Layout of IPB (Insulated Phase Bus)

07/03/2020 8:38 AM

In our project, we are faced with the choice to either have the IPB cross through or over the firewall. Can someone please guide me as to which of the two layouts of IPB is better and what benefit does one have over the other? Can there be any concerns related to firefighting for any of these two options?

a. Above the Transformer Firewall

b. Through a hole in the Transformer Firewall

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Layout of IPB (Insulated Phase Bus)

07/03/2020 4:30 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Apr 2020
Posts: 15
#5
In reply to #1

Re: Layout of IPB (Insulated Phase Bus)

07/10/2020 11:36 AM

Thank you so much. Very helpful answer. I appreciate it.

Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#2

Re: Layout of IPB (Insulated Phase Bus)

07/04/2020 5:06 AM

I presume that you are referring to factory made sections of insulated busbar similar to the ISOBAR MR™ product. If the wall is not yet built, go through, pack round the bars with fireproof material in sachets and clad both sides with an insulating fireproof material. If the wall already exists then go over rather than cutting a new hole.

With factory made bars the shorter and simpler the layout, the cheaper it is to construct and the lower chance of mistakes. One reservation, make sure that you can get the bars through the hole. If there are bends or obstructions planned close to the hole inserting a long solid bar can create severe problems for the erection crew. Been there, made that mistake myself, don't follow my example. To be fair there were no obstructions present or on the drawings when I measured up but they had appeared by the time we came to install.

Cutting a hole in an existing wall, which as it encloses a transformer is probably cast concrete, is messy, time consuming and may structurally compromise the integrity of the wall. You expose rebar when cutting a hole and it is not possible to seal it so that there will no subsequent corrosion.

Provided that any hole is correctly packed and clad there is no difference in respect of fire fighting.

Register to Reply
Active Contributor

Join Date: Apr 2020
Posts: 15
#6
In reply to #2

Re: Layout of IPB (Insulated Phase Bus)

07/10/2020 11:37 AM

Thank you So much. I appreciate it.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: Layout of IPB (Insulated Phase Bus)

07/04/2020 6:58 AM

The fire wall has 30 min rating. If you make a hole through it (for passing the IPBD), the fire rating may be compromised. I doubt codes will allow that. I have seen the IPBD taken over the fire wall.

Height of the firewall needs to be above the level of transformer conservator and thus there is no way height can be reduced.

__________________
Raghunath
Register to Reply
Active Contributor

Join Date: Apr 2020
Posts: 15
#7
In reply to #3

Re: Layout of IPB (Insulated Phase Bus)

07/10/2020 11:39 AM

Thank you for your response. I appreciate it.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#4

Re: Layout of IPB (Insulated Phase Bus)

07/07/2020 7:13 AM

If possible,do not penetrate the firewall,go over it,under it,or around it.

That is the best option overall from a liability perspective,not necessarily the cheapest at the time of installation.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Active Contributor

Join Date: Apr 2020
Posts: 15
#8
In reply to #4

Re: Layout of IPB (Insulated Phase Bus)

07/10/2020 11:40 AM

Thank you so much for helping me out.

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

HiTekRedNek (1); jhhassociates (1); Qurrat (4); raghun (1); SolarEagle (1)

Previous in Forum: Differential Protection   Next in Forum: UPS 24VDC o/p 40A Rating

Advertisement