Voltage Between Earth and Neutral 220V

06/07/2020 5:43 AM

the volatage between earth and neutral is 220 V. there is no continuity between the neutral and earth. and also between phase R and earth its 380 V, Y and earth is 380 V, while blue phase and earth is 34 V. regarding the phase and neutral is 220 for all phases.

i thought the earthing is not good i prepared a new earth pit then the voltage between earth and neutral was 3 volt and after 2 days again there is 220 v. i checked there is no continuity between earth and phases.. i am stuck with it can any body please suggest me why this is happening and whats the solution is.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: voltage between earth and neutral 220V

06/07/2020 6:18 AM

What are your phase to phase readings..? What do you expect to see in each of these readings?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Associate

Join Date: Jan 2018
Posts: 26
#4
In reply to #1

Re: voltage between earth and neutral 220V

06/07/2020 7:54 AM

phase to phase in 384.. ry, yb, br all same... but exact resaon i cannot find why there is 380 V between earth and phase for r and y phase. i checked with clamp ammeter 0.4 A in neutral and .34 A in earth.... and when i switch of all the machine connected to the distribution board and short the neutral and ground and remove the short phase to neutral is 20 V for all the r, y, b.

another thing my Distribution panel is connected to a distribution transformer. the secondary side has 3 phase and neutral as usual. the body of transformer is grounded. there is no problem with the phase to neutral. its 220 with all the phase and no unbalance is found.

earth and neutral need to be at same potential if the short earth and neutral will i be able to find a solution with compromising the safety factor.

Register to Reply
2
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#2

Re: voltage between earth and neutral 220V

06/07/2020 6:22 AM

Apparently there is a loose or corroded connection to Earth.

A differential voltage between two conductors means a resistance exists between them.

Check all connections.Galvanic corrosion,vibration etc.can cause unreliable connections.

CAD welding is the preferred method for connection to a grounding grid instead of crimp or clamp style.

Even dissimilar metals can be bonded with this method.

https://www.uedinc.com/pdf/cadweld_exothermic_welding_manual.pdf

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Good Answer (Score 2)
Associate

Join Date: Jan 2018
Posts: 26
#5
In reply to #2

Re: voltage between earth and neutral 220V

06/07/2020 7:55 AM

i check teh continuity of the earth from panel to pit , pit to distribution panel board it 0.8 ohms.

Register to Reply
Associate

Join Date: Jan 2018
Posts: 26
#3

Re: voltage between earth and neutral 220V

06/07/2020 7:53 AM

phase to phase in 384.. ry, yb, br all same... but exact resaon i cannot find why there is 380 V between earth and phase for r and y phase. i checked with clamp ammeter 0.4 A in neutral and .34 A in earth.... and when i switch of all the machine connected to the distribution board and short the neutral and ground and remove the short phase to neutral is 20 V for all the r, y, b.

another thing my Distribution panel is connected to a distribution transformer. the secondary side has 3 phase and neutral as usual. the body of transformer is grounded. there is no problem with the phase to neutral. its 220 with all the phase and no unbalance is found.

earth and neutral need to be at same potential if the short earth and neutral will i be able to find a solution with compromising the safety factor.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#6

Re: voltage between earth and neutral 220V

06/07/2020 8:10 AM

If possible, disconnect all loads (open breakers). It appears there is a fault between the blue phase and earth somewhere. If the problem disappears with all breakers open, close them one at a time until the problem returns.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7

Re: Voltage Between Earth and Neutral 220V

06/07/2020 10:18 AM

"there is no continuity between the neutral and earth."

Get your terminology correct or nobody will understand what you are doing. You do not have a neutral. By definition a neutral is bonded to earth. With proper bonding the bonding connection between earth and neutral needs to only sustain a fault current long enough for automatic disconnects (fuses and circuit breakers) to interrupt the fault condition. You might have a return and how this node interacts with your three phases is the key to your dilemma.

You must identify how the power transformer wiring, particularly the secondary wiring.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8

Re: Voltage Between Earth and Neutral 220V

06/07/2020 3:43 PM

the volatage between earth and neutral is 220 V. there is no continuity between the neutral and earth.

Down here that would be a big red flag as the earth and neutral need to be solidly connected (both at same 0V potential) as we run a MEN (multiple earth neutral) earthing system.

I don't know what country or earthing system you are running but if it is similar you need to check your earth neutral bond in your switchboard.

__________________
jack of all trades
Register to Reply
Power-User

Join Date: Feb 2020
Posts: 482
Good Answers: 7
#9

Re: Voltage Between Earth and Neutral 220V

06/07/2020 10:34 PM

Please provide a clearly labelled schematic of the voltage source and load, and the circuitry between them.

__________________
Light is only half of what you think it is.
Register to Reply
2
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#10

Re: Voltage Between Earth and Neutral 220V

06/07/2020 11:33 PM

Blue phase, reading only 34 volts to ground, has an earth fault on it, or is intentionally grounded such as a corner delta ground, as was done years ago.

The system is otherwise ungrounded, whether intentionally or not. That is why you do not measure 220 volts phase to ground/neutral on all 3 phases.

Your ground fault current is drying out your earthing connection, possibly.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Voltage Between Earth and Neutral 220V

06/08/2020 2:02 AM

One of the possibilities is a loose or missing neutral-to-earth link at the main distribution transformer.

Have the local utility supplier check this out and report before proceeding.

This is a safety issue. The system should remain isolated until the above report is to hand.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jan 2018
Posts: 26
#13
In reply to #11

Re: Voltage Between Earth and Neutral 220V

06/08/2020 4:03 AM

thank you for your valuable comment,

you are right the neutral ground bonding has been intentionally cut by whom and why have got no idea. but the earthing for the equipments is good.

our system not make use of the neutral so the person who or organization who made the connections left out neutral wire and instead used this wire as body ground which is connected to the earth of the factory. so personal safety is not compromised. but still the neutral bar which is not grounded have connections to the light and air conditions due to which a residual voltage (or floating neutral) is found.

what i paln is to shut down the particular transformer and make a separate earth pit and connect the neutral to this earth pit.

and would like your suggestions regarding this solution or another most feasible solution.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#14
In reply to #13

Re: Voltage Between Earth and Neutral 220V

06/08/2020 10:58 AM

It’s possible that the earth fault on the blue phase could not be found or repaired easily, so essentially converting the system to ungrounded operation allows continued operation.

That is, until a second ground fault occurs on a different phase. This now becomes a phase to phase fault, and will activate your protection.

Adding a 10 ohm ~500 watt resistor between neutral and ground converts your system to high resistance grounding, then you can use a loop type galvanometer to trace the location of your ground fault, if it comes to that.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #13

Re: Voltage Between Earth and Neutral 220V

06/09/2020 1:46 AM

If the neutral link is missing then the installation becomes an IT one, in which case improving the local earth will achieve diddly squat.

A discussion with the local distribution network operator is overdue, on safety grounds.

Who is to blame is irrelevant.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Voltage Between Earth and Neutral 220V

06/08/2020 2:31 AM

Another thing to try is to connect a low-wattage filament lamp between neutral and earth upstream of all residual current devices briefly, and measure again.

Remove the lamp immediately after measuring.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#15

Re: Voltage Between Earth and Neutral 220V

06/08/2020 4:57 PM

Quaiser,

Two important points you have mentioned:

First-- you "prepared a new earth pit then the voltage between earth and neutral was 3 volt and after 2 days again there is 220 v"

Second-- you measured 0.34A on the earth connection.

Another person suggested that the continuous current into the earth pit has dried it out and raised its resistance enough so the voltage has risen as you noted. R=E/I, so your pit resistance has risen to 220/0.34 or about 660 ohms.

Often an ungrounded (non-earthed) system is desired, if installed with earth detectors in place. Then the first fault to earth will be shown by the detector, giving you time to find it and repair it without a sudden and unplanned shutdown of your process. You don't mention having any earth detectors, so I assume you have a fault in the earth conductor.

Almost all power systems in plants will have capacitive and inductive coupling between the conductors and neutral. This can be anywhere from a few to hundreds of volts. You appear to have this along with the resultant neutral-earth voltage this causes because of an open earth connection.

As others have said, find the open earth connection and also check to find why you have 0.34 A on the earth conductor (it should be significantly less). This current is probably due to a high-resistance fault somewhere in your wiring or equipment.

--JMM

Register to Reply
Participant

Join Date: Jun 2020
Posts: 1
#17

Re: Voltage Between Earth and Neutral 220V

06/09/2020 11:48 PM

Hi, the problem is two parts. One is neutral to earth is more. Another B phase to neutral is very less.

The reason may be Bphase is getting connected to neutral with a very low resistance and neutral is not earthed solidly.

I hope your system is load side star and neutral solidly earthed.

If you are sure that the reasons mentioned above are not true, please check your transformer. Use multimeter to check continuity and IR tester for insulation values.

Like to hear the feedback from you

Ayyagari Srinivas

Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#18

Re: Voltage Between Earth and Neutral 220V

06/10/2020 1:09 AM

Why is blue a phase?

Most wiring schemes use blue as neutral and have brown/ red or grey/ black as phases.

Please check your local wiring regs. Sounds like someone mis-wired this. Error may not show up until new protection is added.

__________________
Madness is all in the mind
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #18

Re: Voltage Between Earth and Neutral 220V

06/10/2020 9:11 AM

Heritage installation: before the latest BS7671 changes, red/yellow/blue were phases and black neutral. Now, brown/grey/black are phases with blue neutral. Lots of potential (pun intended) to get it wrong now!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#23
In reply to #20

Re: Voltage Between Earth and Neutral 220V

06/10/2020 10:25 AM

Those changes were back in 2006.

I suppose someone who has qualified since then may have been working on another part of the system and crossed the blues.

__________________
Madness is all in the mind
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#24
In reply to #23

Re: Voltage Between Earth and Neutral 220V

06/11/2020 5:00 AM

That's why qualification as an Electrician takes several years' training and experience.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#25
In reply to #23

Re: Voltage Between Earth and Neutral 220V

06/11/2020 5:19 AM

That possibility doesn't explain why there is no continuity between neutral and earth, nor why the testing Electrician ignored it before its first energising nor why subsequent individuals testing it have also.

The original poster has not given details of the location of the installation. Were it to be in a hospital, for example, where IT installations are commonplace, one wouldn't expect continuity between neutral and earth except in the case of a first fault; generally a first fault will not stop the installation operating, which is vital to save lives if it were driving life support systems.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#26
In reply to #25

Re: Voltage Between Earth and Neutral 220V

06/11/2020 7:47 AM

Yes, we once again do not have sufficient information from the OP to provide clear guidance. One of the pivotal missing pieces of information is what region is this installation. We could then suggest which code the installation should be following.

From Wikipedia, here the National Electrical Code defines a neutral as this:

  • Neutral wire is the return conductor of a circuit; in building wiring systems, the neutral wire is connected to earth ground at only one point. North American standards state that the neutral is neither switched nor fused except in very narrowly defined circumstances. The neutral is connected to the center tap of the power company transformer of a split-phase system, or the center of the wye connection of a polyphase power system.

The United States electrical codes require that the neutral be connected to earth at the “service panel” only and at no other point within the building wiring system. Formally, the neutral is called the “grounded conductor”; as of the 2008 NEC, the terms “neutral conductor” and “neutral point” have been defined in the Code to conform to what had been common usage.[1]
If a conductor is not connected to earth ground then it is not a neutral! (The relevant NEC code is available to all after registering. The Wikipedia text was copied.)

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#27
In reply to #26

Re: Voltage Between Earth and Neutral 220V

06/11/2020 9:49 AM

Indeed.

British practice allows for variations.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#21
In reply to #18

Re: Voltage Between Earth and Neutral 220V

06/10/2020 9:44 AM

I don't know what the standard is now, but in the 1990's when I (in the USA) was engineering the electrical for a beverage can warmer being shipped to Australia, the required color code was Red/White/Blue for phases and Black for neutral. My panel builder had a challenge to do things that way.

I don't recall that we were told what country this installation is in.

--JMM

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#19

Re: Voltage Between Earth and Neutral 220V

06/10/2020 5:45 AM

...a stab in the dark...maybe a fault (I guess broken neutral) on a totally separate system using 'earth' as a (temporary return) - (or even intermittent phase/earth fault) thus causing a 'high' earth voltage at the place you test it....

...it could be a +220v earth to 0v neutral reading...

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Associate

Join Date: Jan 2018
Posts: 26
#22

Re: Voltage Between Earth and Neutral 220V

06/10/2020 10:15 AM

thanks for all the comment pwslack, jmueller, rwilliams and rest people thanks. this community solves most of the problem beside getting extra solutions and reason that may have caused that..

coming to the problem almost the problem is solved.. there are three drive 250 KW the cables shields for the output side is the reason i could find.. the shield is exposed and today it came in contact with the conductor resulting in the drainage of current through shield to the ground and causing OC fault. i think i need to reinstate the shield and insulating medium for the cable by electrical putty, rubber tapes then a copper braid above to connect to broken shields and again insulating with a rubber tape and pvc tape and at the end with the heat shrink tube.

its tedious so i would update as soon as possible. thank you

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Feb 2018
Posts: 13
#28

Re: Voltage Between Earth and Neutral 220V

06/11/2020 10:02 AM

If you share the transformer with a neighbor, the problem could be there. Or, the transformer bonding has failed. Talk to your electric utility.

Register to Reply
Register to Reply 28 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ayyagari srini (1); GM1964 (2); Haymaker (1); HiTekRedNek (1); horace40 (1); jack of all trades (1); jmueller (2); PWSlack (7); Quaiser (5); redfred (2); rick_shoop (1); Rixter (1); rwilliams (2); SolarEagle (1)