Anonymous Poster #1

Cause of Blown Fuse?

10/07/2020 7:49 AM

Please I want to know the cause of a 10A fuse of inside the panel of CAT generator model 700 blowing

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#1

Re: Question

10/07/2020 8:47 AM

A short circuit is my WAG. This could be caused by frayed wire insulation. You might even be having electronics (capacitor) breaking down but that will be difficult to trouble shoot.

If you can see inside the failed fuse element area (a glass fuse) look to see if the whole fuse element vaporized. This will happen when a large overcurrent condition happened like a wiring short circuit causing the fuse to quickly open the circuit. If instead the fuse element appears to be intact or only a small break in the element exists then either a small but repeated overcurrent condition happened over time making the element brittle. In this latter case one only has to replace the fuse. A technician or electrical engineer with additional testing equipment may be able to safely modify the circuitry to prevent future "soft" fuse failures but simple replacement will still likely be the most cost effective solution.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#10
In reply to #1

Re: Question

10/08/2020 5:52 AM

Simply replacing a fuse that blows often is bad and extremely dangerous advice! If a fuse blows there is a fault which could if left running could potentially cause a fire or electrocution injury to operating personnel. You don't know if the fault is getting progressively worse. Get a qualified person to diagnose and fix the fault.

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Cause of Blown Fuse?

10/07/2020 9:37 AM

The first thing to do is to check that this is the proper fuse for that location...so you'll need a wiring diagram for that model number of CAT...Then get a few replacement fuses, and clean the fuse holder properly and I would add some conductive grease to both the fuse holder and the fuse contact surfaces...and replace the fuse...If it blows again immediately, then you know you have a short...so now you have to trace it out to check if possibly a component has failed, or the insulation on a wire has failed and the wire is touching to ground....

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #2

Re: Cause of Blown Fuse?

10/07/2020 9:20 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Cause of Blown Fuse?

10/07/2020 10:56 AM

Simple. There was a fault. The current passing through it at the fault event was more than it was designed, developed, type-tested and warranted to withstand. It did its job in disconnecting it. Somewhere else, there will be a mark where something went BLAT! All that is needed is to locate it. That spot cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4
In reply to #3

Re: Cause of Blown Fuse?

10/07/2020 11:41 AM

That's not necessarily true, if there is a bad connection in the fuse holder it can heat up causing the fuse element to melt...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#6
In reply to #4

Re: Cause of Blown Fuse?

10/07/2020 10:50 PM

Correct. Or it could be a simple matter of trying to connect and run too many devices at the same time, or a single device that requires more startup current than the generator can safely provide.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #6

Re: Cause of Blown Fuse?

10/13/2020 7:11 AM

That would indicate a design problem.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#13
In reply to #12

Re: Cause of Blown Fuse?

10/13/2020 9:47 AM

True, but we've all seen bad designs in use before.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#14
In reply to #12

Re: Cause of Blown Fuse?

10/13/2020 10:59 AM

Possibly. In a Google search, I failed to find a CAT generator with the model #700; so I have no idea of the size of this generator. If it is a generator with an output of 700 VA, this fuse could be in the output circuit. If it is a generator with an output of 700 KVA, then obviously the fuse would have to be feeding the control circuit.

We obviously need more info re: the specific model.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#15
In reply to #14

Re: Cause of Blown Fuse?

10/13/2020 11:15 AM

Sometimes I feel that we need Carnac the Magnificent as a CR4 member to help our visitors.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 4)
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#7

Re: Cause of Blown Fuse?

10/08/2020 12:11 AM

You might have more luck if you revealed the actual model number of the generator, this could be perhaps a 700kW or 700kVa or 700W generator, your 10A fuse might be control power, not likely to be excitation or stator leads. It’s likely that some unknown component failed, or that a wire insulation failed at a chafe point, so the control circuit is short circuited.

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#8

Re: Cause of Blown Fuse?

10/08/2020 12:48 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 807
Good Answers: 65
#9

Re: Cause of Blown Fuse?

10/08/2020 4:15 AM

There is only one way to find out why the fuse blew and that is to fault find on the circuit with the generator not running and ascertain where the fuse is in the electrical circuit.

Before any reasonable hypothesis as to why the fuse blew it is necessary to have more information on the generator rating and the actual circuit the fuse is to protect? Is it on the diesel motor protection and connected to 24V to feed the oil, water, fuel pump, fuel shutoff Mobray switch, or whatever, usually a glass fuse or a normal automotive type.

If in the DC excitation circuit, does it feed the exciter winding or the AVR, auto voltage regulator or in the AC to DC rectifier. The fuses used in this section are often HRC fuses.

More information is needed before anyone can even hazard a guess as to the cause of the open circuit adjacent fuse ends

__________________
Hare today, goon tomorrow!
Reply
Power-User

Join Date: Nov 2011
Location: NASA-Glenn Research Center, Cleveland Ohio
Posts: 389
Good Answers: 17
#11

Re: Cause of Blown Fuse?

10/08/2020 7:32 AM

on the older style generators (15yrs old) the cap is the first thing that goes wrong on portable generators. on the newer generators there is a voltage regulator assembly. the second would be to check the carbon contacts.

i'm not sure this would cause a direct short, but repair a unit, this is where you would look to before all other. a direct short should be on the other side of the fuse. i would first put an ohm meter (or a continuity tester) and measure between the wire and the frame (not painted) you will probably find that there is a direct contact.

at this point it is just finding the component or wire that is the culprit.

Reply Score 1 for Good Answer
Participant

Join Date: Oct 2020
Posts: 2
#16

Re: Cause of Blown Fuse?

10/15/2020 9:45 AM

Thanks to you all, I've gotten the fault, it's a faulty wire bridging each other

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#18
In reply to #16

Re: Cause of Blown Fuse?

10/15/2020 11:47 AM

Good! Now comes a tricky question many overlook, why did the insulation breakdown? From my experience this happens most often because the the wiring bundle was not properly strain relieved and/or secured to another support structure. Having a bundle of wires self supporting themselves in a high vibration environment like a generator will cause the insulation to be eventually chaffed away and shorting out the conductors.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19
In reply to #16

Re: Cause of Blown Fuse?

12/15/2023 7:03 AM

BLAT indeed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Oct 2020
Posts: 2
#17

Re: Cause of Blown Fuse?

10/15/2020 9:57 AM

I've gotten the fault, it was a wire insulation failure. Thanks

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #17

Re: Cause of Blown Fuse?

02/22/2024 3:19 AM

Every day is a leaning day.

BLAT indeed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 20 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abdulhamid (2); dkwarner (2); jhhassociates (1); PWSlack (4); redfred (4); rwilliams (1); setlock77 (1); SolarEagle (4); Stef (1)

Previous in Forum: Intelligent MCC   Next in Forum: Static Discharge Earthing for Gas Loading/unloading Tankers

Advertisement