Criteria for stopping cooling tower fans

10/18/2007 2:16 AM

We have a cooling tower containing 12 cells and each cell has one fan. We have lower limit of 27.7C on the CW outlet temperature. When we reach this temperature, we have to stop 1 fan and if required more than 1 fan. We don't have any system or sequence of which fan to stop. Can some one guide me what should be the basis of establishing some sequence for this purpose?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#1

Re: Criteria for stopping cooling tower fans

10/18/2007 3:41 AM

Trial and error I think, never had to do it myself. Off hand can't think of any problems, unless you would like to highlight some? The only thing I can think of is restarting a fan, local inspection should indicate how fast a fan is running in reverse, experience should then guide you as to whether it trips on overload when restarting. This would possible suggest fans on the ends. But you will need to check.

Regards JD.

Register to Reply
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#8
In reply to #1

Re: Criteria for stopping cooling tower fans

10/18/2007 11:12 PM

I think CW refers to COLD WATER, as opposed to chilled water from the condenser, rather than a clockwise rotation you might be more familiar with.

Rich

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply
Participant

Join Date: Oct 2007
Posts: 4
#2

Re: Criteria for stopping cooling tower fans

10/18/2007 5:15 AM

Thanks JDRETIRED for your reply. I meant to ask about some basis of selecting which fan to stop first, which second, third and so on. The cells are numbered A,B,C,D,E,F,G,H,I,J,K,L and 6 cells (A to F) are in one concrete block and remaining 6 on another. If we stop for example A, B this means 4 cells are operational on first block and 6 on another. Will it make a difference in draft conditions, evaporation rate etc?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Criteria for stopping cooling tower fans

10/18/2007 6:11 AM

<Will it make a difference in draft conditions, evaporation rate etc?>

It certainly will. Evaporation in the cells switched off will be much lower.

Why is there a bottom limit of 27.7degC? What happens to the processes connected to the tower when the local wet-bulb temperature drops lower than this figure?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Brecksville, OH
Posts: 1621
Good Answers: 18
#7
In reply to #3

Re: Criteria for stopping cooling tower fans

10/18/2007 11:08 PM

Given your above statement and assuming that the tower water is corrected to the same headers in both sumps, wouldnt it be advisable to shut off one fan in each group, preferrably in the central portion of each sump to reduce end effects?

__________________
"Consensus Science got us into this mess, then why can't it get us out?" : Rephrase of Will Rogers Comment
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #7

Re: Criteria for stopping cooling tower fans

10/19/2007 3:35 AM

Good advice for the original poster.

27.7degC does seem unusually high, and unusually concise, for the lower-end temperature for a cooling tower. Usually the cooling loop approaches, or achieves at periods of low demand for 'coolth', the local wet-bulb temperature, so the tower is probaby located in low latitudes. Switching off a fan, or a group of fans, would mean that the cooling circuit won't be doing as much cooling as it could. Why is this under consideration (rhetorical question)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Oct 2007
Posts: 4
#15
In reply to #14

Re: Criteria for stopping cooling tower fans

10/19/2007 8:08 AM

27.7 degree entigrade is our design tempertaure for condenser back pressure of 65 mm of Hg. This corresponds to about 8% wetness in the steam at the last stage of the LP turbine, but if we allow the CW outlet temperature to go down below 27.7, wetness will increase which will damage the last stage blades.

Register to Reply
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#18
In reply to #15

Re: Criteria for stopping cooling tower fans

10/19/2007 8:33 AM

The easier control then would be variable pump output. Probably much more responsive to have a 2 or 3 degree throttling range, maybe even on the hot side of the turbine, to improve the operation automatically. Either a throttling valve on the pump output, or a variable speed drive for the pump. Probably a lot cheaper to have a throttling valve near the pump, (less high pressure line). Hydraulic, pneumatic, stepper or voice coil control is a relatively cheap installation. Coil control is probably the more expensive to operate and highest failure rate, especially for a large system. You also might find that with better control, the equivalent of 30 degree water might be more efficient. Your steam dryness is based on the output temp of the hot water, and the quicker response of direct control may allow for safer, lower cost operation, without worrying about whether a fan is off or not.

Regulate your flow at the demand to regulate your steam chilling (Why?), and you could improve your efficiency and operational safety. Then you don't nrrd to disturb the engineers nap.

Rich

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#19
In reply to #15

Re: Criteria for stopping cooling tower fans

10/19/2007 9:03 AM

Yes makes sense now, Inspection of the stopped fan/s and your own personal experience I think will guide you to make the right decision.

Regards JD.

Register to Reply
Participant

Join Date: Oct 2007
Posts: 4
#20
In reply to #19

Re: Criteria for stopping cooling tower fans

10/23/2007 12:50 AM

Thank you all for your good comments. Yes need for maintenance of fans will I think will be good basis for selection of fans. Also experience will guide us better.

Register to Reply
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#17
In reply to #7

Re: Criteria for stopping cooling tower fans

10/19/2007 8:17 AM

The updraft of proximate fans will combine and be more efficient than distant updrafts.

Rich

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#4

Re: Criteria for stopping cooling tower fans

10/18/2007 7:05 AM

The lower limit of 27.7C seems a bit of a challenge, I assume it to be tied up with efficiency, cost of cooling against load gain? Does this occur on load reduction, or is it hot well temp effecting the feed heaters? or some thing else? Yes it will effect evaporation, but why is that important in regarding to the final outlet temp? Is there a problem with make up water supply, leading to chemical and sludge problems?

Regards JD.

Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#6
In reply to #4

Re: Criteria for stopping cooling tower fans

10/18/2007 5:34 PM

Giving a bit more thought to the 27.7c limit. I was wondering if a miss interpretation has occurred? Cooling fans take a heavy load when starting, and a temp of 27.7C may be necessary before starting to prevent the fans tripping on overload due to cold dense air? This then would only be a starting criteria and would not apply to having to stop them? Is this a large unit or are the fans common to a group of smaller uints.

Regards JD.

Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#9
In reply to #6

Re: Criteria for stopping cooling tower fans

10/18/2007 11:24 PM

Sorry looked at post again, I had assumed power house operation. Which would put the lower temp requirements into a different light.

Regards JD.

Register to Reply
Power-User

Join Date: Jun 2006
Location: Central America
Posts: 227
Good Answers: 1
#5

Re: Criteria for stopping cooling tower fans

10/18/2007 10:19 AM

If your maintenance strategy is fixed-time maintenance you can use run time as the basis of selecting which motor to take off line first. In this case you´d want to wear out your motors more or less evenly. It will require a modest investment on a PLC, wiring, and programming the logic.

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#10

Re: Criteria for stopping cooling tower fans

10/18/2007 11:34 PM

Typically, multi-tower arrays are usually parallel operation, hot water to all towers through a manifold, cold return through a common return line. Shutting down one fan still leaves the hot water running through a tower, resulting in a n influx of hot, probably over 35° water mixing with your cold water, if you try to maintain 27, shutting down one fan out of four suddenly boosts your cold temp to 29. On/off cycles are going to be excessive, wasteful, and wearing. Are the motors 3Φ or single? Varying fan speed would generally be a better bet, un;ess you can shut down the water through a tower at the same time. That depends on whether or not 2 or 3 towers can supply enough water to your pumps.

Do all 8 towers supply a single chiller?If you are saving 5 kw shutting down one fan, a 1° lower cold side temp probably saves you 100 kw at the condenser. Try reading the electrical load of your condenser with a 27.7 CW, and then do the same with 26.7 CW. You might find that turning of a fan is a very costly thing to do, besides the added maintenance from start/stop cycles. And, you really don't save any water, if that is the concern, because hoter water evaporates more water than coole, and any water evaporating is contributing 1000 BTU/lb for it's evaporation, whereever it is occuring.

I really think shutting your fans down is a false economy of a non-engineer.

Rich

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply
Anonymous Poster
#11

Re: Criteria for stopping cooling tower fans

10/19/2007 12:02 AM

It is a problem related to ambient temperature. Please specify ambient temperature.

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#12
In reply to #11

Re: Criteria for stopping cooling tower fans

10/19/2007 12:06 AM

Probably more related to the ambient dew point than the temperature.

Rich

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings
Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#13

Re: Criteria for stopping cooling tower fans

10/19/2007 12:24 AM

I had assumed a large cooling tower, but if it is a small aux, then there is one other consideration. In the power station we had a small cooling tower for the H2 plant, the policy was to shut down a single fan as H2 plant operation required, the result was that the idle fan bearings all became pitted due to vibration, and the policy had to be reviewed. Just thought I'd mention it in passing. My neighbour who has extensive experiance with chillers and associated cooling towers is away, roaming the outback of Australia, so I will keep an eye on the post.

Regards JD.

Register to Reply
Power-User

Join Date: Dec 2006
Location: Bolingbrook Illinois, a southwest suburb of Chicago.
Posts: 367
Good Answers: 3
#16

Re: Criteria for stopping cooling tower fans

10/19/2007 8:15 AM

Is it possible thast your chiller (not the towers) are giving the 27.5 as design temperature for the rated output of the chiller? If that's the case, any lower cooling water temperature will increase the efficiency AND the output of the chiller, which should be substantially lower cost to run either centrifugal or piston compressors. The fan coil units, or process, will stop warming the chilled water if the temperature is below a set-point (thermostat setting) and your chilled water loop temperature will drop, dropping the hot water temp to the towers. The cooler water will not evaporate as much water as the ΔT to dewpoint is less. If you have let's say a 1000 kw chiller, the electrical draw at a cold water temp of 27.5 and a chilled water temp of 10, would be say 1300 A. If the cold water temp drops to 25, I'd guess the draw on the compressor would drop to 1100 A, and if the chilled water temp drops to 9 because of low use, the compressor would shut down, until the water out reached say 12. That would be 0 amps for a bit. Presuming a 5 kw fan, shutting down 1 fan @ 10 A would need to be off for 130 minutes to save the same as 1 minute of compressor off cycle. The compressor is chilled gas cooled, and will not suffer from short cycles, and are a really rare failure item with proper care.

I realize you probably have a pair of compressors, maybe one for each bank of towers, and if the lag chiller is not needed, a whole bank of towers will shut down. A 20 min off-cycle of the lag towers would need 80 minutes of 1 fan off-cycled, without considering the 1100 of 1300 A saved by a chiller cycling off. Here's a thought, set a temp sensor in the tower sump, 1 for each motor, motor A off at sump temp of 20, b at 18, c at 16, d at 15 etc. Using the same lead fan and lag fan will end with a fried fan on the lead more often. You will have to change out that motor more often. Cycling through the fans as lead/lag would result in all of the fans needing replacement at about the same time. My preference would be repeatedly replacing the lead fan motor several times before the #3 fan motor needed to be replaced, too.

Your choice.

Rich

__________________
"People find it easier to forgive you for being wrong than for being right" J K Rawlings