Hi. Can anyone advise me on repairing or replacing with electronic, the AVR on an old Markon 15kVA 3-phase generator. The original has 2 x 3-phase transformers, one of which broke loose and seriously damaged one of the coils. The rotor is also 3-phase (4 slip-rings).
Thanks
Re: Old Markon generator, trouble
01/28/2020 1:08 AM
01/28/2020 1:34 AM
01/28/2020 6:13 PM
Wow, that was quick and to the point. Thank you. I am not convinced that that AVR will be able to supply enough power for a 15kVA generator, but your response 1) does give me more confidence to find a higher-rated one. 2) Confirms the circuit arrangement.
01/28/2020 10:07 PM
If you understand the principals involved you should be able to make it work...good luck
01/29/2020 8:05 AM
so will this somehow energize the third leg and does it subsequently lower the output by a third?
he stated that one winding was damaged.
01/29/2020 12:44 PM
Well I would hope the damage has been repaired, as this would seem to be a prerequisite to normal function...
01/29/2020 12:53 PM
one winding of the old feedback circuit is damaged. The electronic AVR will render that redundant.
01/29/2020 12:59 PM
Looking again, this won't work. There are 3 coils (4 brushes) on the rotor, at least oner will need to be fed with DC. This diagram is for a brushless system.