09/03/2019 8:04 AM
is it possible to install NMR84 in hand dip hatch? if yes how can we do the manual dip
can it be install in still-pipe
Re: Endress & Hauser Raddar NMR84
09/03/2019 8:31 AM
A1) yes.
A2) That's a question for the Designer to answer, not CR4.
A3) yes.
09/03/2019 9:13 AM
<...Raddar...> Radar is used whenever the measurement is too difficult to carry out by most other techniques. The prospect of <...manual dip...> suggests that radar is overkill for the application.
Has the plant passed through a formal HazOp Study yet?
09/04/2019 5:11 AM
If the hand dip hatch is a true refection of the level to be measured.
The mount must be secure and free from vibration.
Yes,it can be mounted in a still-pipe,provided that it is of at least 100 mm diameter.
A still-pipe is one of the factory recommended mounting methods.
These devices are very reliable and require very little maintenance if properly installed according to the User Manual.
Here is a link in case the manual has been lost or misplaced:
https://portal.endress.com/wa001/dla/5001045/8424/000/00/TI01253GEN_0116.pdf
Reference page 15 for installation.
Good luck.
09/04/2019 8:59 AM
Thanks for replying
If the radar installed, hand dip will not be possible? its floating roof tank, my question any alternative or idea to make both of them possible
09/04/2019 10:41 AM
In the case of a floating roof,I would suggest securely mounting a 6" diameter pipe to the inside of the tank,extending to the bottom.
Cut the bottom of the pipe at a 45 Degree angle to allow the level inside of the pipe to be the same as the actual tank level.
Alternatively, a pressure transmitter mounted to the bottom of the tank,perhaps on an outlet flange.You will have to know the specific gravity of the liquid.You will need a method to transmit this data to a display terminal or computer.
Rosemount makes some good ones,such as the 305L level transmitter.
It is available with 4-20 mA HART®, WirelessHART®, FOUNDATION™ Fieldbus, PROFIBUS®, 1-5 V Low Power HART®
The company will be glad to answer all of your application questions.
Here is a link to their site.Select your country from the drop down menu.
https://www.emerson.com/en-us/automation/rosemount
Here is a link to a laser sensor for floating cover storage tanks:
https://www.azosensors.com/article.aspx?ArticleID=755
A laser monitor looks like the best option to me,but you will have to do your homework to decide which is best for your application.
Good Luck!
09/04/2019 11:58 AM
Why <...Raddar...>? Why not some other technique?
What is in the <...tank...>, its temperature and its pressure?
09/10/2019 5:53 AM
If gauging reference hight changed, Do I need to recalibrate the whole tank and establish new calibration table or not?
10/02/2019 4:13 PM
Yes, of course.