500 KV Auto Transformer with Oil to SF6 Bushing Test

03/30/2020 1:48 PM

I work in thermal power station, main step up transformer is manufactured by ABB

transformer voltage :500/24 kv

Transformer rating : 500 M.w.

it equipped with oil to SF6 bushing and connected to 500 KV GIS manufactured by Siemens at 500 kv side at 24 kv side is connected with iso phase bus isolated with air

According to transformer manufacture ABB it is required to achieve the electrical tests of transformer annually but its very difficult to disassemble the GIB link and direct transformer connection every year and which cause harmful damage for the GIS equipment and change all filter at the GIB from transformer to first isolated gas barrier).

The test required from transformer manufacture

1. Turns ratio test

2. Winding resistance

3. Measure the insulation power factor

4. Perform insulation resistance tests

My question is Due to all previous purpose I discuss the possibility to achieve previous electrical tests without disassemble the link each of gib and transformer by using the earth disconector in GIS and use it to connect bus between transformer and GIS with the earth and I can use the earth as high voltage terminal and 24 kv side i can disassemble easy

Note

distance between the GIS and the transformer terminal will isolated with sf6 and sf6 will affect the insulation power factor test

I can overcome the error in winding resistance by subtract the resistance of gib

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: 500 kv auto transformer with oil to SF6 bushing TEST

03/30/2020 5:23 PM

Stop trying to take shortcuts and follow recommended procedure..it is what it is...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6216
Good Answers: 248
#2
In reply to #1

Re: 500 kv auto transformer with oil to SF6 bushing TEST

03/30/2020 10:51 PM

Agreed! The humongous replacement value of that transformer makes it well worth treating it with great respect! There's a reason the manufacturer gave those directions. If you don't follow those directions, any warranty is worthless.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
2
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#3

Re: 500 kv auto transformer with oil to SF6 bushing TEST

03/31/2020 3:35 AM

You cannot buy these transformers at the local electrical supply,and they are probably made-on-demand,so if one fails,you may be down for quite a while.

Can you Imagine trying to provide power while it is down with diesel generators?

In addition to the cost of replacement of the transformer,there will be other significant damage if it fails.

I have seen I beams melted into puddles when 113kv has failed.

Instead of trying to overcome the error in the GIB,you should correct the error in your resistance to doing it properly according to specifications.

You should not gamble if you cannot afford to lose.

Do you feel lucky?

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Good Answer (Score 2)
Associate

Join Date: Jan 2017
Posts: 30
Good Answers: 3
#7
In reply to #3

Re: 500 kv auto transformer with oil to SF6 bushing TEST

03/31/2020 4:14 PM

Hello RedNeck.

You must be feeling "fully charged" - living so close to the homestead of Nikola Tesla.

Sticking to 'specifications' does not protect you from making errors or incorrect interpretations. The man has a point, . . . do you take some short-cuts and get the transformer tested, . . . so that it can be put to service and generate some revenue? Or do you take a couple of weeks to disassemble the GIS and more, just so that you can stick to specifications?

An engineer is supposed to be able to weigh the costs and benefits of things he does and make a decision. This man is not an engineer - as he can mot make a decision.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#11
In reply to #7

Re: 500 kv auto transformer with oil to SF6 bushing TEST

04/01/2020 8:47 AM

It is obvious that he is not an engineer or he would not be seeking advice from sources of unknown qualifications.

The manufacturer is the best source of information for this.

He should consult with them for the possibility of alternate methods;they are the most qualified for their product.

Their specifications may err on the side of caution for liability and safety concerns.

The courts are full of companies and families of people that have taken short cuts.

As I said,"Do not gamble if you cannot afford to lose."

I have seen first hand the results of short cuts in electrical causing actual "shorts" and it is not pretty.

If he feels lucky,then by all means use an unapproved ad-hoc method for testing.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #11

Re: 500 kv auto transformer with oil to SF6 bushing TEST

04/01/2020 12:54 PM

It sounds as though the Original Poster has contacted the manufacturer already and simply doesn’t like what the manufacturer says.

it’s only to be hoped that no other CR4 reader is in the vicinity when something goes BANG!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6216
Good Answers: 248
#15
In reply to #13

Re: 500 kv auto transformer with oil to SF6 bushing TEST

04/01/2020 1:51 PM

In my very limited but real experiences, the destruction will continue for longer than just BANG!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Associate

Join Date: Oct 2013
Location: Saudi arabia
Posts: 40
#18
In reply to #13

Re: 500 kv auto transformer with oil to SF6 bushing TEST

04/01/2020 2:17 PM

no i didnt contact with manufacture

what i want from CR4 before taking any decision to find some one illustrate to me the effect of sf6 on power factor and capacitance test

Register to Reply
Associate

Join Date: Jan 2017
Posts: 30
Good Answers: 3
#20
In reply to #18

Re: 500 kv auto transformer with oil to SF6 bushing TEST

04/01/2020 9:57 PM

Sounds like you have never testa a sizeable transformer before. Every transformer has bushings and you HAVE TO TEST IT WITH THE BUSHINGS. It is not possible to do it otherwise.

It does not matter if the bushing is oil-filled or SF6 insulated, . . . you have to test it with the bushing.

You do the bushing test separately, . . . and subtract the readings from the transformer readings. The HV bushing must have a "Test-Tap" to do the measurement.

Normally, . . . the HF6 bushing will measure a power factor (DF) considerably lower than an oil-filled bushing and lower than the transformer power factor (DF).

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#23
In reply to #18

Re: 500 kv auto transformer with oil to SF6 bushing TEST

04/03/2020 7:43 AM

Overcome <...didnt contact with manufacture...> in the first instance.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#21
In reply to #13

Re: 500 kv auto transformer with oil to SF6 bushing TEST

04/02/2020 11:49 AM

NO,not BANG,more like BOOM! with mushroom cloud and X rays of the vicinity.

https://www.youtube.com/watch?v=-UGh9jOChHI

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22
In reply to #21

Re: 500 kv auto transformer with oil to SF6 bushing TEST

04/03/2020 7:41 AM

The update is appreciated.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: 500 KV Auto Transformer with Oil to SF6 Bushing Test

03/31/2020 7:58 AM

Your main problem is performing the insulation power factor test. As you said, the winding resistance test can be done as you propose, and turns ratio won't be affected by the bus. Insulation resistance is such a "coarse" test in comparison to the insulation power factor that as long as it gives a good value for both transformer and bus together you are okay there.

However, the insulation quality of the connected SF6 bus becomes part of the total insulation power factor test results, so to get good data for the insulation of the transformer alone you must disconnect it from the bus.

If you ground the HV side and only do the measurements from the LV side, you are only testing part of the transformer insulation. Insulation Power Factor tests measure 3 main quantities: Insulation quality HV to ground, HV to LV, and LV to ground. If you ground the HV, you cannot measure the condition of the HV to ground insulation or the HV to LV, since everything is now LV to ground. And the HV to ground and to LV are probably your more critical measurements (at 500kV!).

So to do complete tests, you are stuck having to disassemble/disconnect the HV GIS. Have you talked to the GIS manufacturer to see if there is a way to provide a test link of some sort, that could allow you to do what you need to? I am not all too familiar with details of GIS manufacture to know if something like that is available. I know that there are test links made for air bushings, which allow transformers to be tested without having to unbolt the connecting bus, by opening a mechanical link. I have not heard of it for GIS, but that doesn't necessarily mean it isn't available.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 3)
Associate

Join Date: Oct 2013
Location: Saudi arabia
Posts: 40
#5
In reply to #4

Re: 500 KV Auto Transformer with Oil to SF6 Bushing Test

03/31/2020 11:32 AM

Thanks for your reply and your value note about the grounding. I didnot mention that the grounding and neutral connections are at oil to air bushings, so it's no problem to disconnect the ground and complete the test. My concern is the effect of sf6 on the output value.

Register to Reply
3
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#6
In reply to #5

Re: 500 KV Auto Transformer with Oil to SF6 Bushing Test

03/31/2020 2:11 PM

Since you are taking baseline readings and really looking for changes, why not include the SF6 in the baseline, and only do the complete disassembly if you see a base line departure unexplained by your test condition log?

Major work taking apart important critical components of your equipment increases the probability of a problem caused by your testing procedure, perhaps higher risk than the historical reliability of your class of transformer. Your job is to assure the reliability and operability of the whole installation, not just the transformer.

i would write an exact description of your test procedures, illustrated so that there would be no additional guidance needed for your test technicians, and find someone at ABB to share it with. If it is not a viable method, they will be able to point out the deficiencies and advise you appropriately.

Register to Reply Good Answer (Score 3)
Associate

Join Date: Jan 2017
Posts: 30
Good Answers: 3
#8

Re: 500 KV Auto Transformer with Oil to SF6 Bushing Test

03/31/2020 5:08 PM

Yes, your biggest problems are measuring the C&DF as well as the insulation resistance. HOWEVER, as each of these test consists of THREE PARTS - Hi-Gd, Hi-Lo, and Lo-Gd, . . . you can perform the Hi-Lo test accurately, as this configuration is not influenced by all the additional items of the Hi or the Lo side.

Furthermore, . . . you can perform the test Hi-Lo as well as Lo-Hi, in which case you should obtain the same answer, . . . same capacitance & DF.

As the Hi-Lo insulation is the most important one in a transformer, and is found to be good, then the Hi-Gd and Lo-Gd insulation can also be considered to be good.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6216
Good Answers: 248
#9
In reply to #8

Re: 500 KV Auto Transformer with Oil to SF6 Bushing Test

03/31/2020 11:16 PM

I have zero practical experience with transformers like this one, so don't hesitate to correct me.

But the title says "auto transformer". In my experience that term refers to a transformer where the low voltage winding IS part of the high voltage winding. If that is the case, how can one measure the insulation resistance between two parts of the same winding?

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#10
In reply to #9

Re: 500 KV Auto Transformer with Oil to SF6 Bushing Test

04/01/2020 7:49 AM

dkwarner, you are correct - I missed that in the title of the post (it was not mentioned in the OP's descriptive text). Since this is an auto-transformer, there is only one test of the HV/LV winding insulation to ground, not 3 as I mentioned (HV-G, LV-G, HV-LV).

If the OP can disconnect the LV bus, and use the HV's grounding disconnector switch as a test point, he may be able to do what he suggests. He would have to disconnect the ground connection of the disconnector from actual earth so that he can do the test. That still leaves the added impact of the SF6 GIS that is connected to the HV bushings of the transformer.

I don't know what type of insulation power factor test equipment the OP is using, but Doble Engineering (world leader in such testing) recommends having the transformer winding disconnected from anything else that can contribute to the test readings. It's not just the SF6 gas in the bushings & GIS that impact it. There are also physical insulating stand-offs that support the conductor inside the GIS at some points, as well as the GIS bushings between sections themselves. All of these will contribute to the insulation power factor readings.

Even if the OP gets a baseline reading including the GIS contribution, if there is a change you might not be able to tell whether it points to a problem with the transformer or the GIS. Either one could be a large expense to diagnose and repair, but I'd say the transformer is likely the more difficult. My recommendation is still to test the transformer separately.

On a separate note, I think ABB's insistence that the transformer be tested annually is excessive. Other, independent (e.g., NETA) maintenance test standards would recommend that the electrical tests be done at about 3-year intervals, with insulating oil sampling and analysis done annually. Condition-based maintenance procedures would vary that interval based on operating conditions, previous history, etc.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Associate

Join Date: Jan 2017
Posts: 30
Good Answers: 3
#12
In reply to #10

Re: 500 KV Auto Transformer with Oil to SF6 Bushing Test

04/01/2020 8:53 AM

Gentlemen, . . . the problem is "heysam" who does not know how to describe what he has. A 500kV/24kV, 500MVA generator transformer is NEVER connected as an AUTO-TRANSFORMER.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #12

Re: 500 KV Auto Transformer with Oil to SF6 Bushing Test

04/01/2020 12:55 PM

One might fear for the future, then...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Oct 2013
Location: Saudi arabia
Posts: 40
#16
In reply to #12

Re: 500 KV Auto Transformer with Oil to SF6 Bushing Test

04/01/2020 2:07 PM

three phase bank transformer 167 MVA for each phase

Register to Reply
Associate

Join Date: Jan 2017
Posts: 30
Good Answers: 3
#17
In reply to #16

Re: 500 KV Auto Transformer with Oil to SF6 Bushing Test

04/01/2020 2:14 PM

"haysam", . . . it would appear that you are not capable of describing the transformer you have. It may be best for you to post the NAMEPLATE of the transformer before things get to far out of hand.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Oct 2013
Location: Saudi arabia
Posts: 40
#19
In reply to #17

Re: 500 KV Auto Transformer with Oil to SF6 Bushing Test

04/01/2020 2:22 PM

thanks for your support i will send it

but my question is how the sf6 affect the power factor and capacitance test to take decision

Register to Reply
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!