How to select the number of exhaust fan required. Fan size-450mm. Room is 4.5 meter × 3.7 meter x 3.5 meter height.
15kva ups and 60kw lt distribution supply at 415vac 3 phase is fed from here. Loads are located at field which is outside of the room.
Re: Electrical LT Distribution Room Ventilation
06/30/2020 3:02 PM
This 450mm fan - what is the rated volume of air moved per minute, please?
What is the free area of the proposed air intake grilles?
Is this room a stand alone building?
Is this room in Equador (warm) or Yukon Territory (cold)?
06/30/2020 6:13 PM
6200 m3/hr
Air intake from main door 1200mm × 2500mm.
No windows.
Equatorial.
06/30/2020 11:50 PM
You seem to have a fan that is driven at high speed, it should be slower,, much slower....by my calculation you are changing the air in less than a minute when only a tenth is required to be changed per min...Your exhaust fan should be as near the top of the room as possible, opposite the door intake...
https://www.ashrae.org/File%20Library/Technical%20Resources/Standards%20and%20Guidelines/Standards%20Intepretations/IC_62-1-2007-17.pdf
07/01/2020 2:48 AM
What is the risk of pulling rain into the room, especially at <tap, tap, tap, press equals...> 106 air changes per hour?