Interposing Potential Transformer

07/09/2020 5:21 AM

Is it recommended to have an Interposing Potential Transformer, just like an ICT? The issue is, at present, in an old installation, they got only a single secondary PT connected in Star/Star, for metering. Now, due to a stipulation by the authorities, they need a open delta PT. They do not want to replace/modify the existing PT. Can we introduce a 110V/110V, 3-Phase, Star-Open Delta IPT for connecting to a Neutral Displacement relay? The burden requirements are taken care of. Have you seen any such IPT? Is it recommended/advisable? If not, what could be the issues?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Interposing Potential Transformer

07/09/2020 7:16 AM
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #1

Re: Interposing Potential Transformer

07/09/2020 10:09 PM

And, to think that you have thought that I do not know anything about ICT that you are giving me a Quora link to know what is ICT....

Please read and comprehend the question fully before answering hastily. I have asked about IPT and NOT ICT.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#6
In reply to #3

Re: Interposing Potential Transformer

07/09/2020 11:44 PM

Anonymous may just be complaining about your use of a TLA...

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Interposing Potential Transformer

07/09/2020 12:25 PM

Yes, auxiliary PTs have been used to get a phasing configuration different from what the main PTs provide, of which what you describe is a very common example. Modern digital protective relays can usually work with Wye-connected PT inputs and compensate in their calculations for the configuration really needed, but older relays aren't as flexible. And I think the term you really want is "open corner delta" or "broken corner delta." Just plain "open delta" is a little different, where only 2 PTs are used to get 3 phases of secondary.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #2

Re: Interposing Potential Transformer

07/09/2020 10:10 PM

Of course! The customer has a older version relay. And, I meant broken delta.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#5
In reply to #4

Re: Interposing Potential Transformer

07/09/2020 11:43 PM

The high voltage wye is grounded on those systems, and it appears the primary wye of the auxiliary PTs must also be grounded. This is as mentioned by C. Russell Mason, The Art And Science Of Protective Relaying, see Page 320. He also mentions that you need a significant burden on the secondary to avoid an unstable neutral condition when the line section is indeed operated ungrounded, to avoid false trips. Normally your 59G relay comes with that resistor. The VA capacity of your auxiliary PTs you may want to match to your primary PTs. He references an AIEE Transaction from 1941 that perhaps gives information to size that resistor, and whether it is better installed in line with the primary wye ground connection.

I think I’ve seen dual secondary PTs used for both broken delta ground relay polarization and metering, BTW.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7

Re: Interposing Potential Transformer

07/13/2020 5:17 PM

Interposing CTs are not uncommon. So no reason interposing PT should be problem.

As for CT, you do not want interposing transfo to give extra error. Relays 59 are not high burden.

I would look at an interposing PT with twice the saturation voltage of existing & see how it works out on availability, burden etc.

Register to Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#8

Re: Interposing Potential Transformer

07/23/2020 9:22 AM

Is it normal to use metering core for protection? Even if you use a IPT, input for that IPT will be from metering core of existing PT?

If yes, we can replace existing meter with protection relay which has 59N protection as well which will derive from three phase VT connection.

If you don't want to disturb the meter, I think there are some stand alone 59N relays which can still calculate V0 from three phase voltage. This can be connected in parallel to meter. See one type in below link.

https://www.prokdvs.com/items/20

Thanks,

Vijay

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Anonymous Poster (1); electricalexpert65 (2); PeterT (1); rwilliams (2); vijaymail_electrical (1)