Replacement of Transformer

05/16/2020 11:51 PM

Dear all

Question on the subject of electric power:

please can any one help me to solve this question

two synchronous generator each have (50MVA,10KV,0.8PF) connected to power

transformer have three winding (LV1(delta),LV2(delta) and HV(star) rated power

(55MVA,55MVA,110MVA) rated voltage (10,10,132)KV. this transformer replaced by

another transformer have tow winding only((LV(delta),HV(star)(110MVA)(10/132KV)

the questions:

1- if we replaced the transformer are there any limited in generator load

2- after we replace the transformer the generators will connected to same busbar

in low voltage side(delta side) are the generators will effected.

thanks for all

Register to Reply
Pathfinder Tags: replace of transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#1

Re: replace of transformer

05/17/2020 1:06 AM

I am afraid the fault levels of 10kV bus will go up considering that the two generators are now paralleled at 10kV bus before taken to the transformer 10kV terminals.

It may also increase the fault current contribution to 11kV bus from generators but this may not be much of a concern.

__________________
Raghunath
Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: replace of transformer

05/17/2020 3:35 AM

Is there a qualified Electrical Engineer at the facility that might help?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: replace of transformer

05/19/2020 8:08 AM

...after all, <...we...> seems to suggest that there is one...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3

Re: Replacement of Transformer

05/18/2020 7:09 PM

As Raghun explains, the fault current will increase considerably at your generator breaker. A three winding transformer is a common way to limit fault current between two high fault current sources, especially with local generation. The contribution from one generator has to pass through 2 reactances to get to the other generator breaker. As a guess, you need 1000MVA switchgear for your breakers. The decision to replace the transformer with a different type is likely a mistake that could result in an explosion or fire if both generators are on line and one of the breakers is commanded open by fault relaying.

The likely economical fix for this mistake is to purchase and install a pair of series reactors between each breaker and the transformer, restoring the missing impedance provided by the original transformer winding configuration.

When you consult an actual electrical engineer to size the reactors, you should confirm the actual fault duty of the generator breakers, based on current data, including the subtransient reactance of the generators.

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

PWSlack (2); raghun (1); rwilliams (1)