Yellow Phase of VT Secondary Earth

09/07/2020 2:09 AM

Good morning gentlemen.

I was poring over drawings of our 6.6kV metalclad switchgear (NEI Reyrolle) and saw something i didn't see before.

The yellow phase (L2) of VT secondary is earthed instead of its STAR point or neutral. This VT's primary is connected to main 6.6kV busbar which steps down 6.6kV to 100Vac, from which then two leads Red(L1) and Blue(L3) are taken to a transformer (inside a different panel) which steps it up from 100Vac to 110Vac, which is then fed to an auto-synchronizer (as bus voltage).

There is another VT, but for the generator, which has two secondary windings, both of which are in STAR and separate from each other. One winding for protection relays and other for metering and synchronization (to the same auto-synchronizer as above) of generator to the bus. However, like above, both windings have their L2 (Yellow phase) grounded, instead of the Star or neutral point.

I wanted to know the reason for this. Is this any old British standard or practice? Or is there any advantage?

L1-n and L3-n were found to be 50-60Vac and n-L2 was found zero volts.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Yellow Phase of VT Secondary Earth

09/07/2020 9:04 AM

This sounds like it's stepped down for some unknown requirement, perhaps a control voltage or for powering monitoring equipment, or perhaps for making coffee, who knows....I don't see anything unusual, they just needed a neutral for the circuit, where else would you get one....This is going from 3Ø to a split phase supply and would supply 50v- 60v- 100v or 120 volts...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Commentator
Pakistan - Member - New Member

Join Date: Dec 2007
Location: PAK
Posts: 68
Good Answers: 1
#2
In reply to #1

Re: Yellow Phase of VT Secondary Earth

09/07/2020 10:10 AM

I'm sorry I put the question the wrong way and put too much detail.

I wanted to know why the 6.6kV/100V VT secondary Yellow phase is grounded for both metering and protection circuits and star neutral point is kept afloat.

Thanks

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: Yellow Phase of VT Secondary Earth

09/07/2020 10:24 AM

Yeah that's probably a code requirement, for safety....You wouldn't want a higher voltage source bleeding over to a lower voltage circuit in case of short...the neutral is probably grounded slightly upstream....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#4
In reply to #2

Re: Yellow Phase of VT Secondary Earth

09/08/2020 12:33 AM

Maybe not enough detail. How many potential transformers do you have, and are you sure they are connected in star on the primary? Normal practice is to use 2 PTs connected in open delta, and Phase 2 is grounded for safety, to tie either Phase 1 & 3 at a fixed offset of 120V to Earth.

Register to Reply
2
Commentator
Pakistan - Member - New Member

Join Date: Dec 2007
Location: PAK
Posts: 68
Good Answers: 1
#6
In reply to #4

Re: Yellow Phase of VT Secondary Earth

09/08/2020 5:42 AM

One bus, divided in two sections coupled via a bus-coupler (breaker). There are four generators, two on each bus section.

There are two 6.6kV/100V VT's - one each bus section. Both primary and secondary is star connected. Primary connected to bus thru fuses. Secondary star point (Neutral) is afloat while yellow phase (L2) is grounded. The VT's provide voltage (L1 and L3) both for metering and auto-synchroniser.

The VT's on each generator are also same configuration as above. Only difference is that they have two secondary windings. One set of windings for AVR and other for protection relays & metering. But both secondary windings have their yellow phases grounded, but not the star neutral. And yes, all four generators have a 12Ohm neutral ground resistor.

I've attached photos for ease of understanding.

Edit: Refer to VT2 in both drawings

Register to Reply Good Answer (Score 2)
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#8
In reply to #6

Re: Yellow Phase of VT Secondary Earth

09/08/2020 10:39 AM

Supplying 3 potential transformers in each measurement location is unusual in U.S. practice, in switchgear. Normal is 2 connected open delta with phase 2 grounded. Supplying 3 transformers does make it easy to furnish polarizing voltage for ground fault detection on ungrounded systems, plus there is no phase shift with relays & meters, current vs voltage.

You should be able to ground any leg you want on the secondary of your PTs, just don’t ground the neutral also. I suspect the leg is grounded for personnel safety, and they chose to make it similar to the open delta de facto standard.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#5

Re: Yellow Phase of VT Secondary Earth

09/08/2020 2:28 AM

This is common practice in olden days with high resistance grounded or isolated systems.

Intention is the earth fault protection at generator terminals which is set sensitive should not maloperate for a phase-to-ground fault in VT secondary wiring.

IEEE 242 (Buff book) on protection & IEEE C37.101 & 102 on generator protection discuss this further.

If the earth faut protection is delayed, the y-phase grounding can be exempted.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Commentator
Pakistan - Member - New Member

Join Date: Dec 2007
Location: PAK
Posts: 68
Good Answers: 1
#7
In reply to #5

Re: Yellow Phase of VT Secondary Earth

09/08/2020 5:59 AM

Isn't grounding one phase of secondary of VT same as producing a phase-to-ground fault??

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9
In reply to #7

Re: Yellow Phase of VT Secondary Earth

09/08/2020 12:08 PM

That's is true if the star point is also grounded.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #7

Re: Yellow Phase of VT Secondary Earth

09/10/2020 10:19 AM

...and not a <...fault...> in that case, because it is intentional.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Yellow Phase of VT Secondary Earth

09/08/2020 5:28 PM

Is this thread constrained to <...gentlemen...> for any particular reason or can others reply if they aren’t?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#11
In reply to #10

Re: Yellow Phase of VT Secondary Earth

09/08/2020 6:50 PM

I think we’re a very tolerant organization...

Register to Reply Off Topic (Score 5)
Commentator
Pakistan - Member - New Member

Join Date: Dec 2007
Location: PAK
Posts: 68
Good Answers: 1
#12
In reply to #10

Re: Yellow Phase of VT Secondary Earth

09/09/2020 2:02 AM

Haha

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #12

Re: Yellow Phase of VT Secondary Earth

09/10/2020 10:21 AM

Rude.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PWSlack (3); raghun (2); rizwan (4); rwilliams (3); SolarEagle (2)

Previous in Forum: Voltage Drop on Motor Circuits   Next in Forum: Electrical Bulk Material

Advertisement