Motor Contribution to Earth Faults

10/17/2019 9:56 PM

Consider a delta/Wye 66kv/22kv transformer supplying a bus then from the bus a feeder supplying another delta/eye 22kv/6.6kv transformer. From this second transformer a bunch of DOL motors are powered.

The delta sides of the transformers are not earthed. The Wye sides are at their star points.

If an earth fault occurs between the two transformers, say on the bus, will motors contribute to the earth fault? My understanding is that motors will only contribute to phase-phase faults as the delta/Wye transformer supplying the motors is not earthed on the delta side?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Motor contribution to earth faults

10/17/2019 11:56 PM

I believe that is correct...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Motor contribution to earth faults

10/18/2019 3:03 AM

If <...an earth fault occurs between the two transformers...on the...22kv...bus...> then it is upstream of the motors. As the motors are isolated from the <...earth fault...> by the <...22kv/6.6kv transformer...>, they cannot contribute to the fault in themselves.

However, the fault will only persist for as long as the circuit protective device(s) take(s) to disconnect it; at that point, the motors lose power and stop.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6216
Good Answers: 248
#3

Re: Motor Contribution to Earth Faults

10/18/2019 10:47 PM

"Consider a delta/Wye 66kv/22kv transformer supplying a bus then from the bus a feeder supplying another delta/eye 22kv/6.6kv transformer."

As I read this, the output of the first transformer is a Wye connection, and the input of the second transformer is a Delta connection. Is that correct?

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Motor Contribution to Earth Faults

10/21/2019 2:15 AM

If all 3 phases are short-circuited then no supply voltage and the EMF in stator windings are from the rotating remaining magnetic field in rotor up to demagnetizing.

If one phase is missing the rotor still rotating in the same direction but the magnetic field is split in two: one direct rotating in the same direction with the rotor and the second is rotating in opposite direction. So we have two EMF's in all three phase windings -one positive sequence and one negative sequence.

The phase s and t connected with remaining healthy phase the direct EMF is compensated by supply voltage but the opposite does not. At transformer Tb secondary phase rs- 6.6 kV- it is magnetically connected with RN [22 kV] and so, in my opinion, the current supplied by the phase rs of the induction motor contains both components.

I take an example of 66/22 kV 20 MVA 8% ,22/6.6 10 MVA 8% and a motor 6.6 kV 670 kW [66 A rated 6.4*66=422.4 LRC ].

Vbase=22 kV

The maximum EMF produced it could be: 6.6 kV.

The motor direct impedance it is: Zm6.6kV=6.6/sqrt(3)/0.4224=9.02 ohm

At 22 kV the motor impedance will be: Zm=Zm22kV=Zm6.6kV*22^2/6.6^2=100.2 ohm

The opposite motor impedance will be the same.

Neglecting the resistances and the transformer Tb Zo the motor contribution will be:

Iscm22kV=22/sqrt(3)/(2*Zm+2*ZTb)

Iscm22kV=22/sqrt(3)/(100.2+3.872)/2=0.061025 kA

If we compare this current with the short-circuit current supply from the System[Grid] then:

if we take 3000MVA SYSTEM Short-circuit power then Zsys22kV=22^2/3000=0.161 ohm

ZTa=22^2/20*8%=1.936 ohm

ZTb=22^2/10*8%=3.872 ohm

The the short-circuit current at 22 kV supplied from System it is:

IscSys=22/sqrt(3)/(0.161+1.936)=6.057 kA

Iscm/Isc=0.061/6.57*100=1%

__________________
Julius
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Motor Contribution to Earth Faults

10/21/2019 7:25 AM

Er, um, the OP is talking about an <...earth fault...>, not a <...short-circuit...>.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6
In reply to #4

Re: Motor Contribution to Earth Faults

10/26/2019 1:22 AM

Sorry. It is here a mistake. Instead of:

Iscm22kV=22/sqrt(3)/(2*Zm+2*ZTb)

it has to be:

Iscm22kV=3*22/sqrt(3)/(2*Zm+2*ZTb)

and then:

Iscm22kV=3*22/sqrt(3)/(100.2+3.872)/2=0.183 kA

__________________
Julius
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); dkwarner (1); PWSlack (2); SolarEagle (1)

Previous in Forum: Ordinary Motor on VFD   Next in Forum: Distribution Transformer Protection

Advertisement