Differential Protection

07/01/2020 5:14 PM

Dear all

are the vector group effect on transformer differential protection.in the other word if

we put wrong vector group in the setting of protection relay,the relay operated or not?

thanks for all

Register to Reply
Pathfinder Tags: Differential Protection
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: differential protection

07/01/2020 6:03 PM

Yes the specific vector group input is necessary for the proper protection of the transformer...

https://www.microener.com/contenu/uploads/2012/08/DIF87_PRELIM-ME.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Differential Protection

07/02/2020 5:35 AM

There will be a phase shift between the HT side current and the LV side current, particularly in Delta/Star Transformers. If this is not taken care, even during normal loading conditions, the relay could see a differential current and if the setting is lower than this current, the relay would operate. And, yes! by programming a wrong vector group, the relay might operate for thro-fault conditions too.

Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#3

Re: Differential Protection

07/04/2020 4:37 PM

Looks like you got the answer earlier. Anyway i may add that it actually depends. It depends on how far is the value of the set vector group from the real one.

Also the differential current's value varies with the load. Theoretically it should not but reallity beats theory. Since the set vector group differs from the real one, the relay calculates (on the assumption of a digital relay used) a different differential current than it should be. Once the treshold is reached the relay trips. Good luck with that.

Worse is not to trip when it should. Get fireworks as a result.

If you have already experienced a real trip with a wrong vector group I'd love to check the oscilo if you may share it with us.

__________________
The time is ......now
Register to Reply
Associate

Join Date: Mar 2019
Posts: 29
#5
In reply to #3

Re: Differential Protection

07/07/2020 9:47 PM

thank you very much for all

Register to Reply
Associate

Join Date: Apr 2009
Location: Muscat Oman
Posts: 27
#4

Re: Differential Protection

07/06/2020 9:56 AM

I want to share my experience in this topic. i found that if we put vector group in wrong the relay will give nuisance trip.when i worked in 7.5 MW Power plant having 10MVA Generating Transformer. During commissioning the plant, The transformer trip by differential relay near to full load condition. Then we checked the relay and found setting problem. we put correct vector group and reached full load.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Differential Protection

07/08/2020 11:30 AM

Why anyone would want to do this might forever remain a mystery, then.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

B.JEYACHANDRAN (1); electricalexpert65 (1); henry98 (1); nikolay (1); PWSlack (1); SolarEagle (1)

Previous in Forum: Static Transfer Switch Safety Configuration   Next in Forum: Layout of IPB (Insulated Phase Bus)

Advertisement