We have had at our install base a dry transformer with the following specs :
1) Rating = 3MVA
Ratio : 22000/400V
Impedence = 8%
Connection : Dyn11
Design of Low voltage winding is expoxy cast resin while high voltage winding is VPI.
The transformer have been energized for 2 months with no load applied and having no problem.
Just recently, we loaded up the transformer to 2.5MVA for the first time for about 30-45 mins, and the transformer restricted earth fault protection trigger and trip the transformer.
After which, we realized that the bottom of one of the windings have been burnt and this has probably to cause the winding to be shorted to ground.
This is an extremely rare incident, to which we have no clue on what are the probable causes that could have cause this to happen.
My guess, is somehow, the heat generated during actual load application has somehow break down the insulation and cause the inter-turn fault between the windings and then somehow this puncture a hole through the epoxy and then short the windings to ground.
If this is the case, then are there any additional tests that we can conduct to capture this problem?
The transformer has gone through all the necessary IEC tests prior to energizing it
If anyone has encountered any similar cases , please share with me your findings.