Synchronization

11/18/2019 2:30 PM

Dear all,

Why do we need only one phase voltage transformer for synchronous? What about other

phases? Since in our power plant for synchronous generator with grid we have three

voltage transformers in generator sides, but in grid side we have only one voltage

transformer in phase/S.

Thanks to all!

Register to Reply
Pathfinder Tags: synchronization
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9914
Good Answers: 1141
#1

Re: Synchronization

11/18/2019 4:23 PM

Well, if your phase rotation direction matches (e.g. ABC, ABC), if one phase is synchronized, the other two should obediently follow at 120 and 240 degrees behind and also be synchronized.

Register to Reply Good Answer (Score 3)
Associate

Join Date: Mar 2019
Posts: 29
#2
In reply to #1

Re: Synchronization

11/19/2019 4:19 AM

thank you for your replay

for phase rotation it is ok . but what about other conditions like voltage amplitude and

frequency

thanks

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #2

Re: Synchronization

11/19/2019 11:10 AM

One alters the frequency until the two systems are synchronised, and then one closes the switch. The two then stay synchronised.

If there is a voltage difference between the two sources then the greater will supply current to the lesser. Other equipment sorts this out.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9914
Good Answers: 1141
#7
In reply to #2

Re: Synchronization

11/19/2019 1:56 PM

When you synchronize the generator with the bus, the frequency will be exactly right. Once the breaker is closed, increasing the throttle will allow the generator to assume some load (real KW). (The throttle should be set in "droop" mode when the generator is paralled with the bus.)

If the generator voltage is not the same as the bus, there will be reactive current flowing between the generator and the bus (cross current) and the load will appear to the generator to be reactive. The voltage regulator should have circuitry to adjust the voltage to minimize cross current.

http://www.fgwilson.ie/files/generator-set-synchronising-with-and-running-in-parallel-with-a-supply-utility.pdf

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#4
In reply to #1

Re: Synchronization

11/19/2019 6:50 AM

I agree. A very primitive but effective method of manual synchronization was the use of a 10 watt clear incandescent light bulb across one incoming/outgoing phase.When the light went totally dark,they were synchronized and the transfer switch was actuated.

This was used on a circa 1950's GE 3.125 MW co gen set.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9914
Good Answers: 1141
#5
In reply to #4

Re: Synchronization

11/19/2019 9:22 AM

I've seen generators with two lamps monitoring the voltage between two phases of the generator and bus. When the generator is brought up to speed, the lamps brighten and darken in synchronism and the breaker should be closed when the lamps are dark.

One time a generator had been repaired and the phase rotation had been accidentally reversed. The lamps oscillated out of phase indicating the problem.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: Synchronization

11/19/2019 4:28 AM

In order to check synchronism between generator supply and grid supply, 1-phase voltage vectors are only considered both on generator side as well as on grid side.

If the generator step-up transformer is YNd1, Y-N vector on grid side is matched with y-b on generator side.

Three phase VT at generator terminals has other jobs also to do in addition to providing y-b voltage vector to synchronising scheme (Voltage input to Protection, metering, AVR etc. to name a few).

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2019
Posts: 29
#8

Re: Synchronization

11/20/2019 2:01 AM

thanks for all

sorry but suppose the voltage on three phase in grid not equality how we can

depend on only one phase to synchronization (because we have one voltage

transformer in phase/s)

thanks

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9
In reply to #8

Re: Synchronization

11/20/2019 5:52 AM

You are probably meaning slight unbalance in phase voltages that appears due to lack of transposition of conductors in the transmission lines etc.

Bear in mind, synchonisation doesn't mean only matching of voltage magnitude.

It is also

  • phase angle,
  • speed of voltage vector (frequency) and of course the
  • voltage magnitude.

Of these parameters, the tolerance available in voltage magnitude matching is like 5%.

I am sure the voltage deviations in different phases is definitely below the allowed tolerance of 5%.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2019
Posts: 29
#10
In reply to #9

Re: Synchronization

11/20/2019 6:03 AM

thank you very much for your replay

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #8

Re: Synchronization

11/27/2019 8:06 AM

Because if one phase is synchronised and the direction of rotation of the two sources is the same, the other two will be as well and there will be much rejoicing when the switch closes.

If they're not rotating in the same direction then one has no business attempting synchronisation, because it simply cannot happen and there will be much misery were one to try, otherwise pronounced "BANG!" and accompanied by blown fuses, smoke and the like. Pure folly.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

henry98 (3); HiTekRedNek (1); PWSlack (2); raghun (2); Rixter (3)

Previous in Forum: Recognize the Device?   Next in Forum: Single Core Cables in Trefoil in Conduit/Pipe

Advertisement