09/21/2020 8:45 PM

I had lightning hit a tree close to the disconnect for my water well. it blew the fuses, and a contact relay, it also took the well pump out. The tree, disconnect and the well are layed out in a triangle, the well is the farthest from the other two. My question is did it go from the tree to the pump, or from the tree through the electrical system to the pump?

Register to Reply
Pathfinder Tags: water well/ lightening
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33401
Good Answers: 1817
#1

Re: lightening water well

09/21/2020 10:33 PM

A lightning strike is a violent event, anything can happen....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: Sep 2020
Posts: 5
#4
In reply to #1

Re: lightening water well

09/22/2020 1:05 PM

Thank you for those words of wisdom!

Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#7
In reply to #4

Re: lightening water well

09/22/2020 2:15 PM

I must be getting old I can't find a Mork "sarcasm" meme.

__________________
High Tolerance is Beautiful
Register to Reply
Guru

Join Date: Jul 2012
Location: Madison, WI.
Posts: 2074
Good Answers: 77
#18
In reply to #1

Re: lightening water well

09/23/2020 9:59 AM

I can attest to what SE posted. We had a strike earlier this year. Could not find the point of the strike but the results were obvious. It came through the low voltage electrical system. Took out the garage door openers control on both my unit and my neighbors. Took out the cable modem. Took out the ethernet port on the wifi router and the computer but not the printer. Killed the doorbell and both wired smoke alarms.

Everything else was just fine.

Go Figure.

__________________
Knowing is the end result of learning, not believing.
Register to Reply
4
Guru

Join Date: Jul 2008
Posts: 1693
Good Answers: 145
#2

Re: Lightning Water Well

09/22/2020 7:03 AM

Probably both and more that you don't know about. There will be a flow of electrical energy (current density) out from the strike through the ground a bit like the waves moving out when you throw a rock into a calm pond. In addition, when the current encounters a conductor (pump wires, possibly metal pipes, etc.) the current will probably have a very strong preference to flow in the metal (inductance is a funny animal) and this will considerably disturb the symmetrical flow suggested by the pebble in the pond.

Before "the lightning strike" there was at least one leader "strike" going part way from the ground to the cloud. These are much less violent than the main strike but they can cause damage and if there were multiples then you may have had 'little strikes" in places you don't know about.

The conductivity of the soil will affect how much energy flows in what direction. Moisture content, clay vs. black dirt, sand vs. rock, all affect the current flow and who gets what first.

In addition, the radiated electric field from what could be 100,000 amps or more current in the lightning strike will induce significant and often damaging currents and voltages in nearby conductors.

If you have ever noticed a lightning strike "flicker" it is because multiple strikes down the same channel are common. If your event had multiple strikes then not only could they have been in different locations but also the first could have burned something out resulting in the energy from next strike taking a different path.

So, SolarEagle's "anything can happen" sums it up pretty well.

__________________
Few things limit our potential as much as knowing answers and setting aside questions.
Register to Reply Good Answer (Score 4)
Member

Join Date: Sep 2020
Posts: 5
#5
In reply to #2

Re: Lightning Water Well

09/22/2020 1:09 PM

Is there any way to protect the pump?

Register to Reply
2
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#6
In reply to #5

Re: Lightning Water Well

09/22/2020 2:12 PM

I've added hard wired surge arrestors to many pieces of outdoor equipment.

I've seen the surge arrestor blown up and the equipment ok.

__________________
High Tolerance is Beautiful
Register to Reply Good Answer (Score 2)
2
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7955
Good Answers: 459
#8
In reply to #5

Re: Lightning Water Well

09/22/2020 10:21 PM

As JE stated above, surge arrestors would be a good place to start.

If you were to install surge arrestors, my recommendation would be for surge arrestors to be placed line-to-line and from each line to earth ground. Metal Oxide Varistors (MOV's) are fast to activate but they have limited energy dissipation. If you were to place Gas Discharge Tubes (GDT's) in parallel with the MOV's, then the GDT's can 'take over' when the clamping voltage across the MOV's continues to rise as the device heats up. Keep in mind that when a GDT is tripped, the voltage drops to a relatively low value and stays there until the arc is extinguished. Therefore, the circuit protection device for your well pump will be tripped as a result.

Caveat: Any electrical installation will also have to comply with the local authorities having jurisdiction (AHJ).

But then again, what do you think the probability might be for another hit in the same vicinity?

I have been living in this location in Maryland for over 24 years. In all that time, we have only had one lightning strike that was close enough (neighbor's tree hit about 50 ft away) to actually damage electronics in the house. And there seemed to be no rhyme or reason for why some things were damaged, and some things were not. Lightning's capriciousness is legendary.

Good luck with your quest.

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Dec 2008
Location: Mogale City, Gauteng, South Africa
Posts: 13
Good Answers: 1
#11
In reply to #8

Re: Lightning Water Well

09/23/2020 12:42 AM

We had two lightning strikes to the same tree in two weeks. Both strikes took out all of my electronic devices that weren't on UPS. The second strike occured two days after I had replaced everything.

My Insurer was not a happy chappy

__________________
larryvan
Register to Reply Off Topic (Score 4)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33401
Good Answers: 1817
#12
In reply to #11

Re: Lightning Water Well

09/23/2020 1:27 AM

Maybe the insurer is willing to pay for the extra protection you seek...If not, I would just have the tree removed...and add a little extra bulk to the service ground...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Dec 2008
Location: Mogale City, Gauteng, South Africa
Posts: 13
Good Answers: 1
#14
In reply to #12

Re: Lightning Water Well

09/23/2020 2:30 AM

Tree is history, unfortunately.

Also got rid of satellite dish and related TV service.

All electronic devices are now behind 2000kVa UPS's.

__________________
larryvan
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32212
Good Answers: 839
#27
In reply to #14

Re: Lightning Water Well

09/27/2020 4:14 PM

<...200kVA ups...> is a lot bigger than can be supported on a domestic supply, which is the order of a factor of 8 smaller!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32212
Good Answers: 839
#28
In reply to #27

Re: Lightning Water Well

09/28/2020 12:07 PM

Er, actually 2000kVA and 80 times. Oooops!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33401
Good Answers: 1817
#9
In reply to #5

Re: Lightning Water Well

09/22/2020 10:22 PM

The question is how much protection is cost effective, there is always a trade-off...how much trouble and expense are you willing to invest in protecting this equipment, how critical is the application + cost of replacement - lifetime probability of lightning strikes that disable the equipment + cost of protection....

http://www.sumteremc.com/content/lightning-protection#:~:text=Connect%20a%20grounding%20lead%20to,significant%20distance%20from%20the%20building.

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Commentator

Join Date: Jun 2014
Posts: 59
Good Answers: 1
#10
In reply to #5

Re: Lightning Water Well

09/22/2020 10:44 PM

You don't say how many times that "particular tree" has been hit by lightning.

You don't say how big your property is.

You don't say how much you are willing to spend to protect your water pump; however, if you are willing to spend the money, you might try a Faraday Cage with a field of ground radials to reduce the earth-ground resistance to near zero.

The cage should be a minimum of 2 inch thick wall tubing. Do not use Galvanized pipe. The ground radials should be, at least, #4, and as long as you can afford.

The radials must be brazed to the tubing; otherwise, the connections will corrode and cause the resistance to rise.

I recommend that you research grounding and bonding on the internet, either draw up, or have a set of plans drawn by an Engineer, to be submitted to your planning agency. You'r3e going to want this approval for your insurance company.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Location: NASA-Glenn Research Center, Cleveland Ohio
Posts: 389
Good Answers: 17
#16
In reply to #5

Re: Lightning Water Well

09/23/2020 7:10 AM

no, there is NO way to protect the pump. no matter what anyone tells you.

surge protectors do not work for a lightning strike, ok i take that back, they CAN work if the lightning hits the line a mile away and sends a surge of much lower energy than the strike itself, much lower. my house or the pole next to it has been hit 4 times in 30 yrs. first 10 it was hit 3 times and then when the trees became taller than the house (i think the trees dissipate the static buildup before it gets to the point of an arc), i have not been hit until two yrs ago when the top of my electric pole got smacked. blew the insulators to pieces and shattered the car windows (among electrical things). one time there was a strike near my home, it energized the telephone line, which blew out my modem and entered the electrical system in the house and fried other electronic items (seems like the electric eyes on the garage door are susceptible as they go every time). as someone else said, 100,000 amps.. there is nothing to protect from that except mother earth.

you can "help" protect your equipment by grounding everything as much as possible. i have a metal shop, i have two grounding straps on each end of the building. long copper poles (8') need to be put into the ground. grounding is your best insurance, maybe plant more trees.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3

Re: Lightning Water Well

09/22/2020 10:24 AM

Does it really matter?

__________________
Good moaning!
Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 812
Good Answers: 65
#13

Re: Lightning Water Well

09/23/2020 1:56 AM

Or did it go from the ground, through the water to the pump and on to the electrical supply. All you can say was it got into the water well pump circuit.

We installed a number of surge diverters that consisted of an enclosure, two 100KA MOV diverter blocks in a Pi configuration with an air cored inductor which supplied the 240V to a "protected system". The second diverter was paralleled with an AC capacitor

Did they work, yes, did they fail under lightning strikes, yes, did the "protected system" remain protected from harm, sometimes! Nothing can be guaranteed with lightning except that it will surprise you!

In a previous life I worked with surge diverters in substations and it was well documented that after a surge had been diverted the voltage impressed across the system rose at the rate of 70KV per foot on 11KV transformers primary so that is why the lightning arrester is mounted right next to the bushing and connected to it with a very short straight wire, no pigtail for that forms an air cored coil.

A case in point. There was a very large, 40m 1.2m dia Hoop pine in the paddock 150m from the house and 20m from an underground telephone cable. The tree was struck, the phone line and accessories were fried and a light switch in a shed was turned to plastic confetti. The only common denominator was the earth.

We also have a stand of "protected Trees" on an ironstone hill side and every storm that comes through takes great pleasure in swatting the growing ones and from the farm shed the trees can be watched lighting up and turning to wood chips.

Lightning is a stubborn beast and follows whatever path it wishes no the one designed by man for protection. So lightning must be female mustn't it?

__________________
Hare today, goon tomorrow!
Register to Reply
Participant

Join Date: Sep 2020
Posts: 3
#15

Re: Lightning Water Well

09/23/2020 6:44 AM

Electricity will take all available paths. Your well was one of them.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#17

Re: Lightning Water Well

09/23/2020 8:27 AM

I recall an instance where lightning struck nearby a house,and the house had an intricate pattern in the wall paper,outlined in metallic foil.

The strike followed the pattern,and vaporized all of the foil pattern in the paper,but left everything else untouched;Didn't even scorch the paper around the foil.

Go figure!

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Power-User

Join Date: Dec 2019
Posts: 160
Good Answers: 14
#19

Re: Lightning Water Well

09/23/2020 1:03 PM

I suspect the problem was more EMP related than what path the current took. Significant induced current in devices near the nanosecond magnetic field created by the lightening strike can generate a transient voltage that will exceed any protection device capability as well as exceed insulation dielectric rating . While surge protectors are important it becomes an expensive proposition to protect power circuits like well pumps. I've installed transient suppression on instrumentation at the transducer and at the equipment it's connected to and have still had devices damaged. The area I live in isn't prone to much lightning and most is of the sheet-lightning variety but in one instance a strike to a tree a few feet from a house in our area blew out, literally, the power outlets throughout the house; by that I mean some the outlets were hanging on their wires out of the box with significant flash burns in the outlet plastic body. Needless to say appliances didn't fare well either. I was really surprised and it impressed me on how much damage lightning can do even if it's not a direct strike.

Register to Reply
Member

Join Date: Sep 2020
Posts: 5
#21
In reply to #19

Re: Lightning Water Well

09/23/2020 11:38 PM

Than all of you for your input! Have you ever heard of grounding a tree?

Register to Reply
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#20

Re: Lightning Water Well

09/23/2020 11:23 PM

It would be interesting to see a " map " of how the energy irradiated from the point of contact at the tree to the distribution area. Maybe se can provide that.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33401
Good Answers: 1817
#22
In reply to #20

Re: Lightning Water Well

09/24/2020 3:13 AM

I had a customer once I was at his house and he showed me a tree on the side of the house that had been struck by lightning just the day before, well it was a bizarre sight, the trees roots that were growing just below the surface had exploded out of the ground all around the tree, and the tree had lost several branches but was still standing mostly intact, there was potholes all around the tree where the large roots were some 10 to 12 ft away and some closer, the lightning had entered the house and caused his computer screen to iridesce but you could still see what was on the screen and the computer was still working...I don't remember all the little damages there were, but it was really hit or miss...I had one customer had their A/C condenser unit hit and it reversed the polarity of both the fan motor and the compressor...I knew a guy once he had been hit by lightning and it killed every hair cell on his body and burned a hole through his watch...anything can happen when you let that much electrical energy loose, it's unpredictable.....mostly what you protect from is near misses, a direct hit and all bets are off....

Here's a tree that was struck, you can see the pattern in the ground probably from the root growth...

This guy was struck, it left burn pattern...

Here's a Walnut tree section that was struck by lightning...

Lightning struck this pin on the green...

Chimney strike...

Pretty cool shot here....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Member

Join Date: Sep 2020
Posts: 5
#29
In reply to #22

Re: Lightning Water Well

09/28/2020 9:07 PM

Those were some cool pictures thank you!

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#23

Re: Lightning Water Well

09/24/2020 6:59 AM

Here is an interesting link to global lightning strikes,almost in real time...a 2sec delay:

http://www.lightningmaps.org/?lang=en#m=oss;t=3;s=0;o=0;b=0.00;ts=0;y=29.0754;x=-35.6836;z=2;d=8;dl=4;dc=0;

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#24

Re: Lightning Water Well

09/24/2020 1:13 PM

This is what lightning rods are for. If you are concerned, put one up, run a ground wire and install a really good earth ground and let the weather have it's fun. Look up the EPRA site and look through their information on lightning strikes, results and protection. You can't protect for everything, but you can put in a basic protection system that will provide an easier path to ground than your well and supply power lines.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Hmmm...

Join Date: Jul 2010
Location: Maryland
Posts: 567
Good Answers: 29
#25

Re: Lightning Water Well

09/24/2020 3:06 PM

My Dad used to sell submersible well pumps. Lightning was the biggest failure mode for the pumps right after old age. Most manufacturers add spark gaps right at the pump and some offer protection for the control boxes in the house but, as SE said, lightning is a comprised of a huge amount of energy and anything can happen.

As far as direction, it's impossible to say. Do your water lines and the electrical supply to the pump go near the tree?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32212
Good Answers: 839
#26

Re: Lightning Water Well

09/24/2020 5:53 PM

The latest version of British Standard 7671 contains a protocol for determining whether surge protection is to be installed on the incoming supply to any electrical installation. It is a developing practice though, with all regulations, it is not retrospective.

The Original Poster might take its principles into account in the restoration and repair of the equipment in question, perhaps.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 29 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

AWSCWI(RETIRED) (1); Brave Sir Robin (1); BruceFlorida (1); Crabtree (1); Gperkins61 (1); HiTekRedNek (2); imboden (4); JE in Chicago (2); Jpfalt (1); larryvan (2); Lo_Volt (1); PWSlack (3); R_i_c_h (1); rashavarek (1); setlock77 (1); SolarEagle (4); Stef (1); tonyhemet (1)

Previous in Forum: 1 m x 1 m Parallel Plate Capacitor at 300 kV   Next in Forum: Lithium Ion Battery Parameters

Advertisement