CT Currents Splitting Between Phases in Relay

07/09/2020 8:01 AM

Dear Engineers,

We were testing Siemens 7SJ66 relay for measurement circuit verification by primary injection. We were using ISA T3000 current injection kit. Attached is the scheme of how CT wiring is done.

While we inject current in Y phase CT like 300A, we measure in IL2 and Io as 300A in relay display.

But while we inject same 300A in R phase, we see as below. Same is observed when injected in B phase with only difference is IL1 is 0A and IL3 will be 300A

IL1: 250A

IL2:50A

IL3:0A,

Io:300A

I1:250A

I2:50A

We checked all wiring tightness, CT secondary winding resistance, all found OK.

But when we try same current injection from secondary injection kit (omicron CMC256+) directly to relay terminals by injecting 5A, we don't see this issue.

We even tried with new wirings from CT to relay terminals but same issue repeats.

Any one can help us out why current is splitting in Y phase?

Thanks,

Vijay

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Pathfinder Tags: CT wiring Relay Relay Testing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: CT Currents Splitting Between Phases in Relay

07/09/2020 11:19 AM

One might be tempted to look for a phase-to-neutral connection in the downstream power wiring, and eliminate it when found.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#2

Re: CT Currents Splitting Between Phases in Relay

07/09/2020 3:32 PM

Here is what I think is happening:

When you inject current with the ISA T3000 current injection kit, the CT under test actually has 3 windings, your single wire injection winding (primary) and two secondary windings, the CT winding going to the relay and the single winding that is the bus phase.

If the bus phase is open, no current will be induced into that "winding", and the output to the relay winding will give the correct reading (300A). If the phase is connected to a load, there is a complete circuit and the induced flux from your test set drives current in this circuit instead of the current in the winding to the relay.

Bottom line is you have a connection (either load or short) between Blue and Red.

Register to Reply Good Answer (Score 2)
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#3
In reply to #2

Re: CT Currents Splitting Between Phases in Relay

07/22/2020 8:12 AM

I checked same current injection by laying new cables from CT secondary to relay terminals and still the same issue happens.

This CT has only 2 secondaries, metering and protection cores.

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: CT Currents Splitting Between Phases in Relay

07/22/2020 8:22 AM

...then the cause of the problem has not yet become apparent. There's only one thing to be done:

Keep looking.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#5
In reply to #4

Re: CT Currents Splitting Between Phases in Relay

07/23/2020 4:01 AM

The subject feeder is now loaded and all currents are balanced. It is a mystery why the CT behaved during our testing.

Anyways thanks for your help. Will keep you posted if anything comes up in my mind regarding this.

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

PWSlack (2); Rixter (1); vijaymail_electrical (2)