Single Core Cables in Trefoil in Conduit/Pipe

11/25/2019 7:48 AM

We have installation of 9 single core cables (3 x r-y-b trefoil groups, 10kV Cables) laid directly buried under ground without any pipes/conduits. On transition from underground to above ground to connect to the motor terminals,

Can I use each trefoil group in a conduit/pipe till the motor terminal. Are there any disadvantages in it?. The installation is in IEC Land.

Register to Reply
Pathfinder Tags: single core cable Trefoil
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Single Core Cables in Trefoil in Conduit/Pipe

11/25/2019 9:37 AM

The only disadvantage I'm aware of is the sizing of the pipe/conduit. Twisting cables into a trefoil makes them stiffer than each cable individually run, so installation may be difficult. Going up one or two pipe diameter sizes from the minimum for thes cables loose should mitigate this.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#4
In reply to #1

Re: Single Core Cables in Trefoil in Conduit/Pipe

11/26/2019 12:13 AM

Considering the trefoil formation will nullify the flux, metallic conduit that will be robust and supports the cables can be safely used.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Single Core Cables in Trefoil in Conduit/Pipe

11/25/2019 12:22 PM

...as would choosing a material for the <...conduit...> that is non-conductive.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Single Core Cables in Trefoil in Conduit/Pipe

11/25/2019 12:28 PM

IEC Land? Is this where glaciers are melting?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#5
In reply to #3

Re: Single Core Cables in Trefoil in Conduit/Pipe

11/26/2019 2:42 AM

Thankfully they melted on Lon Gisland. Giving you 300 yrs of great tasting freshwater.

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #5

Re: Single Core Cables in Trefoil in Conduit/Pipe

11/27/2019 12:54 PM

Close, but it's actually Lawn Guy Land.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #6

Re: Single Core Cables in Trefoil in Conduit/Pipe

11/27/2019 1:25 PM

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8

Re: Single Core Cables in Trefoil in Conduit/Pipe

11/28/2019 3:17 AM

If you are in IEC World I'd prefer three-core cables instead of single core. The problem with single core it is the unbalance between currents and a mistake in cable grouping [let's say r,r,b instead of r,y,b ] could produce current difference between conductors of a same phase and induce current in conduit.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: Single Core Cables in Trefoil in Conduit/Pipe

11/29/2019 12:30 PM

See also-for instance:

https://pdfs.semanticscholar.org/e84e/444ab5899f91301f7e738dbd92b01e8d0a23.pdf

__________________
Julius
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: