Earthing System

02/16/2020 1:17 PM

dear all

in generator we used neutral grounding transformer to limit fault current to 10A and in

unit aux. transformer we used NGR to limit fault current to 400A.and in some

transformer the neutral point directly earthed.

my question why in generator current limited to 10A but in transformer 400A.and

why some transformer directly earthed

thanks

Register to Reply
Pathfinder Tags: Earthing system
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: earthing system

02/16/2020 1:26 PM

Fault currents are established to prevent damage to the system, and for safety to personnel....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#2

Re: earthing system

02/16/2020 10:18 PM
__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3

Re: earthing system

02/16/2020 11:42 PM

The earthing design is affected by the voltage of the system you are protecting.

A 400A system is designed to limit iron damage in rotating equipment operating at a high voltage, ie 4000V, where the charging current of the system is relatively high. The 400A rating is chosen based on the sensitivity of the protection equipment, so that selective operation of the protection is possible. The 400 amperes is usually allowed to flow for 10 seconds, enough time to sense & clear the fault.

High resistance grounding can be applied on lower voltage systems, allowing continued operation of the distribution system as long as there is only one phase faulted. Those systems have low charging current, less than 10 amperes, so a low wattage ground resistor can be used. Same reason for your neutral grounding transformer for your high voltage generator, reactance grounding.

Solidly grounded systems are inexpensive, provide plenty of fault current to ensure quick isolation of the fault, and reduce higher voltages associated with other systems during a fault. If you get a ground fault in an expensive large motor, it will allow more damage to occur to the lamination iron, possibly requiring scrapping of the motor, painful for a $20,000 motor, for instance.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Earthing System

02/17/2020 8:41 AM

All the fault current does is trigger (a) circuit protective device(s) once it is above a predetermined level. A <...400A...> fault requires rather more copper than a <...10A...> fault, and the latter represents a lower total value of equipment installation. It is also potentially [sorry about the pun] less hazardous to personnel who may be in contact with the earth conductor(s) when the fault occurs.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Earthing System

02/18/2020 2:23 AM

In rotating machines, any stator earthfault would involve the (CRNGO) core in the fault current path. As the core material is highly resistive, the heat due to the fault current flow would be more and thus the core damage. Any winding damage could be rectified at a local re-winder but for core damage rectification, the machine may have to be sent to the manufacturer. This would involve cost and increased downtime. So, core damage has to be avoided, as much as possible. Each rotating machine will have a core damage curve and a typical fault current withstand of CRNGO core is 25A/1sec. So, wherever rotating machines are involved in the network, it is safe to limit the earthfault current to less than 25A. A typical value is 10A.

In case of transformers, even though the winding is capable of handling the rated full load current continuously, to offer safe operator and/or livestock protection, it is safe to limit the earthfault current. At the same time, limiting to a very low current might make detection & isolation difficult. So, to enable detection & isolation, in case of transformers, it is general practice to limit the earthfault current to about 200 to 400A.

In case of low voltage secondaries, with the neutral distributed to cater to single phase loads, non-electrical personnel too handle electric appliances. So, to ensure safety of those personnel, the neutral is solidly grounded, so that, in the event of an earth fault, full three phase short circuit current flows and the transformer's SCPD (Short Circuit Protective Device) would clear the fault in milliseconds, before it could hurt the operator. That is, the fault is cleared without the need for any special earth leakage/earth fault protective device.

Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); PWSlack (1); rwilliams (1); SolarEagle (1); StandardsGuy (1)