Anonymous Poster #1

Rated Enclosure Class

04/21/2020 6:05 AM

Hi,

What is rated enclosure class 15? I have found it in a Siemens product specification but I couldn't gather further information from Siemens.

In the NEMA website, I found an enclosure class up to 13. What is 15? Or is it something else? If anyone is familiar, please help.

Thank you.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Rated Enclosure Class

04/21/2020 6:14 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2
In reply to #1

Re: Rated Enclosure Class

04/21/2020 6:18 AM

...so <...enclosure class 15...> should therefore read IP15.

https://en.wikipedia.org/wiki/IP_Code

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#3

Re: Rated Enclosure Class

04/21/2020 6:19 AM
__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Rated Enclosure Class

04/21/2020 7:57 AM

I’ve never seen anything made to IP15 before. That would be somehow only be able to stop items larger than 55mm, but at the same time stop water???

More than likely it’s a typographical error.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#7
In reply to #4

Re: Rated Enclosure Class

04/21/2020 9:29 AM

IP65 = First Digit - Solids

The first digit indicates the level of protection that the enclosure provides against access to hazardous parts (electrical conductors, moving parts etc) and the ingress of solid foreign objects.

IP65 = Second Digit - Liquids

The second digit defines the protection of the equipment inside the enclosure against various forms of moisture (drips, sprays, submersion etc).

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#8
In reply to #4

Re: Rated Enclosure Class

04/21/2020 10:28 AM

The hand cannot carry a glass of water.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#9
In reply to #8

Re: Rated Enclosure Class

04/21/2020 12:36 PM

Consider a pedestal mounted floor fan.

The guard keeps hands and fingers out.The exclusion is for objects up to 50 mm,not only 50 mm.They drop a 50 mm ball on the enclosure for testing.

The openings must not be larger than 50 MM.

The motor on the fan can be waterproof.

The hand could spill the water on the motor with no problem.

Make sense now?

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply Off Topic (Score 5)
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#10
In reply to #8

Re: Rated Enclosure Class

04/21/2020 12:44 PM

IP refers to Intrusion Protection.

The 50MM refers to the maximum opening size in the enclosure.

A 50 mm ball should not pass through,such as a fan guard.

The motor on the fan inside of the enclosure can be waterproof,dust proof,etc.

Picture a pedestal fan with a guard over the fan blade but an enclosed motor and shaft.

Spilled water will pass through the guard,but will not intrude on the motor.

A single enclosure can do it all in some cases.

https://www.nemaenclosures.com/blog/ingress-protection-ratings/

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#17
In reply to #4

Re: Rated Enclosure Class

04/22/2020 1:41 PM
IP15Protected from touch by hands greater than 50 millimeters.Protected from low pressure water jets from any direction.

http://www.dsmt.com/resources/ip-rating-chart/

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#19
In reply to #4

Re: Rated Enclosure Class

04/27/2020 1:29 AM

I too think so. Surprised, why IEC doesn't indicate any guidance!

__________________
Raghunath
Reply
Anonymous Poster #1
#5

Re: Rated Enclosure Class

04/21/2020 8:27 AM

Actually IP class was mentioned separately as IP23 for Transformer Panel and IP54 for MV/LV panel. But again rated enclosure class was mentioned as 15. That's why I am confusing.

The above specification is for a Ring Main Unit panel of 11kV/415V.

Thanks.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Rated Enclosure Class

04/21/2020 8:55 AM

Something is wrong, then. Go back to the originator of the information, and ask there.

It only takes a chain of 6 phone calls to reach anyone on the planet. Try it and see whether or not it works!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 807
Good Answers: 65
#12
In reply to #6

Re: Rated Enclosure Class

04/22/2020 3:44 AM

What a lot of rubbish! May only work pre covid19 and when not dealing with an item manufactured in China, Korea or Taiwan, get real with your answers!

__________________
Hare today, goon tomorrow!
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #12

Re: Rated Enclosure Class

04/22/2020 4:14 AM

A company of the same quality as <...Siemens...> will have laid in provision for these difficult times and at the moment, the forum has no idea where Anonymous Poster #1 is on the planet and where the installation is located.

"I haven't failed. I've simply found a hundred ways that don't work." - Anon.

Invitation declined.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#15
In reply to #13

Re: Rated Enclosure Class

04/22/2020 9:30 AM

I am from India and the installation is located in city of Kolkata.

Anyway thanks for your suggestion. I'll have to check with the supplier.

What are some operational and maintenance difficulties that may arise with compact outdoor substation of 2mva? If anyone has practical experience please share.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #15

Re: Rated Enclosure Class

04/22/2020 11:01 AM

All manner of things.

However, for a more concise local answer it would be best to contact directly people experienced in these things in the same general locality. The forum does not have their phone numbers nor the incentive to make the calls.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Hobbies - CNC - New Member

Join Date: Aug 2006
Location: Western Australia
Posts: 767
Good Answers: 58
#11

Re: Rated Enclosure Class

04/22/2020 2:51 AM

IP15.

First letter - 1 = protection for hand and items no smaller that 50mm.

Second letter - 5 = Protected from low pressure water jet (6.3mm) from any angle.

In other words you can't get your hand into it and you can hose it down.

__________________
If you can't explain it simply, you don't understand it well enough. (A.E.)
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#14

Re: Rated Enclosure Class

04/22/2020 5:18 AM

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Score 1 for Good Answer
Anonymous Poster #2
#18

Re: Rated Enclosure Class

04/23/2020 7:10 AM
Reply
Reply to Forum Thread 19 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); HiTekRedNek (4); JRaef (1); PWSlack (4); raghun (1); redfred (1); SolarEagle (3); Stef (1); The Prof (1)

Previous in Forum: Fault Level of Substation   Next in Forum: How Can I Solve This Stability Determining Problem?

Advertisement