Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151

Heating Elements in 3 Phase Configuration

08/14/2020 3:00 PM

This is something that I have never done before, and I don't have an "expert" at hand to answer my questions.

I am designing a heated tool that will have three zones each controlled independently with its own thermocouple, controller, and solid state really. I have available 3 phase, 208 volt 3 wire to power this. I need something in the range of 1000 watts to heat each zone.

I have selected cartridge heaters rated 600 watts @ 240 volts, two wired in parallel for each zone. Using Ohm's law, I calculate the resistance of each heater to be 96Ω and for 2 in parallel, the total resistance 48Ω This would give me about 900 watts @ 208 volts, and a current of 4.3 amps. for each zone.

I plan to wire these in a delta configuration. The three phases labeled X,Y,Z:

ZONE 1 X-RLY1-LOAD-Y

ZONE 2 Y-RLY2-LOAD-Z

ZONE 3 Z-RLY3-LOAD-X

Where the LOAD is the two elements in parallel with a total resistance of 48Ω.

Will this work?

Are my calculations correct?

What will be the current in each phase, assuming all zones are on?

__________________
The older I am, the better I used to be
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Heating elements in 3 phase configuration

08/14/2020 3:56 PM

Is this 3 phase with a wild leg ?

Otherwise it should be 240v from phase to phase....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Off Topic
Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151
#2
In reply to #1

Re: Heating elements in 3 phase configuration

08/14/2020 4:05 PM

No, the power supply is 208 3 phase Y , but I don't have a neutral line available.

__________________
The older I am, the better I used to be
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: Heating elements in 3 phase configuration

08/14/2020 4:23 PM

...or you might have a weird setup like this....

amps equals voltage divided by resistance, or:

I = E/R

https://www.industrialcontrolsonline.com/training/online/electricity-101-basic-fundamentals

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #3

Re: Heating elements in 3 phase configuration

08/14/2020 4:40 PM

So yes you are correct....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#16
In reply to #5

Re: Heating elements in 3 phase configuration

08/16/2020 1:39 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151
#6
In reply to #3

Re: Heating elements in 3 phase configuration

08/14/2020 6:12 PM

That's exactly what we have in our facility, 208 v phase to phase and 120 v phase to neutral

__________________
The older I am, the better I used to be
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#20
In reply to #3

Re: Heating elements in 3 phase configuration

08/16/2020 7:25 PM

Wait how did you calculate the ohms, because I get 1200 watts/ by 208 volts = 5.77 amps...? Because when you lower the voltage you only get 75% of the heat....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#21
In reply to #20

Re: Heating elements in 3 phase configuration

08/16/2020 7:43 PM

240 - 208 = 32 ....240/32= 7.5 5.77 * .75 = 4.33

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#22
In reply to #21

Re: Heating elements in 3 phase configuration

08/16/2020 8:33 PM

The 2 lines drawing 4.33 amps for a total of 8.65 amps, then coincide at the single delta point, allowing for phase angle efficiency boost of 13.33%, that gives a total amperage at the delta point of each leg of 7.50 amps...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Off Topic
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4

Re: Heating elements in 3 phase configuration

08/14/2020 4:28 PM

I agree your calculations.

Current will be 7.5 amps per phase ( if all the heaters are at maximum power). If you are individually controlling each heater, of course, phase currents will be different.

If you are using normal line power, the unbalance is not a problem - it might be for a small genset off-grid.

The notional phase to neutral voltage is 208/(SquareRoot of 3) = 208/1.732 = 120 volts - 120 volts x 7.5 amps x 3 wires = 2700 watts.

67model

Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151
#7
In reply to #4

Re: Heating elements in 3 phase configuration

08/14/2020 6:26 PM

That's what I needed, the amps per phase so that I can specify my circuit protection and conductor size.

I should be OK with 10 amp fuses and 18 ga wiring?

__________________
The older I am, the better I used to be
Register to Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#8
In reply to #7

Re: Heating elements in 3 phase configuration

08/14/2020 11:23 PM

You have to take into consideration the length of the run due to the resistance and voltage drop over distance, then the insulation rating of the wire, probably want to go with a thhn, the conductor stranded or solid and material cu,al or clad wire, also the wire run is bundled in a conduit or raceway...I should think a #12 stranded thhn copper conductor...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151
#13
In reply to #8

Re: Heating elements in 3 phase configuration

08/15/2020 8:46 AM

The wiring will only be a few feet and in open air.

__________________
The older I am, the better I used to be
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#9
In reply to #7

Re: Heating elements in 3 phase configuration

08/15/2020 5:41 AM

Ba aware of the ambient temperature where the conductors must traverse.

You should terminate the heater elements with a high temperature wire,such as EPDM lead wire to exit the high temperature zone into a lower temperature area.

I agree with SE,no less than a # 12 THHN (194F) conductor.

Better safe than sorry;do it once,and do it right.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151
#12
In reply to #9

Re: Heating elements in 3 phase configuration

08/15/2020 8:41 AM

duplicate reply

__________________
The older I am, the better I used to be
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#14
In reply to #7

Re: Heating elements in 3 phase configuration

08/15/2020 2:05 PM

There are various types of fuses - rewirable [fusing current such that according to local regs, a 10 amp rewirable fuse must feed cable rated 15 amp minimum with normal cartridge "single use" fuse], glass tube (poor fault breaking capacity, around 30 amp); high breaking capacity ceramic cartridge HBC/HRC to 38mm meter fuses breaking 50,000A upwards at 1000V. Also MCBs and other circuit breakers.

A one square millimetre PVC insulated (40 'C rise at 30 'C ambient) copper cable [18 AWG about 0.8 sq.mm] is rated 10.5 amp 3 wires in a conduit in a thermally insulated wall, but 15.5 amp clipped to a wall in a room.

Since you have not given any details, I agree with other posts #8,#9 suggesting #12 AWG.

The heaters may have integral high temperature tails which can be joined to standard cable - if not, the post #9 advice applies. Hi Temp tails should be used to enough length that standard terminals & cables are not overheated.

Register to Reply
Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151
#18
In reply to #14

Re: Heating elements in 3 phase configuration

08/16/2020 2:26 PM

I guess a little more detail is required at this point of the discussion.

The tool I am designing is a punch press die. The heated part of the die is on the top half, the reciprocating portion of the die. I plan to terminate the cartridge heater leads in junction boxes mounted to the upper half of the die and insulated from the heated components. From there, I plan to use SJEOW cables, one for each phase, about 6 feet to the control cabinet containing the temperature controllers, relays, and internal circuit protection (10 amps). Power will come from a 20 amp plant circuit.

Because I want the die to be easily installed and removed from the press, I intend to use threaded pin and socket connectors between the SJEOW cables and the junction boxes. The one problem I am looking at now is how to securely connect the thermocouples (type J).

__________________
The older I am, the better I used to be
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#23
In reply to #18

Re: Heating elements in 3 phase configuration

08/16/2020 9:10 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#10

Re: Heating Elements in 3 Phase Configuration

08/15/2020 7:32 AM

Hey GG I thought I remembered you retired a few years back: what happened? Or is my own ageing brain playing tricks.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151
#11
In reply to #10

Re: Heating Elements in 3 Phase Configuration

08/15/2020 8:38 AM

I thought I retired too. But, my former employer won't let me rest in peace. The extra income is nice though.

__________________
The older I am, the better I used to be
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Dec 2019
Posts: 160
Good Answers: 14
#15

Re: Heating Elements in 3 Phase Configuration

08/16/2020 1:06 AM

Your power/phase is 1200 watts @ 240V. @208 it's 208/240*1200=1040W. The line current is I=P/E√3 = 2.9A/Phase. It appears you forgot about the square-root of 3 in your calculation.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#17
In reply to #15

Re: Heating Elements in 3 Phase Configuration

08/16/2020 10:23 AM

Rich, it's the heat!

All the resistors are energised line to line, at 208V.

Current = V/R; Watts = current x Volts = (V/R)* V = V2/R.

Power at V1 = V12/R

Hence, Power at V1/(Power at V) = V12/V2

1200W*(208/240)2 = 1200* 0.75111 = 901.33 = 900 watts to practical accuracy.

Register to Reply
Power-User

Join Date: Dec 2019
Posts: 160
Good Answers: 14
#19
In reply to #17

Re: Heating Elements in 3 Phase Configuration

08/16/2020 6:03 PM

Alas, it is true but you have to account for the phase angles of the voltage sources and how the line current is affected. I did error in using 1040 Watts, I forgot to use the total power and used only a single leg. 3,120 watts should have been used and the line current should have been 3-times higher, about 8.7A. The current through each load resistor is voltage divided by the resistance and the power is still E^2/R but the line current isn't the same as the load current in a balanced 3-phase system, hence the square root of three in the calculation.

Register to Reply
Power-User

Join Date: Dec 2019
Posts: 160
Good Answers: 14
#24
In reply to #17

Re: Heating Elements in 3 Phase Configuration

08/17/2020 1:34 PM

Well, I realized that I did a "face-plant" on this one. In calculating the ratio of the voltages I forgot to square the ratio. P1/P2 ∝ (E1/E2)^2. So, hopefully error free, P=3,600*(208/240)^2 = 2,704 watts. The line current, again hopefully sans errors, I=2,704/208/√3 = 7.5A. I do apologize for my fumbled thinking. I haven't benefited as much from aging as I had hoped! I guess math has the electronics equivalent of "the amount of equipment damaged is directly proportional to the operators experience"...

Register to Reply
Register to Reply 24 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (3); gringogreg (7); HiTekRedNek (1); R_i_c_h (3); Randall (1); SolarEagle (9)