The transformers I had seen earlier used to come Nitrogen filled from the manufacturer and used to be oil filled at site. However, the transformer supplied to one of our project came oil filled up to the core level and the balance space was to be filled up with oil at site. There was a delay of about 5 years in commissioning the transformers. The pre-commissioning checks and testing are in progress. The Commissioning Engineer stated that the water content is higher than the permissible level and hence air drying and vacuum drying has to be carried out. The transformer oil has been drained out completely into another tank. The first cycle of dry air filling (24 hours) and vacuum drying (48 hours) has been completed and the second cycle is in progress. However, there is no appreciable reduction in the moisture content. The Commissioning Engineer stated that we may have to do 3 or4 cycles to reduce the moisture content.
What are the standard values of the dew point and RH value for a healthy transformer. Can we predict how many cycles are required to dry out the moisture content in the transformer. The transformer has to be urgently commissioned to start the other activities.