Fault Level of Substation

04/18/2020 3:25 PM

We have a substation which has 4 transformer. 1×33/11kv, 3×33/6kv. All are 5mva each. Supply coming from a government bigger substation located 5 km away. What is the fault level of this substation?

I do not know how to calculate. Searched internet but not found something. Please help.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Fault level of substation

04/18/2020 3:46 PM

There is a theory that says it takes a chain of only six telephone calls to reach anyone on the planet. So, start making calls until the team running the <...government bigger substation...> can be asked the question and give a satisfactory answer.

Simples ξ.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2

Re: Fault level of substation

04/19/2020 12:57 AM

I agree with PWSlack if you know these 6 numbers and could trust them...However, in this Covid-19 era..I agree with you.

When I was 22 and MS in Electrical Machines, my first job was -in a utility distribution unit- to calculate a voltage drop. After days of deep study I did it!

That remember me the Baudelaire "l'Albatros": His big wings bother him to walk.

A vague appreciation-let's say "proportions"-you can get from IEC 60076-5 Power Transformer Ability to withstand short circuit-for instance: for 33kV system 1000 MVA short-circuit should be the limit.

Zsys=33^2/1000=1.089 Ω

From ABB Switchgear Manual vol.3 Fig. 3-14 an overhead line of 36 kV 70 mm^2 ACSR presents Z1=0.38 Ω/km that means total 5*0.38= 1.9 Ω.

If we take 33 kV as base voltage the three phase short-circuit apparent power at transformer high voltage terminals will be: Ssh=33^2/(1.089+1.9)=364.3 MVA Isc=364.3/sqrt(3)/33=6.37 kA

Transformer uk%=7% [minimum according to IEC 60076-5]

At secondary transformer terminals [keeping the same reference voltage 33 kV] Ztrf=33^2/5*7%=15.25 Ω

Ztot33kV=1.089+1.9+15.246=18.235 Ω

Sshtrf=33^2/18.235=59.7 MVA

So for 6 kV Isc will be 59.7/sqrt(3)/6=5.74 kA and 3.13 kA for 11 kV.

__________________
Julius
Reply Score 1 for Good Answer
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#3

Re: Fault Level of Substation

04/20/2020 12:02 AM

The good information you received is half of the information you need to calculate the available fault energy. The other half is the amount of time for any upstream protective device (probably a fuse) to clear the fault. If you can't find the clearing time then you can use the anticipated amount of time for a person to escape the area after a fault (crawl, walk, be blown through the air, or whatever)--this usually is 2-10 seconds. The available fault energy is a function of I2t. Since all of this is presently guesswork you need to follow the advice also given--to ask the supervisors or engineers at the substation.

--JMM

Reply
Reply to Forum Thread 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); jmueller (1); PWSlack (1)

Previous in Forum: Motor Starter for 250 KW 3 Phase Induction Motor   Next in Forum: Rated Enclosure Class

Advertisement