Lightning Arrester Selection

05/05/2020 2:35 PM

I have a 75kVA, 3 phase 50Hz, 11kV/415V pole mounted transformer for incoming. It is Dyn11 with neutral solidly grounded. I want to select an lighting arrester. Should I check with the electric supply company about the transformer connection and neutral grounding details from which I am receiving supply? I mean how do I decide on TOV, short circuit current withstand and nominal discharge current rating. I have read some online papers but It's still not clear to me. I may be asking some obvious questions. I am sorry for that but please help me with this.

Thank you.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Lightning Arrester Selection

05/05/2020 6:17 PM

I would refer to the power utility for the location this transformer will be installed for advice. All of your concerns are related to your local weather and local power grid configurations.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Score 1 for Good Answer
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 807
Good Answers: 65
#2

Re: Lightning Arrester Selection

05/05/2020 10:31 PM

Check with the supply utility as in Aus the transformers come connected with primary and secondary surge diverters/lightning arresters. If you wish to protect your incoming supply then they should be able to advise you on the KA rating and class of arrester you can use on your incoming supply. There are also three phase units made by a number of manufacturers to help suppress the incoming spike and I have installed a number of these units in the past on buildings to protect the computer systems and office equipment.

__________________
Hare today, goon tomorrow!
Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3

Re: Lightning Arrester Selection

05/05/2020 11:19 PM

The main thing to find out is if the line you are fed from can be considered effectively grounded. We normally assume ungrounded for lines like that, so your line protector steady stare voltage is equivalent to line potential, 11kV to ground for surge arrestor steady state conduction withstand voltage without damage. This varies with the surge protector design, and how important this transformer is to your operation. Experience and budget will dictate the amount of energy can be transferred when the voltage exceeds the conduction threshold. More capacity, lower likelihood of transformer damage.

You can get some estimate from the utility of how long a low current ground fault could persist on their line, overhead lines can flash and be hit multiple times to ground, but you typically can’t count on covering all possible situations.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Lightning Arrester Selection

05/06/2020 3:22 AM

A <...75kVA, 3 phase 50Hz, 11kV/415V pole mounted transformer...> is an unlikely object to <...have...> in the private domain, as few in that domain will have the necessary skills to deal with the <...11kV...>, making this a very strange and alarming post. Merely asking the question in an open forum convinces readers that the necessary skills and training are not to hand.

In all cases of <...Should...check...>, open a dialogue with the <...electric supply company...>, and have its trained staff handle all of it, for safety's sake, as getting it wrong involves half a day out with the local Undertaker and the remainder a lifetime of sorrow for loved ones. A suitable telephone number will be found on the latest bill for payment from that organisation.

If the above is to be ignored, then please ensure that all other CR4 readers are some distance away during the work activity.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PWSlack (1); redfred (1); rwilliams (1); Stef (1)

Previous in Forum: Powering a WW2 Searchlight   Next in Forum: Motor Terminal Overvoltage in Steady State by Using VFD in ETAP Analysis

Advertisement