Re: Equipment without certificates according to IEC standards
09/01/2019 3:46 PM
It's a big standard. Put really simply:
1) Industrial gear allowed if installed in Ex d flame proof enclosures (refer IEC 60079.1)
2) Simple apparatus (mechanical switches and read switches, etc - nothing with energy storage or conversion elements) protected by an intrinsic safety barrier or galvanic isolator located in the safe zone (non-hazardous area) or fitted into a suitable Ex rated enclosure if located in the hazardous area (refer IEC 60079.11)
3) Industrial gear allowed in Ex e rated enclosures under certain circumstances as long as it is installed in Zone 22 ONLY and all controls, windows, glands, etc penetrating Ex e enclosure are Ex rated also (refer IEC 60079.31)
There may be other exceptions for mechanical gear, etc that I have missed.
Re: Equipment without certificates according to IEC standards
09/01/2019 4:27 PM
Good answer. The technique of pressurisation, Ex p is also applicable to equipment like large motors which have sparking commutators or sliprings. Need for clean air supply & certified enclosure, monitoring & control system limits usefulness compared to Ex d but could be used for hydrogen & other risks Ex d cannot meet.
Re: Equipment Without Certificates According to IEC Standards
09/02/2019 7:53 AM
Referring to post #1, even a "simple" switch must be insulated for 500V [not sure if AC or DC, I think AC is correct] along with its cable/ terminals - using the "blue IS" terminals has its merits.
This is because e.g. a short to frame in an Ex d motor with earth cable CSA equal to live cable will raise frame of motor [and its skid] to 1/2 supply voltage to ground. A switch on its skid connected to earth at intrinsic safety barrier could spark to local metal if just, say, 12V rated.
There are also material limitations, which apply - magnesium or even some aluminium alloy enclosures could cause ignition if a steel hammer dropped on them.
Cadmium plating became the preferred corrosion treatment for parts of electric kit, but I remember a "panic" when it was discovered that spark ignition energy in an IS circuit was halved? compared to zinc plate on which limits were proven. Having a big safety factor between ignition & IS barrier limits was justified.
An earlier "system-shock" was the lid blowing off an overloaded Ex(d) junction box containing only terminals/cable in a mine. It turned out the terminal insulation decomposed & burnt with tracking & high temperature. Prior to that, it was accepted all sorts of kit could be put in Ex d enclosures without regard to material, quantity & fault level.
Re: Equipment Without Certificates According to IEC Standards
09/02/2019 3:38 PM
While the Ex d boxes are designed to handle the explosion inside pressure piling is a real problem and can easily cause the box to rupture if careful consideration to component placement and compartmentation is not considered.
Re: Equipment Without Certificates According to IEC Standards
09/02/2019 12:16 PM
It is all in the standard, which is there to be read and understood.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Re: Equipment Without Certificates According to IEC Standards
09/03/2019 4:25 AM
There is a page in Wikipedia with this information therein.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Ask for training in the safe use of electrical equipment in potentially explosive atmospheres. This is not a topic for the untrained.