Ordinary Motor on VFD

10/15/2019 1:28 PM

Can we run an ordinary motor on VFD, ACS800 in this case ?.

Since the drive was tripping after running for some hours with the original motor,and there was no issue with VFD itself & also motor, we are left with the option to take trial of VFD with other similar motors.This is also suggested by VFD OEM.The motor and drive were installed around year 2010.

We have similar motor 132kw presently running on DOL.Can we take trial of this motor with VFD for some time.

Kindly guide.Thank you.

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Ordinary Motor on VFD

10/15/2019 2:51 PM

Let me get this straight , you can't determine the cause of the VFD tripping, so you want to substitute another motor to see if it's the VFD, or the motor that's failing...Is this the case?

http://www.industrialknowledgezone.com/5-rules-for-motor-vfd-compatibility/

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1369
Good Answers: 105
#2

Re: Ordinary Motor on VFD

10/15/2019 11:34 PM

Solar Eagle link advice is good, and you want to be conservative with a motor that expensive.

Your troubleshooting efforts are incomplete. It makes much more sense to find the cause of the problem than to just give it up to superstition. The ACS800 is a mature technology, so either the drive is defective or the motor/load has a problem.

You first need to tell your remote audience just what fault the drive displayed when it tripped. If no fault displayed, then make your RUN command as a single pair of wires, so no external problem is likely. If the simple RUN command version fails, with no fault indication, it is likely the drive itself has a problem.

The character of the load is essential to correct VFD operation. The ABB technical support may not understand the nuances of your unidentified driven machine, which then could make the VFD fall short of replacing a DOL starter.

Register to Reply
3
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#3

Re: Ordinary Motor on VFD

10/16/2019 12:34 AM

The ACS800 drive is in my opinion a rather good drive. If it was tripping there should be what caused the trip in the fault logs.

I have run "standard" motors on the ACS800. But be careful - depending on the motor you may need to add du/dt filters, common mode filters, and motor lead terminating networks. This is rather well spelled out in the ABB ACS800 installation manuals.

I have found that most motors in the last 20 years already have a VFD rating - search out the data on your motor / contact the motor manufacturer - you may have the answer in hand.

When you install a new motor be sure to enter the motor data in group 99, and do the ID tests - they are quick. DTC mode motor ID is best done with an uncoupled motor.

Register to Reply Good Answer (Score 3)
Associate

Join Date: Oct 2019
Location: BANGALORE. INDIA
Posts: 54
Good Answers: 1
#4

Re: Ordinary Motor on VFD

10/16/2019 3:41 AM

Technically we should not use ordinary motor with VFD combination for the following reasons.

1. Ordinary motor runs at constant speed with small to blow air to cool the motor. When the speed is reduced by VFD the fan speed also will come down and hence air flow will be reduced leading to rise in winding temperature and lead to premature failure.

2. The ordinary motor uses un-insulated bearings. The motor for VFD application should be fitted with insulated bearing on one side or provide bearing insulation to avoid the shaft current circulation.

3. Normally the ordinary motor speed will be (synchronus speed – slip) and slip may be 4 %, where as the VFD motor speed may require to run it above the synchronous speed, and vibration severity will increase to the square of the speed. If you consider your speed required is 1.2 times than synchronous speed, the vibratin amplitude wi,, be (1.20) ^2 = 1.44 times and the rotor and bearings may not with stand.

4. The earthing may not be dedicated one for ordinary motor an earthing flat will be alf of the current capacity where as for VFD application, it should have dedicated earthing, and earthing should be 2.5 times more in cross section if G.I flats are used.

This topic is discussed in this forum 4 or 5 times. Pl. search in this forum and you will find many members have shared their experience and knowledge.

DHAYANANDHAN.S

__________________
DHAYANANDHAN.S
Register to Reply
Member

Join Date: Apr 2019
Posts: 6
#5

Re: Ordinary Motor on VFD

10/16/2019 6:29 AM

I agree with most of the comments. First and foremost the motor needs to be inverter duty rated which all newer motors are. Rated and insulated to run 90% of rated speed. The drive will have a fault or trip code stored unless it is an external issue with the start or stop command. If there are no codes for the stop of the motor try running it with the drive itself, local. This will tell you what and where the issue is.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Ordinary Motor on VFD

10/16/2019 7:14 AM

Undefined: <...we...>.

CR4 is not a permission-giving entity.

One must be aware that the thermal losses from a motor that is driven from a VFD, as opposed to DOL, are slightly higher. This affects the cooling performance, especially when the speed drops below 100%. Provided the motor is protected internally thermally, as many larger motors are, then this characteristic will protect the motor going into temperatures it is not designed for. However, if correctly protected it may trip on high temperature.

The original posting is incomplete: <...drive was tripping after...some hours...> - on what parameter does it trip, please? Numbers?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Ordinary Motor on VFD

10/16/2019 6:23 PM

"Can we take trial of this motor with VFD for some time."

Yes, depending on your acceptable level of risk exposure. Any motor will run for "some time", the question will be the definition of "some". For motors that were never designed to run on inverter power, that may be as short as weeks, for others it may be months or years. There is no way to know. But if your definition of "some time" is just long enough to ascertain the cause of the shutdown because you ahve exhausted all other means of troubleshooting, then it should be fine.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
2
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#8

Re: Ordinary Motor on VFD

10/17/2019 1:15 PM

Thank you guys...Unfortunately, the drive tripped immediately 8-10 sec after starting in motor ID run mode.Upon checking found winding short.On inspection after opening the motor,found small damage near drive end side of the stator.

The motor was healthy( 50Mohm) with respect to insulation before trial and was running till 3weeks back in DOL.

We suspect that there could be some weak point on the winding and it failed this time, which might have occurred at any other day.!

__________________
"Know something about everything and everything about something"
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#9
In reply to #8

Re: Ordinary Motor on VFD

10/17/2019 2:03 PM

Thanks for the update!

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #8

Re: Ordinary Motor on VFD

10/18/2019 5:29 AM

So, the drive was right, then, and the protection was doing its job. Great stuff.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#11
In reply to #10

Re: Ordinary Motor on VFD

10/18/2019 11:39 AM

Yes. But two things remains unresolved.

1)Why there drive was tripping some time( hours) after running with the original motor.

2)What would have made the second motor to fail immediately after stating on VFD, if the assumption of weak insulation point in the motor ruled out.

I will get back if i got answers

__________________
"Know something about everything and everything about something"
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13
In reply to #11

Re: Ordinary Motor on VFD

01/26/2020 12:59 PM

To both questions; VFDs are good “fault finders” in that because of the nature of how they work, by pumping DC voltage pulses at very high frequencies and possibly creating capacitive effects that increase those voltages, any small seemingly insignificant flaw or nascent failure in the motor windings will become evident in a much more dramatic way shortly after being run from a VFD. Often times if you use standard measuring tools, such as 500VDC meggers, they will not see those flaws yet. I always recommend using 1000VDC meggers on 400 V class motors that are going to be run from VFDs.

And if you just used a DMM to measure the resistance, that is all but useless. All it tells you is that the motor insulation is not open circuit, but is just sufficient to handle a 9VDC battery...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#15
In reply to #11

Re: Ordinary Motor on VFD

02/20/2020 10:11 AM

Since there was no issue found with either motor or cable or drive, we went with varnishing of motor after winding inspection.

The motor is running healthy since last 3-4 months! But it still remains a big misery as what really was the problem that we could not pin point & resolve.

Thank you all for spending your valuable time and being ready to help.

__________________
"Know something about everything and everything about something"
Register to Reply
Active Contributor

Join Date: Jun 2019
Posts: 12
#12

Re: Ordinary Motor on VFD

01/25/2020 5:13 AM

The old motor( not an inverter duty motor) can be run on variable frequency drive. The following measures are required to run an ordinary motor on VFD.

1. If the motor is used to deliver less torque than its rated torque, the ordinary motor can be used. With VFD, the losses in the motor increases and necessary extra cooling is required.

2. The distance between the VFD and motor should be as minimum as possible to avoid higher voltage at the first turns of the motor caused due to standing waves of PWM inverter.

3. For the constant torque application throughout the speed range, the cooling of the motor at lower speed is required.

4. The shaft needs to be grounded through a carbon brush to prevent circulation of bearing current else the bearing may get damaged.

Related Article:Why V/f ratio is kept constant in VFD?

Register to Reply
Active Contributor

Join Date: Feb 2015
Location: Greater Memphis, Tn. Metro
Posts: 20
#14

Re: Ordinary Motor on VFD

02/19/2020 3:32 PM

The simple answer is yes you can run a non vfd rated motor on a vfd.

I would need to know some specifics before I could begin to diagnose your issue.

What is the fault?

what is the application?

Was the drive commissioned by someone profficient with drives?

I'm guessing that this is a 175 Hp and would need to know your application to determine whether or not a VFD or across the line starter would be most beneficial.

Unfortunately you haven't provided enough information to properly offer a suggestion on anything other than if you can use an ordinary non-vfd rated motor.

__________________
Dave Oliver
Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

daveoliver (1); dhayanandhan.s (1); giri (3); GW (2); JRaef (2); PWSlack (2); rwilliams (1); SolarEagle (1); vimal76 (1); Wayne Hager (1)

Previous in Forum: Leg Combinations   Next in Forum: Motor Contribution to Earth Faults

Advertisement