the MW and Power Factor [cosφ] meters on Genset #1 reading at time intervals after connection & before/at trip? How do readings compare with "OK" gensets.
  2. If you have an "Excitation Current/Field Current" meter, what does it read just before connection & how does it change after? What do the same meters on "good" sets read for each MW load up to full load for comparison?
  3. Can you operate in a "manual" mode, with Genset #1 governor and AVR settings made by operator using switches/buttons to Raise or Lower? This could bypass a defective load sharing system.
  4. Does your AVR have an MVR or excitation current regulator selection for testing? This could avoid faulty AVR parts & show Genset #1 can work without "Loss of Field".
  5. What is the usual power factor of your load [on two Gensets?] and its MW when you are making tests for this problem?
  6. What make and type are your AVRs? It may be possible to get data & suggest which modules can be swapped from genset to genset to see "if problem moves with module XX".

67model

Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#11
In reply to #9

Re: Generator Synchronization Problem

08/16/2019 10:14 AM

Another question...

7. Is the "Loss of Field" detection <a relay on a "Generator Protection Panel">?

If it is, they are often in a glass front case or rack and can be unplugged to swap them from Genset to Genset.

67model

Reply
Reply to Forum Thread 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (3); Brave Sir Robin (1); Hendrix Leva (2); horace40 (1); jdretired (1); Just an Engineer (1); rashavarek (1); Rixter (1)