with stand capacity or short circuit current?

10/27/2007 12:46 AM

is the rating of a protective device like over load current, fault level, short circuit current and with stand capacity same? please put light on this with example.

thyanks and regards

__________________
manirul
Register to Reply
Pathfinder Tags: with stand current
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: with stand capacity or short circuit current?

10/27/2007 4:02 AM

I would say probably yes..but you would need to consider the application and specifaction of the particular device. Read the specifications.

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: with stand capacity or short circuit current?

10/27/2007 6:07 AM
  1. over load current = long term excess current in a circuit, but not a short circuit or ground (earth) fault
  2. fault level = the amount of current flowing during a fault of any kind, but also sometimes use when describing the total amount of fault current available in a circuit, i.e. how much current will be capable of flowing to a fault if it happens, base on system delivery capacity, transformer impedances, conductor resistance etc. etc.
  3. short circuit current = fault current if the fault is a short circuit
  4. withstand (it's one word) capacity = the amount of fault current which a device can carry (withstand) without becoming critically damaged from the magnetic forces.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#3
In reply to #2

Re: with stand capacity or short circuit current?

10/27/2007 9:02 AM

Don't forget that time is also a factor in each of these ratings. Withstand, for example is a given voltage (or current), waveform and magnitude for a defined time.

Register to Reply
Guru

Join Date: Jan 2007
Location: Sitting directly behind my keyboard in Albuquerque - USA
Posts: 592
Good Answers: 19
#5
In reply to #2

Practical example

10/28/2007 9:32 AM

A practical example is something I'm doing now:

Upgrading a 30 year old switchboard for installation of a larger Diesel Generator on a vessel.

The bus bars can take the load, and the overload. The bus bars cannot take the short circuit current, and the bus bar bracing (withstand) cannot take the electromagnetic forces (EMF) during short circuit. Before the current overheats the bus bars, they will fly out of the switchboard due to very high EMF pulling them from their braces (mounting).

One complete 60 Hz cycle is approximately 16.6 milliseconds. Peak current will occur in approximately 4 milliseconds, one quarter of the sine wave. The fastest overcurrent relay I know of is half cycle, 4 milliseconds too late. Current limiting fast blow fuses can blow in 2-3 milliseconds, but we are not allowed a non-resettable interrupt device on this vessel.

Solution: Go to 20% sub-transient reactance generator with much lower short circuit current and add some bus bracing.

__________________
If it eats, it's going to be trouble!
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4

Re: with stand capacity or short circuit current?

10/28/2007 12:20 AM

In an Electrical Distribution System,when there is a fault ,there will be excessive current flowing through various devices like,transformers,switch boards,cables,current transformers,switchgear etc.

In a system the maximum current would be during dead short circuit between phases or between phase and earth.

One has to find out(calculate) short circuit current that will flow in the system.

the devices selected should withstand this short circuit current for a period of 1 to 3 sec.

This is the real meaning of short circuit withstanding capacity of the device

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: Oct 2006
Location: Indonesia
Posts: 102
#6

Re: with stand capacity or short circuit current?

10/28/2007 10:33 PM

no, it's not the same.

1. Overload current : the protective device is set to nominal current as rated on the nameplate, but equipment must be able to hold the current flow of 1.15 to 1.5 times of its nominal.

2. Fault level : Unit in MVA, it is 1.732xLine VoltagexShort Circuit Current

3. Short circuit current : you know it. Unit in kA

4. Withstand capacity : capable of holding the peak shortcircuit current usually in max. 3 seconds.

Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#7
In reply to #6

Re: with stand capacity or short circuit current?

10/29/2007 3:27 AM

short ckt current along with time means within that time, that much current can be flow without damaging the conductor, is it not withstand capacity of conductor? again for fault level, it is the highest level of fault(what ever may be the fault) current which can be saifly pass within the time limit, again is it not similar to withstand capacity? if the time 0.1 or 0.3 sec means conductor should be disconnected in this time before reaching the temparature limite, time should be kept in mind for all those cases.

__________________
manirul
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abu Khansa (1); Bluestone (1); JRaef (1); manirul (1); PetroPower (1); ramvinod (1); user-deleted-1105 (1)