Current Measurement of a Motor Run from VFD

01/08/2020 10:59 AM

I request you to clarify me about motor current measurement when running it from a VFD. Generally,the motor name plate specifies,Operating voltage ,Full load current at a frequency of 50 Hz or 60 Hz. My doubt is if I am operating the motor with VFD,

At 10% speed(5Hz),At 25% speed(12.5Hz),At 50% speed(25Hz), ,At 75% speed(37.5Hz), At 100% speed (50Hz), VfD shows current readings.But these currents are measured at different frequencies.Can I equate this current as if the motor is running at 50 Hz.

How to correlate them to current at 50 HZ frequency?

I am thinking say, for example,if the drive shows 35 Amps current at 25 Hz frequency and it shows 35Amps at 50 Hz frequency,it is not same current.i.e.,we have to calculate the current at the same frequency to understand the loading on the motor.Please clarify my doubt.

My second doubt is whether current measurement in the VFD is correct or not correct.Because,the calculation may be assuming same frequency.Please clarify my doubt.

Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Anonymous Poster #1
#1

Re: current measurement of a motor run from VFD

01/08/2020 11:30 AM

Check it with a true RMS clamp meter. It will give you the exact value of current.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#5
In reply to #1

Re: current measurement of a motor run from VFD

01/09/2020 1:33 AM

True RMS gives you the heating value of the current, no need to recalculate or adjust for frequency, when working with VFD specifications, for instance. The true heating effect in the rotating machinery due to frequency is taken care of in the design of the equipment. The requirement for cooling is far more affected by the actual speed of the equipment, due to the common practice of applying motors with shaft driven fans.

Over the typical frequency range we normally consider, the thermal effects on the iron and copper of the frequency changes are all lumped in with the other rating factors, so you get a piece of equipment that is pretty easy to apply.

As to the VFD measure, that is what it is using to protect the motor, so if no good, not a very good VFD, and you will end up with lots of customers with burned up motors. Something will eventually give...

Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: current measurement of a motor run from VFD

01/08/2020 11:31 AM

The important thing is not to cook the motor:

  • It is current passing through it multiplied by the fixed internal resistance of its windings that develops the heat within the motor.
  • For a fixed speed, current is significantly proportional to torque↑1. It would be a rare mechanical contraption that presented more torque to the motor at low speed compared to full speed.
  • Generally, it is preferable to use VFD-rated motors for variable speed applications. One might "get away with it" using non-VFD-rated motors though this is not recommended.
  • Programming the motor full load current, given on the plate attached to it, into the VFD for 50Hz will ensure that the current passing through it won't cause it to overheat, as the VFD will take action once the limit is reached/passed, flagging it as an overload. Overload can take place at any speed.
  • As suggested, the variation of power factor with speed also takes place.
  • Fan cooling is less effective at less-than-full-speed than it is at full speed.
  • Many motors have temperature measuring devices embedded within the windings, which are wired to a trip device, located either in the VFD unit or as a stand-alone item that trips the motor start-and-run holding circuit. Use of these on VFD applications is recommended.

If in doubt, consult a qualified local Electrical Engineer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#3
In reply to #2

Re: current measurement of a motor run from VFD

01/08/2020 11:57 AM

GA

That rare(?) mechanical contraption that makes more torque at lower speeds is a DC motor or traction motor. One does not use a VFD to drive such a motor but with so many using VFD to make an AC synchronous motor move at some rate other than power grid frequency rates I feel this true workhorse of simple speed control has been forgotten.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#4
In reply to #3

Re: current measurement of a motor run from VFD

01/08/2020 4:19 PM

The old work horse is still used in industry,but they are being phased out.

Series wound DC motors have most torque when first starting up,and this torque is limited only by the power supply or current limits within the drive controller.

If current is unlimited,so is speed,and I have seen armatures destroyed by centrifugal force when the controller went bad.

The armature segments actually pulled away and jammed on the motor housing.

They were still making contact with the brushes,and fuses were blown or a fire resulted if someone bypassed the fuses.

As the saying goes "You can't make something foolproof 'cause those fools are so damned ingenious."

The speed is easily controlled by varying the voltage,and synchronization of multiple motors is easily obtained,and once set,seldom needs adjusting,even for varying speeds or loads.

These type drives are used in web systems,such as printing,paper goods,textiles,etc.

These old workhorses are slowly being replaced by the newer AC drives,but they will be around for a long time before they are all relegated to the glue factory.

As for a synchronous AC motor,if it is designed for a slower speed,it will produce more torque at the designed speed than at a higher speed,if power consumed is the same.

Example: A 900 RPM (name plate RPM) motor will have twice as much torque as a 1800 RPM (name plate rpm) motor of the same horse power.

Consider the VF motors in EV's.

Maximum torque from zero speed on up to max speed.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #3

Re: current measurement of a motor run from VFD

01/09/2020 7:14 AM

Torque is stuff that is presented mechanically to a motor for it to overcome. A mechanical load that exerts more torque at low speed than at high speed will eventually cause the motor to stall and, if set up correctly, to trip out on overload.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#13
In reply to #8

Re: current measurement of a motor run from VFD

01/15/2020 6:36 AM

Check out the graphs on this link,espcially the lower one:

https://www.carthrottle.com/post/how-do-electric-vehicles-produce-instant-torque/

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Active Contributor

Join Date: Feb 2015
Location: Greater Memphis, Tn. Metro
Posts: 20
#15
In reply to #3

Re: current measurement of a motor run from VFD

01/30/2020 10:16 AM

There are numerous examples of DC drives controlling a DC motor. These drives are essentially VFDs since the utilize PWM to adjust the speed with the major difference being that they output a DC voltage instead of an AC 3ph. The use of these DC motors is because of the low speed torque as you stated.

__________________
Dave Oliver
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #2

Re: current measurement of a motor run from VFD

01/09/2020 7:17 AM

current the square of the current

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#6

Re: Current Measurement of a Motor Run from VFD

01/09/2020 4:20 AM

All the VFD operated motors that I've seen recently were on pumps. The pump assembly (including motor) included data sheets that indicated the operating envelope for that assembly.

I seldom saw any that were rated beyond +/-20% of mains frequency and typically these were then also rated to +/-20% nameplate voltage with a separate envelope for total power so that these limiting parameters could be programmed into the VFD device.

__________________
Just an Engineer from the land down under.
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Current Measurement of a Motor Run from VFD

01/09/2020 4:28 AM

Current is current is current. There is no “50Hz current” vs “25 Hz current”. There is just the current. In a VFD run system, current is related to torque, not speed. The purpose of a VFD is to provide full torque at any speed, so if your load requires an amount of torque to operate, that should stay the same even if speed changes, ergo current will remain the same as well.

In centrifugal machines like pumps and fans, the load will demand less torque as speed decreases because less load is coupling with the machine, so current does drop with speed. But in most other types of loads, it stays fairly constant.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Dec 2019
Posts: 160
Good Answers: 14
#10

Re: Current Measurement of a Motor Run from VFD

01/09/2020 2:41 PM

When a VFD drives a motor, as the frequency is reduced the voltage applied to the motor is reduced as well. To get an effective measurement of the power being delivered at the various speeds. motor torque T equals the power being developed divided by the motor mechanical angular velocity, which is equal to 4*Pi*f/p (p is the number of poles). I would suggest you use a watt-meter to measure the power because the phase angle varies with load. Using the watt-meter gives you the true power and the torque can be calculated by diving the power my the mechanical angular velocity.

Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 809
Good Answers: 65
#11

Re: Current Measurement of a Motor Run from VFD

01/09/2020 4:00 PM

You can carry out a simple experiment to get your mind around the current drawn by using two RMS clamp on meters, one on the supply at 50/60 Hz and one on the motor supply at whatever value of Hz you are using.

At slow speeds motor overheating with shaft driven fans is a big problem and the slow speed running should be limited.

There was a positive displacement pump on a floc dosing system that would always overheat below 20% speed so the solution was to increase the dilution of the floc to keep the motor above this level. On a small motor like this an external fan was not warranted. Remember heat is the killer.

__________________
Hare today, goon tomorrow!
Register to Reply
Member

Join Date: Sep 2019
Posts: 5
#12

Re: Current Measurement of a Motor Run from VFD

01/12/2020 4:44 AM

VFD measures the dc current using Hall effect Sensors and gives 4-20 mA outputs for actual drive current hence current measured is not frequency dependent. So there's no need to convert it to 50 hz frequency. If you try to measure the current by using out put CT, it will indicate wrong current because standard CT is rated for standard 50/60hz. Again if you measure the current by using input CT before drive, it will also give wrong value because of harmonics generated by drive. I have checked it practically so better go with current signals given by drive. Hope this helps.

Register to Reply
Active Contributor

Join Date: Jun 2019
Posts: 12
#14

Re: Current Measurement of a Motor Run from VFD

01/22/2020 11:11 PM

The output of the PWM inverter is not perfectly sinusoidal and average responding ampere meter does not read the current accurately. The true rms meter reads the correct current because the true rms meter measures the current on the basis of the heating value. The current measurement by true rms multimeter gives the accurate reading at all frequencies.

Register to Reply
Active Contributor

Join Date: Feb 2015
Location: Greater Memphis, Tn. Metro
Posts: 20
#16

Re: Current Measurement of a Motor Run from VFD

01/30/2020 10:32 AM

The current measurements from the VFD are readings from CT that are in located in the inverter section of the output circuit. This is measured after the PWM(pulse width modulation) has been performed and can also be measured on the TLeads(U,V,W) with a true RMS clamp meter.

The reason that you may be perceiving erroneous readings is most likely as result of the V/F curve of the programmed application.

You will definitely see higher currents at extremely low speeds due to the need for higher torque to initiate rotation. As motor speed increases and the motor flux is stabilized the current will settle at rated current at rated speed.

Almost always the current from the VFD will be more accurate than any external measurement. Most VFDs offer analog outputs that are either dedicated or selectable as either a 0-10 vdc, -10-+10vdc, or 4-20 mA signal and this will give you the true output of the VFD.

__________________
Dave Oliver
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); daveoliver (2); HiTekRedNek (2); JRaef (1); Just an Engineer (1); PWSlack (3); R_i_c_h (1); Rakesh Mishra (1); redfred (1); rwilliams (1); Stef (1); vimal76 (1)