Breaker Long Time Delay

10/28/2019 2:19 AM

Why circuit breaker long time delay is mentioned as 6×In.

I have known that it is to avoid nuisance tripping during motor starting. I read in the manuals.

Suppose long time delay is set at 20 seconds at 6In. Ir=1×In. In=1000A

Short time current is 5In and delay is 0.4s

If fault current is 5×In, then will it wait for 20 sec or clear by 0.4sec?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Breaker Long Time Delay

10/28/2019 2:48 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Good Answer (Score 2)
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#12
In reply to #1

Re: Breaker Long Time Delay

10/29/2019 5:36 AM

Nice reference.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Reply
Anonymous Poster #1
#2

Re: Breaker Long Time Delay

10/28/2019 3:10 AM

I read that but I am not clear yet.

The long time delay is supposed to make the relay wait for 20s. Then why it trips in short circuit?

Reply
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: Breaker Long Time Delay

10/28/2019 3:18 AM

The short term setting trumps the long term setting, and usually it would be set the other way around...The information you need to digest is in the link I provided...If you want the breaker to follow the long term setting you would shut the short term setting much higher, or off...You can't have it both ways...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #2

Re: Breaker Long Time Delay

10/28/2019 4:26 AM

A <...short circuit...> will be well over either setting. One needs to protect the wiring!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#11
In reply to #5

Re: Breaker Long Time Delay

10/29/2019 5:23 AM

Yes, it is OR LOGIC. This or that to trip.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#10
In reply to #2

Re: Breaker Long Time Delay

10/29/2019 5:20 AM

Safe limit is not feasible to be over ridden if it is inbuilt.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#13
In reply to #2

Re: Breaker Long Time Delay

10/29/2019 10:51 AM

Adjustable circuit breakers come with current ranges for each time duration. Trip time depends on the current flow.

In this example the log time trip curve is applicable for 1 to 12 times tripping current and takes from 1 to 10,000 seconds. Short time applies for 12 to about 30 times tripping current, taking roughly .02 to 1 second, and instantaneous trip applies for fault currents over 12 to 30 times tripping current in less than .06 seconds and usually in less than 3 cycles of the current. The overlap of short and instantaneous trip times seems a little confusing, but in marginal current for very short duration faults don't always result in an annoyance trip. It allows the squirrel to explode and clear the fault without blacking out Los Angeles.

Reply
Anonymous Poster #1
#4

Re: Breaker Long Time Delay

10/28/2019 3:29 AM

The short time pick up range is 1.5 to 10. As per your suggestion, under which condition i can choose the ranges from1.5 to 6? Because long time delay is fixed at 6×In. I can not manipulate it.

Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7
In reply to #4

Re: Breaker Long Time Delay

10/28/2019 7:46 AM

The pick and delay for short time OC protection is selected based on the coordination requirements with the downstream device(s).

Once downstream device protection curve is finalised, the upstream device curve can be adjusted as required for appropriate coordination.

Protection devices are never set in isolation, either you have an equipment whose characteristics are to be known for giving appropriate settings for the protection device or a downstream device with which coordination is to ensured.

__________________
Raghunath
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Breaker Long Time Delay

10/28/2019 6:29 AM

Where is the user manual for the breaker, please? The manufacturer's phone number will be on it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Off Topic
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#8

Re: Breaker Long Time Delay

10/28/2019 8:58 AM

The circuit breaker trip settings describe a curve on a log-log10 time vs. current plot. the individual settings are used to adjust the curve position and shape. You have to combine the settings to see the final shape of the curve.

The long time curve will have an inverse shape (time decreases smoothly as current increases). You set the pickup current value (In = 1000A) as the start of the curve, at which point the time will be maximum on the plot. The long time delay then gives you a point on the curve that you can aim to, so that at 6 x In, the time will be 20 seconds. If you continued the curve onward, at 10x you may 5 seconds, etc.

The short time curve starts at the point you set, which is 5 x In. If you find on your plot the current value of 5 x In (= 5000A), draw a vertical line downward from that point on the long time inverse curve, until you get to the time of 0.4 seconds. At that point the curve will stop and turn horizontal. Any increase in current above 5000A will still trip in 0.4 seconds.

If there is also a higher, instantaneous trip setting, that will intersect the short time horizontal curve and do the same vertical/horizontal plot as the short time, except at the higher current and shorter time (no intentional delay).

You can see a good example of this plot in the link provided by Solar Eagle (Good answer for him!).

__________________
To get the right answers, first you need to ask the right questions.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Breaker Long Time Delay

10/28/2019 10:57 AM

It is incorrect practice to use a <...circuit breaker...> to carry out <...motor starting...>.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Off Topic
Reply to Forum Thread 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Jpfalt (1); PeterT (1); PWSlack (3); raghun (1); Shyam (3); SolarEagle (2)

Previous in Forum: We Have Two DC Motors of 1550kw Having Different GD2   Next in Forum: Paralleling LV Transformer Solidly Grounded

Advertisement