For what applications, shall 1P+N MCB be installed instead of 1P or 2P MCB?
Pathfinder Tags: mcb
Re: 1P+N MCB
09/29/2020 1:54 AM
In a single pole + neutral mcb... the single pole is used as over-current protection and the neutral leg is used as a disconnect to isolate the neutral, this would be used if you have 2 different sources of power feeding the panel(such as an emergency generator and utility grid or other) and didn't want to mix the neutrals as a safety measure....Generally this is required by code...
Re: 1P+N MCB
09/29/2020 10:24 AM
A swimming pool one example,but there are many.
A pool disconnect must disconnect ALL conductors.
Hazardous locations also,which include service station pumps.
The list is long.Many exceptions and local variations.
Always consult the local authority having jurisdiction(AHJ).
Re: 1P+N MCB
09/29/2020 11:00 PM
when is it a must to install a 1P+N instead of a 2P?
Re: 1P+N MCB
09/30/2020 3:03 AM
When the code requires it.....lacking that, then when common sense dictates....
Good Answers: 128
Re: 1P+N MCB
09/30/2020 9:15 AM
Perhaps it also is influenced by what type of circuit breaker you are using. A 2P breaker that mounts on the panelboard bus is electrically very different from a 1P+N breaker that is lug-lug or a 1P+N breaker designed with the N being lug-lug while the P is attached to the panelboard bus.
--JMM
Re: 1P+N MCB
09/29/2020 7:31 AM
...and codes vary between countries.