Motor Terminal Overvoltage in Steady State by Using VFD in ETAP Analysis

05/09/2020 12:59 AM

Dear CR4 forum members,

When I analyze motor starting by using VFD starter with ETAP software, I found voltage level at switchgear bus is still nice & only small voltage dip happened. But I shocked when I found the motor terminal voltage level to be 220% of nominal voltage until steady state condition. I analyze big motor rating (315 kW, 400V) with high torque load (such as conveyor).

Any CR4 member ever have similar case with me? Any explanation why this overvoltage happened continuosly until steady state condition? Is it possible?

Many thanks,

ATOM, Indonesia

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Motor Terminal Overvoltage in steady state by using VFD in ETAP Analysis

05/09/2020 1:22 AM

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Motor Terminal Overvoltage in steady state by using VFD in ETAP Analysis

05/09/2020 3:25 AM

GIGO perhaps?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#4
In reply to #2

Re: Motor Terminal Overvoltage in steady state by using VFD in ETAP Analysis

05/12/2020 7:13 AM
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3

Re: Motor Terminal Overvoltage in Steady State by Using VFD in ETAP Analysis

05/09/2020 10:37 PM

If you reversed the sign of the conveyor load, it might look like an induction generator, which would cause the voltage to be very high. In the real world, decelerating a heavily loaded conveyor too quickly can cause overvoltage.

There has to be something wrong with the input parameters, in any event.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Motor Terminal Overvoltage in Steady State by Using VFD in ETAP Analysis

05/16/2020 2:20 PM

Well, that's nonsense. So something is wrong with the model in the <...ETAP software...>.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); PWSlack (1); rwilliams (1); SolarEagle (1); Tornado (1)

Previous in Forum: Lightning Arrester Selection   Next in Forum: How Do I Fix the Rectifier Voltage Fluctuation in CEG AC UPS?

Advertisement