Contractor Coil Voltage

05/15/2020 6:52 AM

Hi all

in one of the projects, we have a 6KW 415v Split Ac for cooling of Panels and a rectifier circuit.

we have used Main breaker, 3phase Overvoltage and undervoltage protection relay - a 4p contactor - after that supply is split and has Mcb and rcb combo which in turn will connect to the Split Ac and rectifier circuits.

the logic here is whenever voltage is normal , contactor will be closed and power the AC and Rectifier circuits and in case of overvoltage/ undervoltage They are shutdown
It is also controlled thorough a controller which takes all the input and has the ability to trip the main breaker

I was going through the circuit and I found that the OV UV relay is powered From mains 415vac and then it is used to power a 230V aux relay. the contacts of this relay is wired to the 24vdc coil of the contactor Which will do the switching and power the AC

Now the question:

can we not optimise this slightly complicated system

any ideas would be appreciated

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Contractor coil voltage

05/15/2020 7:14 AM

There are usually no extra controls in a system....what you want to ask yourself is what will change if I remove this part of the system...everything is usually there for a reason, unless the system has been modified in some way from its original design ...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#2

Re: Contractor Coil Voltage

05/15/2020 1:34 PM

Optimized for what; lowest or highest parts count, reliability, profit margin, flexibility, standardized parts, cooling, heating, accurate failure mode detection, other?

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3

Re: Contractor Coil Voltage

05/15/2020 11:43 PM

It is likely that the rating of the voltage sensing relay output is not robust enough to handle reliably the 24v trip coil current & especially interruption. The interposing relay also adds the possibility of remote monitoring of the equipment, as an option for the upgraded version of your equipment.

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4

Re: Contractor Coil Voltage

05/16/2020 12:27 AM

It’s general practice to have all trip circuits and protective circuits in 24 V, independent of source.

The existing system is best with out any interference from AC source.

In this case for any over voltage the contractor coil will not get damaged.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Guru

Join Date: Dec 2009
Location: Land of Shining Waters
Posts: 916
Good Answers: 35
#5

Re: Contractor Coil Voltage

05/16/2020 9:10 AM

There seems to be a suggestion in this thread that it is not even legitimate to ask: Is there a simpler and more elegant method to achieve the same result? Opposition to the posing of this question is an odd attitude to find on an engineering forum - the attitude that this is the way it is done, the way it has always been done, and there is no better way to do it. The question of the original poster is specific to an electrical control circuit, but regardless of the field of endeavor, the question, taken in its generality, is the question that drives innovation. The majority of granted patents make no claim that they accomplish what has never been done before, but that they do exactly what has been done before, but in a simpler, more elegant manner.

__________________
It is easier to let the cat out of the bag than to put the cat back in the bag.
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Contractor Coil Voltage

05/16/2020 1:39 PM

<...the OV UV relay is powered From mains 415vac and then it is used to power a 230V aux relay. the contacts of this relay is wired to the 24vdc coil of the contactor Which will do the switching and power the AC...>

The simplest system would be to do away with all that rubbish altogether, and simply lob a suitably sized crowbar across the open-circuit conductive parts when an electric circuit is needed. That would work too.

What <...we...> does is regulated by the end Client's construction standards. The word <...we...> indicates there is more than one at that location. So why not discuss it among the rest of the <...we...> instead, and find out why it has been done that way, straight from the proverbial horse's mouth?

The forum knows nothing about the Client's standards, because the <...we...> has deliberately withheld this information from it.

Go figure.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard