what is N-0, N-1 condition in load flow study? is it the probability of fault?
manirul
Pathfinder Tags: N N 1 condition
Good Answers: 19
Re: load flow
11/05/2007 3:02 AM
It is node 0,node 1....etc.
Ramesh,Freelance Electrical/automation Consultant
Re: Load Flow
11/06/2007 10:49 AM
It refers to which loads are operating in each case. For the n-0 case, all loads are turned on. For the n-1 case, 1 of each group is turned off. For instance if you have 4 pumps operating in parallel, it is assumed that only three are needed to meet process demands and one is a standby. So for the n-1 case, only three of them would be running. This probably more accurately represents the plant load.
Re: Load Flow
11/06/2007 11:14 PM
Ii think it is related to Contingency load and not for stand by load. The Contingency load could be transmission line, transformer, capacitor bank, shunt reactor, bus section etc. and not the end load like pumps. outage of those element from power system represent by N-condition. i need more clarity in this matter.