Why Positive DC Grounding Over Floating?

01/30/2020 1:37 AM

Dear all

in our power plant the telecommunication equipment it is 48V positive grounded my

question is why positive grounded why not floating what is the useful of this ground

thank for all

Register to Reply
Pathfinder Tags: DC grounded
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: DC grounded

01/30/2020 2:25 AM

Mostly I think for eliminating noise and voltage spikes effecting the signals, the positive ground allows for excess voltage leak off and minimizes corrosion...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #1

Re: DC grounded

01/30/2020 12:10 PM

<...minimizes corrosion...>

Er, um, motor vehicles are negative ground for that reason....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
4
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#5
In reply to #4

Re: DC grounded

01/30/2020 2:06 PM
Register to Reply Good Answer (Score 4)
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#2

Re: DC grounded

01/30/2020 4:42 AM

Also, if the site is relatively large, then grounding will ensure that the local voltage (relative to the other cabinets and such) will be at that same potential. Also, if anything (within reason) is incorrectly connected it will be shunted to ground rather than some unfortunate operator.

In coal mines it was referred to as "transfer potential". Even a simple pipe could run a few miles sitting on insulated supports, so if it wasn't locally grounded you encountered the transferred voltage from the pipe connection point. Combination of outgassing from coal and sparks was to be avoided at all costs.

__________________
Just an Engineer from the land down under.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: DC grounded

01/30/2020 5:05 AM

Floating systems are complex as detection and elimination of ground fault requires special equipment and operationally complex. Yet, this is preferred in DC systems over 50V to prevent loss of supply on first ground fault.

In case of 50V and lower, the possibility of earth fault is low (considering the voltage with earth itself is low and hence the required clearance is low). This is the reason why DC system is grounded.

__________________
Raghunath
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1270
Good Answers: 27
#6

Re: Why Positive DC Grounding Over Floating?

01/30/2020 10:31 PM

Seems to be a very effective, good and stable 48 volts regulation is achieved, by using positive ground, as no inadvertent and accidental voltage increase can be imparted onto the telecommunications system power supply..

Any unnecessary voltage increased is automatically shorted to the ground potential..

__________________
vsar
Register to Reply
Associate

Join Date: Nov 2016
Posts: 38
#7
In reply to #6

Re: Why Positive DC Grounding Over Floating?

01/31/2020 4:06 AM

Dear sir

thanks for your replay

but how unnecessary voltage is automatically shorted to the ground potential.

thanks

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#8

Re: Why Positive DC Grounding Over Floating?

02/03/2020 1:35 PM

Without a ground the system could be floating up at 2kV and no one would know until they touched it.
I know this from experience when someone built a badly designed and constructed power supply test rig... and I had to use it
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: