Water well is OUT

Water well runs on 120v

Circuit does NOT trip in Circuit Box

ONLY the Ground Fault Outlet keeps tripping

The Ground Fault outlet IS working ( tested with other device)

As soon as water well plug is inserted it trips the Ground fault

THIS is what the end of the Capacitor looks like... A brown crud like rust but NOT flaky?

Everything else looks good.

Guesses on this situation?

__________________
There is no recall from extinction.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15620
Good Answers: 986
#1

Re: Is THIS a Blown Capacitor ????

04/12/2020 12:12 PM

My WAG is that you are looking at the blown vent cap of an electrolytic capacitor. If you are lucky the now dry (no electrolyte) capacitor plates shorted out to the case and tripped the GFCI before other damage occurred. In other words, just replacing the capacitor with an identical value in farads and a voltage value the same or greater can return this motor to operation.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Guru

Join Date: Mar 2007
Location: Cajun Country , USA
Posts: 1498
Good Answers: 23
#2

Re: Is THIS a Blown Capacitor ????

04/12/2020 12:30 PM

Another view....Still think its the capacitor? Thank you for the input.

__________________
There is no recall from extinction.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15620
Good Answers: 986
#3
In reply to #2

Re: Is THIS a Blown Capacitor ????

04/12/2020 12:44 PM

Yes I do. Where's the electrolyte? An electrolytic oil should be inside that vessel. It looks like the failure that popped the vent blew all of the failing electrolyte out, a common failure scenario. Regardless it looks like you need to replace that opened capacitor anyway.

If you are not lucky, a motor winding insulation is breaking down to the case thus still causing a ground fault.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9940
Good Answers: 1148
#18
In reply to #3

Re: Is THIS a Blown Capacitor ????

04/13/2020 8:14 PM

I believe you're right. It looks like a non-polarized electrolytic start capacitor.

A typical motor start capacitor, as can be seen by its black colour and can shape

https://en.wikipedia.org/wiki/Motor_capacitor

The electrolyte (brown rusty looking stuff) is a conductor and when it leaked out could very likely have created the sneak path to ground causing the ground fault interrupter to trip.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6219
Good Answers: 248
#7
In reply to #2

Re: Is THIS a Blown Capacitor ????

04/13/2020 1:14 AM

I agree it's probably blown. Since it has four terminals, it's probably two capacitors in one case; a starting capacitor and a smaller running capacitor. They are pretty cheap, but make sure you get the correct unit: Same values of capacitance, and the same or a higher voltage rating as the original. If there is a temperature rating given, the replacement should have the same or a higher temperature rating.

Newer capacitors are commonly smaller in physical size than the originals. If that is the case, make sure to use some form of heat-resistant padding, so the capacitor can't vibrate when the motor is running.

When you reassemble the unit, make sure each of the four (or possibly three) wires goes to its correct terminal. Hopefully, you took a photo before disconnecting the wires. If not, study the motor's diagram on the plate. It should identify the correct terminals.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9940
Good Answers: 1148
#4

Re: Is THIS a Blown Capacitor ????

04/12/2020 1:10 PM

The ground fault essentially measures the difference between the current in the hot side and neutral side. If these are not equal, part of the current is returning to the source via the ground and the ground fault trips. A conduction path to the ground can be either on the hot or neutral side of the pump.

Take the plug for the pump and measure between both the hot and neutral to the ground prong. It should be an open circuit. Check it with the capacitor removed from the circuit. My guess is that the corrosion on the capacitor may be providing a ground path.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#5

Re: Is THIS a Blown Capacitor ????

04/12/2020 7:06 PM

First test:Disconnect the pump with only the capacitor connected.(Motor disconnected from cap and circuit).

If it trips, the capacitor is bad,but there may be another issue involved.

Cap Testers do not use a high voltage for testing,so it may be breaking down under line voltage.

Be sure to ground the capacitor to the ground wire of the supply conductor when you remove it from the motor circuit.

Test# 2 If it trips,remove the capacitor from the circuit,and test the circuit with nothing connected at the pump end of the line.

If it trips,there is a nick in the wiring to the pump,or the wiring insulation is breaking down.

I suspect the capacitor is bad.

I have never seen a good capacitor with a leak outside of the case,in over 50 years of electrical work.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Power-User
Engineering Fields - Biomedical Engineering - New Member Fans of Old Computers - TRS-80 - New Member

Join Date: Aug 2009
Location: Omaha, Nebraska (fly-over country USA)
Posts: 406
Good Answers: 7
#6

Re: Is THIS a Blown Capacitor ????

04/12/2020 10:27 PM

When I was younger (before going to college for electronics) I used to connect small electrolytic capacitors to 110VAC (US).

I'd stand back, watch them smoke then explode. I would find paper shrapnel from the internal wrapping - did you find any paper bits? Tell tale sign of bad electrolytic.

After working on medical equipment, they had electrolytic capacitors the size of a beer can - ALWAYS wanted to connect one of those to AC. Tried to act grown up tho……..

__________________
The most exciting phrase to hear in science, the one that heralds new discoveries, is not "Eureka" but rather "Hmmmmm...that's funny" - Isaac Asimov 1920-1992
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#10
In reply to #6

Re: Is THIS a Blown Capacitor ????

04/13/2020 6:25 AM

I once had a problem keeping goats in their pasture.

The soil was very dry and it was not sufficient to provide a noticeable shock through the leaves and grass,and their dry hooves.

I decided to up the voltage a bit.

I put a high voltage tripler from a color TV on the output.

The output went from 5kv to about 25 kv.

A neon test screwdriver would light up about 5 feet away from the fence.

The goats could smell the ozone and stayed away..for while.When the dew hit the insulators the next morning,it shorted the output,and they got out again.

I removed the tripler,and put a motor start capacitor in parallel with the standard one to give it more"kick".

As I walked away from the charger,I heard a loud explosion behind me.

There was a stringer of aluminum foil and paper leading from about 20 yards away back to the terminals of the cap inside of the charger box.

The cap had been borderline- bad and I didn't test it first,and it could not handle the intermittent load.

There was one escape artist that always led the whole herd out.

I tried everything to stop him,to no avail.

Never try to out stubborn a goat or a cat.

I found that the only way to beat a goat is to eat a goat,so I did.

He was put on the rotisserie after I had him castrated and grazed him for a few months to reduce the musk.

The others must have seen what happened to him because I had no more escapees after that.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Off Topic (Score 5)
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 812
Good Answers: 65
#8

Re: Is THIS a Blown Capacitor ????

04/13/2020 5:00 AM

Most definitely blown so when you get a replacement capacitor make sure you test the capacitance with a capacitance meter and get one that is close as possible to the original value. You will find that they are quoted as +10% -20% but I have never found one that has been +10%. Just replaced one in a water pump and the value on the case of the new one was 10uF but tested at 8uF. I needed an 8uF so I used the one that measured 8uF. The 8uF I changed out was down to 4uF and the pump was having trouble getting started. This is a common failing as the quality goes out of the capacitor

Not being familiar with 120AC as 240 AC is the norm here but the replacement cap for 240VAC is 450vAC or 600VAC motor start duty.

Don't buy a metal can capacitor if you can help it as they fail more often as the motor heat is transferred to the internals from the motor heat and not the other way around and the plastic case insulates the internals should they fail.

Normally the Capacitors are not electrolytic but paper/mylar and the liquid is not electrolyte but insulating oil.

Don't think buying Brand Name capacitors guarantees you quality, sure you pay more but I have just had to change 75uF 450VAC capacitors out on a power correction filter in a welder. I pulled them apart and they all had a common connection problem where the connecting wire had arced the foil away. That is why I test every capacitor for value and Q factor, before installation, buyer beware

__________________
Hare today, goon tomorrow!
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6219
Good Answers: 248
#16
In reply to #8

Re: Is THIS a Blown Capacitor ????

04/13/2020 11:53 AM

A blown capacitor essentially never has its original capacitance, so measuring it with a capacitance meter tells you very little about what value to buy.

Hopefully, NM can either read the values from the Cap or from the motor plate. Or possibly read a part number for direct replacement.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: Jul 2008
Posts: 1693
Good Answers: 145
#9

Re: Is THIS a Blown Capacitor ????

04/13/2020 5:55 AM

Any markings on the sides or top of the capacitor body?

__________________
Few things limit our potential as much as knowing answers and setting aside questions.
Register to Reply
Guru

Join Date: Mar 2007
Location: Cajun Country , USA
Posts: 1498
Good Answers: 23
#12
In reply to #9

Re: Is THIS a Blown Capacitor ????

04/13/2020 6:58 AM

yes... lots of data I do not understand.

__________________
There is no recall from extinction.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#11

Re: Is THIS a Blown Capacitor ????

04/13/2020 6:40 AM

After looking more closely at your first picture,you may have had water getting into your capacitor,evidenced by the rusty enclosure.The terminal looks very close to the metal fitting,and there may have been an arc at some time that shorted the capacitor,or there could be a path for leakage current to get to the ground,which will trip a G Fault breaker.

It only requires .005 amps to trip a GFCI, not even enough to create a visible arc.

Sometimes they will trip due to the arching of the plug when inserted into the receptacle.so a good practice is to plug in the load first with the breaker off,then turn on the breaker.

However,I am still betting that the capacitor is bad.

When you replace the capacitor,put a layer of clear silicone caulk around the terminals and the case seal to guard against water damage in the future.

Please let us know what you find.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Mar 2007
Location: Cajun Country , USA
Posts: 1498
Good Answers: 23
#13

Re: Is THIS a Blown Capacitor ????

04/13/2020 7:00 AM

OK.... Thank you all for the input.

I have a friend in the electrical supply business that says he has one that will work.

Thank you all for helping .

__________________
There is no recall from extinction.
Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#14

Re: Is THIS a Blown Capacitor ????

04/13/2020 8:45 AM

Remember the 7-up commercial where the athlete gives a kid a bottle of 7-up and says "here catch" while tossing him his dirty laundry?

That was my cousin growing up, but instead of soda and laundry it was charged capacitors.

.... Goats leave him alone too

__________________
High Tolerance is Beautiful
Register to Reply
Guru

Join Date: Mar 2007
Location: Cajun Country , USA
Posts: 1498
Good Answers: 23
#15
In reply to #14

Re: Is THIS a Blown Capacitor ????

04/13/2020 9:41 AM

ha ha ha ha

__________________
There is no recall from extinction.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#17
In reply to #14

Re: Is THIS a Blown Capacitor ????

04/13/2020 12:15 PM

I used to do that too when I was a kid,messing around with TV's(only black and white back then) and had no idea what I was doing.Mainly just tube swapping.

I got zapped by a charged cap,and the gears began to turn...Hmm?.....

My first victim was my older brother.I had to hide for the rest of the day.

I fixed a lot of tv's and radios in the neighborhood,and got a reputation as the go to guy for TV and radio repair.

I learned a lot over the years,and learned to troubleshoot boards down to the component level.

I am now long retired and content.

I have been blessed by the good Lord and saved from my own stupidity many times,and for that I am most grateful.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32212
Good Answers: 839
#19

Re: Is This a Blown Capacitor?

04/14/2020 3:24 AM

As these things are usually less than £10GBP including postage it is not worth arguing about it. Just replace it with a new one, and try again, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

BruceFlorida (1); dkwarner (2); HiTekRedNek (4); JE in Chicago (1); netmaker (4); PWSlack (1); redfred (2); Rixter (2); Sid_Sidow (1); Stef (1)

Previous in Forum: UVC Light Used to Replace Pesticides on Farms   Next in Forum: What is it?

Advertisement