11/22/2020 12:33 PM
Hi
I am looking for a resistor part #:
application: for load bank
18 to 20 ohms, 120 VAC, 800 to 1000 Watts.
Re: resistors part #
11/22/2020 1:21 PM
11/22/2020 4:06 PM
They do not list a 1000 watt resistors so it would require series and paralleling a bunch to get the wattage up to 1K.
Then you have the issue of dissipating 1000 watts of heat...not a very professional way to do it...get a heater instead.
11/22/2020 8:48 PM
Many heaters significantly vary their resistance as they heat up. A proper load bank, like these from Ohmite, will keep a very consistent resistance over a temperature range. Without knowing how the OP intends to use this, resistance changes may or may not be a problem. A 1kW halogen lamp could also fit the bill.
Now where will this heat go?
11/23/2020 7:10 AM
I have used heaters and fans when certifying large (50KW) UPS's for acceptance.They produce a lot of heat,even the small 1kw ones.
The rise time is not very critical in these cases.Never had a problem with acceptance.
BTU'S is proportional to the input wattage.
That is why I recommend a heater.
I Know about the large braking resistors used in industry,Warner Brake Co. makes a lot of electric braking and clutch systems,but that is not the link you original gave to the OP.
I decided to cut to the chase and give him a well recognized and effective method to accomplish his objective,without knowing all of the specifics.I figured it would be better than sending him all over the net on a wild goose chase.
11/24/2020 12:42 PM
Look here instead:
https://www.ohmite.com/high-power/
Two of these on a water-cooled plate and you can dump the heat down the sink if you don't want to warm the room.
11/24/2020 12:50 PM
this is a good choice, but expensive
11/24/2020 12:55 PM
maximum working voltage is 5000VDC. But the request is 120Vac. SO This may not work at all.
12/03/2020 11:15 AM
In most cases, it is O.K. to use a part with a higher voltage rating than the operating voltage. Not only is it O.K., most require it.
11/24/2020 4:28 PM
For around $30 he can get the heater I linked to.I have used heaters many times for load testing with no problems.They work well,and last a long time.
I load tested a 25 kw ups and had to put the heaters outside of the building because of the heat load on their A/C units.
11/22/2020 2:20 PM
Please list the suppliers that have been approached so far, and in which countries they operate. This will enable the forum to produce a quicker response.
The duty sounds like a single bar electric fire, available on a well-known internet auction site, for example.
11/26/2020 5:02 AM
11/22/2020 3:54 PM
11/22/2020 4:16 PM
You will not get 1000 watts with 120v and 18 to 20 ohm resistors.
You will need 8.3 ohms to get 1000 watts, and 6.67 ohms for 800 watts.
11/23/2020 5:27 AM
Er, um, try that calculation again, please?
11/23/2020 6:54 AM
No matter how hard I try,Jose Cuervo can not do simple math.And he's not too good at passwords or spelling either.It took him 5 tries to log in.I should have known better.And this morning he is still lingering in the shadows,and I will have to have some hair of the dog before I go any fuuuurther.
I hope to be bak lader.I de ose!
Good Answers: 42
11/23/2020 2:03 PM
I wonder if he needs the ohms and volts and wanted some excess wattage capacity?
I have "over specified" the wattage rating on designs to keep the temp rise down.
(I always thought the lost heat could be used by using a hot water tank heater, but never had any takers - they would add air conditioning to the room first.)
11/24/2020 10:36 AM
Recalculation,sans Jose Cuervo:
I feel much better now.
14.4ohms for 1000 watts,and 18 ohms for 800 watt.
11/22/2020 7:30 PM
11/23/2020 2:23 AM
11/23/2020 12:28 AM
I imagine that this is a replacement part in an already assembled "load bank."
Why not contact the OEM, research the schematic, or look at the print?
11/23/2020 4:44 AM
Why not use a 1Kw jug element as the load resistor and while it is heating the water make yourself a cuppa and think how easy it was to get a useful load with side benefits.
Hare today, goon tomorrow!
Re: Resistors Part #
11/24/2020 10:37 AM
Please give this forum the respect of posting your decision on this matter.
Good Answers: 15
12/03/2020 5:08 AM
If its a simple load bank rather the a component replacement a previous posters suggestion of a 1kW 110V convector heater takes some beating. A useful load bank in a nice container.
The tungsten halogen lamp is a bad idea. A tungsten lamp presents a cold filament to the supply and on initial start up takes around 15 to 20 times the current. Different matter once the filament has warmed up. I believe the heater is a little more gentle.